Answer / rakesh revi
If the total current is 1000A.
Then divide it by 08.
So 1000/0.8 = 1250.
So it need 1250Sq.mm bus bar of copper for a current of 1000A
| Is This Answer Correct ? | 14 Yes | 15 No |
Explain the experiment on ward leonard method of a speed control on a dc shunt motor with an suitable circuit diagram.
How to calculate HT XLPE CABLE for 11 kv / 433 v , 1500 kva oil type transformer system? plz provide step by step calculation
15 Answers Engineers India, Indian Railways, Polycab, Shashwat, Sitara Energy, Sonali Bank,
What is potientiometer.What is the use of it.
Current Transformer's star point must face the protected object for the relay operation?
how to select the cables based on amps ratings ? how to calculate the amps and how to select the cable size
In stepdown transformer 11/415 volt two nos.(R & Y)HT side fuse is blown ,what will be voltage of ry,rb,yb in secondary side
What is the exact minimum vale of voltage between an earth and netural which can damage or can do malfunction of the electronic equipments ? If this is mentioned in any book, pl.give reference.
0 Answers Bhushan Power Steel,
I have iti elec, 1st aid, and 5 yrs experience in 7.5 mw power plant. Am i eligeble for 11kv license in telangana state..when, how to apply for that.?
how hazordious area is classified at an oil & gas plant and categorise suitable class of electric equipment in that area like induction motors, LCS, Lighting Fixtures Fluerescent/Flood lights Mercury& sodium lights, J.Bs, Power Cables etc
11 kg trivevter meter has rating of -/5amps. And pt ratio11000/110v and is connected with 11kv ct/pt unit of cr ratio 75/5amps. And pt ratio of 11000/110v while checking accuracy of meter with HT Accuchek meter what value of PT ratio and CT ratio to be filled in Accuchek meter
We are planning to synchronized DG's with our captive plant in the event of black start of plant, but before sync we checked voltage of DG with our plant voltage and it varies from 5 V to 450 V. So in this condition how we can sync DG with plant ?
how much current does 3ph. 10 hp ac motor draw.
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)