how can we can take BDV test in transformer?

Answer Posted / ilononurb

we can take the break down voltage of transformer oil by
using oil tester. Take oil sample of tr oil and put in to
the testing oil pot with the spere electrode of 2.5mm gap.
Applied gradually the voltage till the oil losses its
dielectric stenght. breakdown voltage will display to the
oiltester meter. As per IEC 156 Standards it should be
40kv.eff.

Is This Answer Correct ?    78 Yes 8 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

Difference between megger test equipment and contact resistance meter test instruments?

1009


Is it possible to measure the voltage of a battery from a single terminal?

1335


Define early construction of human being

1562


What is the reason for using a GE G101 MCB in place of an EP102 MCB if both are capable of AC circuit protection?

2286


Difference between control junction box (cjb) and power junction box(pjb)?

3453






what is the cause of voltage dipp or swell in the transmission lines?

1708


what is the calculation formula for motor starting torque,running torque, running torque.

1327


physical identification of HT & LT panel

1307


CPC cable .PVC \1C....I want to get sure that type is flexible indoor or to be install on trench. please advice .thanx :)

1525


What is the height of DA, DAL, DB, DC & DDE tower?

1837


HOW TO SELECT THE COPPER CABLE SIZES OF MOTORS,TRANSFORMERS?

1651


what is kondo syatem in eletrical traction

1750


what is the relative size of single and three phase?

1510


standard earthing rating for power line..

1757


what purpose to use excaiter in DG.?

2326