Answer / pillay
I believe you are talking about the air drier of a transformer
because this is an electrical forum.
When the transformer gets hot the insulating oil gets expended
and the air inside the conservator tank is pushed out through
the breather pipes and when the transformer gets cooler the
oil contracts and external air is drawn in. A path is created
for the movement of the air and some drying agent is placed
within them like silica gel.So all moisture is trapped by
drier.
Is This Answer Correct ? | 1 Yes | 0 No |
what is stiffness factor
How can claculate to attain the desired PF in the line ( HOW Much KVAR is required ) Pls Give the formula?
Why selected cable colour red yellow and blue in 3 phase Electrical system?
9 Answers Crompton Greaves, Essar, Gridco,
why need to be maintain power factor for industrial customer?
What is the difference between Contactor and Circuit breaker ?
IF i have switchgear with busbar current rating of 1000Amp 35kA then is it necessary to have outgoing breaker kA rating to be equal to busbar kA rating?
We are using Powerica make 100 KVA DG set. Whenever i connect compressor on DG load (Compressor Make Atlas Copco 5.5 kva) that time we face the lot of fluctuation on Dg output. Can you please suggest me how can prevent this fluctuation?
what will happen if a cw rotating altenator being synchronized to ccw rotating altenator
while doing the excitation current test on power transformer what is the value of voltage to be applied? Nomonal rated voltage or 10% of rated voltage? Is it necessary to apply on high voltage side?
How to calculate flow of water delivered by pump when pressure & size of pipe line is given
what is load despatching
Show formula which gives full load current 4.8 amps of a 3 HP motor and 27 amps of a 20 HP motor having 3 phase 460 volts, 0.8 Pf.