Answers were Sorted based on User's Feedback
Hazourdous areas are clasified according to the process of
the plant in a Oil or a gas plant dipends upon the lekages
like gasses or oils where occur in a work place
there are 3 zones
1. zone - 1 where lekages of oil or gas occur in abnormal
conditions
2. Zone - 2 where lekages are never occur in normal
conditions
3. Zone - 0 where lekages are likely occur in normal
operation conditions
the usage of electrical equipment is EXD EXP EXE
| Is This Answer Correct ? | 6 Yes | 1 No |
Answer / b das
For zone-0 ; no electrical equipment
For zone-1 ; only flame proof(FLP) electrical equipment
including cable gland with witht mark "exd","exp" "exi"
(intrinsically safe for instruments)certified by CMRI
For zone-2 ; electrical equipment including cable gland
with mark "exe" but continuous sparking part eg. slipring
etc. enclosure must be "exd"
Apart from above there are again gas group;1A,IIA/IIB,IIC.
Area under IIC most hazordous.
| Is This Answer Correct ? | 4 Yes | 0 No |
how can service sitting be setted for MCCB?Example for sittings IR (CURRENT RATING),IS(CURRENT STARTING)IO (current operating)?
How to calculate motor current for 3 ph & 1 Ph motor from KW rating?
how many types of cbs?with pcific ratings?
What is the difference between ground and neutral ?
What is the difference between earthing,ground&nutral?
how solar power plant energy meter multiplication factor
How many 2 ton window A/c can runs on a 125 KVA generator?
1.what is difference between ATS & STS main use. 2.what is difference between ACB& VCB With symobles,and main partes, manimum range. 3.How many types of relays and main function.
What is meant by SMPS how it working ... and where it used
what is the primary current in 415/415 v when secondry of dry type transformer is shorted.?
Difference Between Differential Relay and Restricted Earth Fault Relay of Power Transformers
How does frequency affect KVA rating of a transformer? If a 500 kva, 500 to 250 v, 60 hz t/f used in Canada is to be operated on 50 hz in Europe frequency then how will its KVA rating change? a-increase b-decrease c-remains same
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)