Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


is there any chance to get shock from the transformer oil at
the time of maintenance due to its dielectric property. . ?

Answers were Sorted based on User's Feedback



is there any chance to get shock from the transformer oil at the time of maintenance due to its di..

Answer / rvkkumar119

di-electrical strength of transformer oil is 40 kv /minute ,
so due to insulating property it will not get shock at any time.

Is This Answer Correct ?    12 Yes 2 No

is there any chance to get shock from the transformer oil at the time of maintenance due to its di..

Answer / durgadas

It is not a elctrical conducter..

Is This Answer Correct ?    7 Yes 1 No

is there any chance to get shock from the transformer oil at the time of maintenance due to its di..

Answer / santoshvarma

Transformer oil will have a dielectric strength of more than
40KV at normal conditions, because of impurities or moisture
the dielectric strength deteriorates and come down, f it
comes down the transformer will be short circuited( primary
and secondary windings) and will be busted until that there
is no case of getting shock for a human body

Is This Answer Correct ?    2 Yes 0 No

is there any chance to get shock from the transformer oil at the time of maintenance due to its di..

Answer / makudeshwaran

At the time of maintenance,
if the di-electric strength of the oil is more,there is
no shock
if the di-electric strength of oil is very low,there is
a chance to get electric shock

Is This Answer Correct ?    2 Yes 1 No

is there any chance to get shock from the transformer oil at the time of maintenance due to its di..

Answer / hareesh

Oil is having a insulating property so by touching the oil how can u getting shock? there is no shock by touching oil

Is This Answer Correct ?    0 Yes 0 No

is there any chance to get shock from the transformer oil at the time of maintenance due to its di..

Answer / sunmoorthy

This X fmr oil it's have specific di- electric strength normally 40kv/min so when this value gone down at that time x fmr safety circuit will be trip the x fmr breaker other wise no chance to get shock...

Is This Answer Correct ?    0 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

What is the difference between Neutral And Earth ?

2 Answers   Ambuja, Reliance,


can anyone tell me can the electromagnetic waves can be reflected back?if so how &by which material it can be reflected back?please tell me so that it can help to my wireless power trasnmission device.

0 Answers  


1. A 380 / 220 V r.m.s. 3-phase 4-wire circuit carries loads of 8 + j8.1 ohm; 4 + j4.1 ohm; and 2 +j2.1 ohmin the three phases respectively. The length of the circuit is 100 m, and the resistivity of the phase conductors is 0.0005 Ω/m. The neutral conductor is of the same size as the phase conductors. a) Select a reference angle 0for the first phase. Then write down the three phase voltages in both polar format and complex number format. b) Make appropriate assumptions, and take temperature effects on resistance is insignificant. Calculate the currents in the three phases. (Note: Determine conductor resistance, and apply Kirchhoff’s Voltage Law) Based on the result, suggest a main switch rating for the circuit. c) Show your preferred direction of neutral current in a diagram, and then determine its value. (Note: Apply superposition principle, and Kirchhoff’s Current Law) Use its magnitude to show that in this circuit, the unbalanced load may increase the voltage drop in some of the phases. (Note: Also observe the common volt drip in neutral) State your assumptions, if there are any. d) Suddenly the neutral wire of the circuit is broken. Estimate the new currents in the first phase, i.e. Phase L1. State your assumptions, if there are any.

0 Answers  


HOW TO CALCULATE THE HEAT AND LOAD OF LT-SUBSTATION WHICH CONTAINS 2*1MVA TRANSFORMERS,LT SWITCH BOARD,MLDB,ACB,BUSBAR,ETC...?

0 Answers  


how we can calculate cable size of 230v,1 hp single phase motor ? panel to motor distance is 25 meter

4 Answers  


a.c&d.c motor&generator

2 Answers   Vizag Steel,


how to interlock 3 nos MCCBs using under voltage coil. please provide me circuit diagram?

0 Answers   Honeywell,


what type of protection used below 132KV feeders

11 Answers   APTransco, Telecommunications, wbsedcl,


why impedance relay is used for medium transmission line protection

0 Answers  


What is the tube exial fan?

0 Answers  


at what base you will tell the direction of rotation of dc motors and generators?

0 Answers  


If two generator running parallel, at that condition both ngr Taken in line or taken any one ngr, but why any one or both Ngr in line? Ngr is use for which purpose?

3 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)