Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


how much current does 3ph. 10 hp ac motor draw.

Answers were Sorted based on User's Feedback



how much current does 3ph. 10 hp ac motor draw...

Answer / ramesh

1 Hp = 746 watts
10 Hp Motor
10*746=7460w
so 7460 w is the power drawn by 3-ph motor. and three phase
voltage is 415 voltage.

so I = P/root3*v*pf*eff
i=Wattage/1.732*415*0.8*0.85
=7460/1.732*415*0.8*0.85
=7460/489
=15.25A

Is This Answer Correct ?    78 Yes 18 No

how much current does 3ph. 10 hp ac motor draw...

Answer / ramesh herur

The current drawn is Approx 16 Amps

Is This Answer Correct ?    46 Yes 12 No

how much current does 3ph. 10 hp ac motor draw...

Answer / karthik.j

10HP = 10*745watts = 7.45kW
I = 7.45/(1.732*415(volt)*0.8(power factor)*0.8(efficiency)
= 16.19Amps

Is This Answer Correct ?    25 Yes 8 No

how much current does 3ph. 10 hp ac motor draw...

Answer / pillay

how much current a 3 ph 10 hp motor takes is depending
on the load it is carrying. Genarally the max
safe current for a motor rated as 10 hp at
440 volts is about 14 amps.If it is consuming less
than 14 amps, that means it is under loaded but if it is
carrying more than 14 amps than IT MEANS IT IS OVERLOADED
which is harmful for the motor.

Is This Answer Correct ?    12 Yes 5 No

how much current does 3ph. 10 hp ac motor draw...

Answer / thalha

3ph 10HP full load current is 13.5...
load current is taken only how the load is connected..
We use star/delta starter mean running current is low than DOL starter...

Is This Answer Correct ?    10 Yes 10 No

how much current does 3ph. 10 hp ac motor draw...

Answer / keshava c

But eff.0.85 how to take o. 85 efficiency

Is This Answer Correct ?    0 Yes 0 No

how much current does 3ph. 10 hp ac motor draw...

Answer / bala.a

Laod = 10 HP = 10 * 0.746 =7.46 KW
= 7.46 * 1000 / RT 3 * 415= 10.38 A
Consider 1.6 Time for starting current = 10.38 * 1.6 =
16.06 A

Is This Answer Correct ?    10 Yes 14 No

how much current does 3ph. 10 hp ac motor draw...

Answer / emitparmar

10 Hp Motor....
1 Hp = 746 watts..

so 7460 w is the power drawn by 3-ph motor. and three phase
voltage is 415 voltage.

so I = P/V,
= 7460/415
= 17.97 A

Is This Answer Correct ?    5 Yes 19 No

Post New Answer

More Electrical Engineering Interview Questions

Application wise, where we should use AC motors and where we should DC motors?

1 Answers   Nespak,


Explain the experiment on ward leonard method of a speed control on a dc shunt motor with an suitable circuit diagram.

0 Answers  


A Question Like A Wire Is Wound Whose Resistance Is Some 132. 44647 Ohms. If A Voltage Of 30 mv, 296 Ma Current Is Applied To It What Is The Resistance.

0 Answers   TCS,


please give me all the Alarm .Trip ,Safety Relays & Conditions of UPS Systems mail me on ashokbabunhce@gmail.com

0 Answers  


Can we parallel two grid with different incoming voltage. Ex.let say one grid is 132kv and another is 220kv.

2 Answers  


without any theoretical calculations, can u approximately tell the current rating of a motor(above 30hp)working at 415VAC.

7 Answers  


Define step response?

0 Answers  


what is mean by kneepoint voltage? when it will happen? ( my doubt is, if CT secondary is open means ct get saturation or blas? what are factors are required for calculations? plz give currect anws:

0 Answers  


how can we measure 220kv or more than these voltages ...?and also how can we conform whether we r getting 220kv from generating stations throuth the h v transmission lines?

1 Answers  


what is the acceptable insulation resistance for motor/transformer?

2 Answers   Reliance, Tata Motors,


If R and Y terminals are short circuited,then power will cut. we all know that power cannot be stored.what will happen to already generated power at power station?

3 Answers  


I want to give Power supply to a house from the Feeder, Total Load of the House is 128 KW, how to calculate cable size for this load ?

5 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)