Answer / vipul kumar
lightning arrester is a device which is used to protect the
equipment against flashing of light or overvoltage by
providing low impedance path for current to ground.
| Is This Answer Correct ? | 176 Yes | 13 No |
Answer / pyobik
Lightning Arresters or Surge Arresters are always connected
in Shunt to the equipment to be protected, they provide a
low impedance path for the surge current to the ground.
Wave trap is a parallel tuned inductor - capacitor 'tank'
circuit made to be resonant at the desired communication
frequency.
It is the effort to utilize the same transmission line
between two substation for the purpose of communications.
At this communication frequencies the tank ckt provides
high impedance and does not allow to pass through them &
onto the substation bus & into transformers.
| Is This Answer Correct ? | 95 Yes | 12 No |
Answer / sivasamy83
Wave Trap,
This is varying the impedance...
The Application is PLCC(power line career communication)
Linghtining Arrester:
This is grounding the surge voltage.....
| Is This Answer Correct ? | 89 Yes | 29 No |
Answer / rakeesh
lighting arrerester s=are used to protect system from the
over voltages like flashs occered themn its act like low
impedance to ground
| Is This Answer Correct ? | 43 Yes | 7 No |
Answer / smita
LIGHNING ARRESTER IS THE NON LINEAR RESITANC (ZINK OXIDE)
WHICH GVES LOW RESISTENCE PATH TO HIGH VOLTAGE AND HIGH
RESISTENCE TO LOW VOLTAGE,IT IS CONNECTED IN SHUNT WITH
EUIPMENT.
| Is This Answer Correct ? | 42 Yes | 8 No |
Answer / thuranga
Lightening Arrester is connected in shunt with the lines so
that is protects from lightening.
when ever the lightening occurs, there is a voltage around
some thousands of voltage appear on line (3500V to 5000V)
for a fraction of seconds(25 to 30micro sec.s) which is more
than enough to damage all the equipment in the grid
connected to it. so when a lightening arrester is connected
then is provides low resistance path such that all that high
voltage is directed towards the earth resulting the
protection of all the equipments connected to the grid.
| Is This Answer Correct ? | 37 Yes | 9 No |
Answer / atul mishra
To protect human life and property, design engineers have to
install lightning protection systems on every GRID
SUB-STATION . The main function of the system is to capture
the lightning stroke, over voltage and then conduct
discharge current safely to the ground. Since there are 100
lightning discharges to the ground every throughout the
world, installing lightning protection systems are very
important for safety to human life and station
| Is This Answer Correct ? | 21 Yes | 10 No |
Answer / trilok kumar (engr-electrical)
Lighting arrestors are used to protect the system from the
lightining surges/high voltage surges.
wave trap is a device that can remove, filter out or
exclude noise and interference from a wave, usually a radio
wave.
It may also be called a Rejector-circuit for radio systems
It is an electronic filtering device designed to exclude
unwanted signals or interference from a receiver.
| Is This Answer Correct ? | 16 Yes | 8 No |
Answer / percy
wave trap dictinguishes b/w power freq waves and
carrier communication waves
| Is This Answer Correct ? | 15 Yes | 9 No |
Answer / jay prakash
a wawe trap is the device which trap the high frequency
signals to enter into substation.
As XL =2 Pi w f L as impedence is directly proprtional to
frequency thus provide high impedane for high frequency
(carrier frequency)& vice versa.
lightning arrester prevent the substation from lightning
impulse, under normal condion impedace of air gap is high
enough for the voltage i.e no discharge, in case of
lightning high voltage appears around air gap and cause a
discharge through air and go to ground and prevent from
fault
| Is This Answer Correct ? | 11 Yes | 5 No |
If 3-Ph motor of same rating connected in Delta & Star for same load one by one then which connection take more current in running (not in starting)for full load.(eg 8.5 KW,3-Ph 400 V)
kindly send me 11KV MV motor differential protection procedure by primary injection method.
where is the need for short circuit test for 3 see is required and why? can you explain in brief with application
what is diff b/w electrical & electronics ?
why we use isolation transformer?
What will happen if the rotor of an induction motor is fed from a 3 phase supply and the stator short circuited ?
what is the use of sdf?
where induction generator is used ?
whether a separate starter is used for a motor while it is connected to a vvvf panel?
what are the factors to be considered while design the breaker either HT or LT??
Why size of HT cable is less then LT cable inspite of the fact that voltage is higher in HT cable?
for 644KW load which MCCB should i use
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)