Suppose am having the PF value .8, so how can we say that
is it lagging or leading?
Answers were Sorted based on User's Feedback
Answer / raveendran.p
Pf is usually spelt as 0.8 lagging or 0.8 leading. There is
error in telling otherwise. However relatively 0.8 can be
assumed as lagging since lagging pf is commonly encountered
in power systems. Leading pf mostly will be stated
explicitely.
Is This Answer Correct ? | 29 Yes | 1 No |
Answer / mukund
if you are considering any equipment such as motor or
lighting load such as fluorescent lights
most of the loads are inductive in nature
you are talking about 0.8 lagging p.f.
people are using capacitor banks to improve p.f. upto unity
in this case it is definately 0.8 lagging p.f.
Is This Answer Correct ? | 17 Yes | 3 No |
Answer / vidhya
THE NATURE OF A POWER FACTOR WHETHER ITS LEADING OR LAGGING
IS DETERMINED BY THE TYPE OF LOAD WE ARE CONNECTING TO THE
SYSTEM.
Is This Answer Correct ? | 13 Yes | 1 No |
POWER FACTOR
1.If the value is -0.8 then it is lagging pf.
2.If the value is +0.8 then it is leading pf.
Is This Answer Correct ? | 13 Yes | 6 No |
Answer / gunasekaran
normally load r lagging nature so it is lagging power
factor only
Is This Answer Correct ? | 3 Yes | 1 No |
Answer / nandu
Raveendran.p is right
if insufficient data is given than it is assumed to be lagging.
Is This Answer Correct ? | 0 Yes | 1 No |
Answer / priya
if generator burden increases with this pf it is said to b lag and vice versa is lead
Is This Answer Correct ? | 0 Yes | 1 No |
Answer / santoshvarma
Just is the KVAR value from multifunction meter if it is
positive then 0.8 is lagging pf and if the KVAR value is
negative then 0.8 is Leading power factor.
Is This Answer Correct ? | 0 Yes | 1 No |
Answer / manoharmadhu kumar
by taking the avarage values of kwh and kvah . by
considering this values we can say that if kvah is greater
it is -0.8 pf or if kwh is greater it is +0.8 pf or if both
values are same it is unity pf or it is=1 pf .
by manoharmadhukumar
Is This Answer Correct ? | 0 Yes | 2 No |
Can someone explain how does an IDMT relay works.
What are documents to be required for export of the material?
what type of earthing do for dry fissure rock?
what is the effect of connecting three phase supply lines to three phase auto transformer output terminals through a fuse of 10Amp and a circuit breaker (MCB). Is this connection permanently destroy the transformer?
What are the Application of CT & PT ?
what will happen if i connect or change line with phase terminal
what are the main differences of delta and star connection
132 KV TRFO BUSHING CT BURNT WHEN A 6.6KV HAS BEEN APPLIED TO IT .WHY .ANY REASON ?
state the working of discharge lamp?
2 hp motar how many amps taken please show me the formula
how induction generator generated the power without excition like syncronous generator.
how we calculate the short circuit capacity of the busbar in LV & HT?