In stepdown transformer 11/415 volt two nos.(R & Y)HT side
fuse is blown ,what will be voltage of ry,rb,yb in
secondary side
Answers were Sorted based on User's Feedback
Answer / elangovan t
If blowing of HT side fuses result in zero magnetising
current in the primary winding, then there will not be any
voltage in ry,rb,yb on the secondary side
Is This Answer Correct ? | 19 Yes | 3 No |
Answer / t. eswara rao
If the primary is DELTA connected, there is no voltage in
the secondary for this case. if primary is star connected
and star point is earthed then it depends upon the
configuration of the transformer, whether it is star-delta
or star-star.It also depends upon the star point earthing
whether it is solidly earthed or through NGR.
Is This Answer Correct ? | 11 Yes | 0 No |
Answer / harish
depends upon the configuration of the
transformer...whether it is star delta,star star.....
Is This Answer Correct ? | 9 Yes | 5 No |
Answer / shashidara
usually distribution trans. are of del/star type . there will b no vltg at secndry
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / hb umesh shetty
there is no voltage in the secondery side,
Is This Answer Correct ? | 3 Yes | 2 No |
what would be the earth to neutral voltage in industries? if it is not main Taine then what will happen?
what is current actully?significance of current...not rate of change of flow.....
what is the contact resistance of Air circuit breaker??
what is the std. earthing resistance for 440V system or m/c, 33000/440 Volt substation? What is the std.?
Define the "All - Day Efficiency" of a Transformer
What is the minimum insulation value required for a cable between phase to phase and phase to earth of 380 Vac 50Hz circuit, having load arround 800 amps.
what is advantage in open delta connection?
what is pilot wire? what is the use of pilot wires?
I am having a 42KW 3 phase electrical heating furnace, heating element is 80/20 nichrome material, my connections is made in such a way that 2 star connection compromising 2 coils per phase so totally 12 coils, shall if i use it unbalanced star condition (instead of 2 group of 3 phase or 1 group of 3 phase, connecting 4 phases of 5 phases) what will be the consequences and is it acceptable?
All we know about T/R, Is it possible to make T/R primery singlr phase and secondery three phase,If it then how?... Need Description
Which is the largest hydropower station in the world?
can a 150 kva 3 phase 440v/230V delta-wye step down transformer can be use as step up transfoermer with connected loads at 440v side?