what is excitation system explain in detail with its
working?
Answer / mike
1) A.C. excitation.
This type of the exciter operated with a.c. supply and rated frequency around 50 until 250 Hz.The output provide with slip ring to be rectified for internal mounted diode cubicles.This types can replaced for commutator on the d.c with solid state rectifier.
The output from rectifier supply to the generator rotor with slip ring for the d.c excitation system. Usually a pilot exciter made from a permanent magnet for supply to main exciter.
For the main exciter,it commonly made in three phase used the combination of diode in a bridge formation.The bridge arm have a several piece of diodes in parallel condition.
The method for short circuit protection is each diode individually fused to remove it from the electrical circuit in when it happen.
2) Brushless excitation.
This excitation system have a similar function between A.C excitation with advance application.The rectifier diode installed on the exciter shaft.The main exciter has its output armature winding on the rotor with its field on the stator.
Normally for rotor output frequency rated around 100 and 250 Hz and it is connected to the shaft mounted diodes.The rotor of main generator can supply the output with directly application.
The pilot exciter can be a permanent magnet generator with frequency operation until 400 Hz.For the small generator,supply can provide from generator terminal to the exciter field.
3) Thyristor excitation.
For this type of excitation system it used thyristor rectifier to directly control the generator filed current and it can response with faster system by controlling the exciter field current.Thyristor excitation fed system is necessary to provide slip rings and brushes to connect to the machine rotor.
This function is important to alert and response to the error or faulty for system stability due to critical application.But it have disadvantage because this system not been developed commercially and not common system for generator at around the world.It also difficult to providing the reliably control signals to them from stationary equipment.
Excitation power may be provided with direct application to the coupled main and pilot exciters or it can fed from main generator terminals using a step down transformer.
Normally the transformer ratio is design to provide full output during the occurrence of a system fault and it reduces the machine terminal voltage for protection system.
Is This Answer Correct ? | 2 Yes | 0 No |
What are the different lines and what are the different types of losses occur on them?
whu does the power factor of diesel generator always be 0.8. please explain
what is relay what is protection & contact multiplying relays where it is used function in brief
sir please tel me how calucalte kwh if home taken load 30ams how maney kwh taken per day.and 3phase motor 5hp per hars how maney load teken and how mach kwh and forward me to electrical table for calicalte kwh and kvr and kvah
how to design step down 12 V, 1mA small transformer from 220 V AC? Because according to VI relation and power transfer it results bulky...
stand by earth fault protection (51G) for transformer rating 2000 kVA,Dyn11,33/0.400 V. LV NCT ratio and necessary resistor and metrosil values how to calculate
Is a contactor (or master relay) required between incoming lines and a VFD? The question goes to safety. If a contactor were used before the VFD and an e-stop engaged then the motor will coast to a stop (i.e. VFD loses power) instead of stopping much faster if the VFD braking fucntion were used. It would make more sense to keep power on the VFD.
what is the need of reactor in between the transmission line?..like powergrid like that..
Which of the following statements is incorrect?(a) 1N = 1 kgm/s2(b) 1V = 1 J/C(c) 30mA = 0.03A(d) 1 J = 1N/m
how to calculate KA rating of C.B?explain with Formula.
What is auto reclose system in Circuit breakers
How one can check the MAIN of a house wiring ?