What will happen to transformer if we gave 5HZ input instead
of 50/60Hz??? explain with reason
Answers were Sorted based on User's Feedback
Answer / devendra chaturvedi
if we gave transformer 5 hz instead of 50/60 hz at constant i/p voltage than B(max.flux density) increases t a very high value which saturates the core,increases the core losses to a very high value which may damage the core and transformer
| Is This Answer Correct ? | 6 Yes | 0 No |
Since V=K*B*frq [V= primary supply voltage -approx.
equal to E-emf]; B=magnetic flux density ; frq=frequency]
then if frq=5 Hz and V=constant B[5Hz]=10*B[50 Hz].The no-
load[excitation] current will be more than 300% rated
current.
You have to reduce the voltage to 10% from rated at 50 Hz
in order to get the same B.
| Is This Answer Correct ? | 3 Yes | 2 No |
For single phase(phase to neutral) having potential difference 230.in three phase(phase to phase)we have 440V HOW...?
what is a,b,c,d checks diesel generator?
Why dnt we generate 5-ph or 7-ph supply like as 3-ph supply
Why P.f. of the system decreases when it is connectect across induction motor? & how to maintain the p.f. of system to unity.?
Please tell me 1 ton = How many Kilowatt (Electrical)
19 Answers Essar, Mitsubishi, Taj Group, VCMS Technologies, Virtuous Retail,
explain impact of tariff on energy management..? and what is ABT tariff
back emf of motor at the time of starting ?
DIFFERNCE BETWEEN DCS AND PLC? HOW IT WORKS?
How to calculate KVA/VA rating of PT or CT from primary & secondary voltage or primary & secondary current?
A commercial Building is designed with 14th floor levels with indoor substation of three phase transformer with rated capacity of 1000 Kva.The transformer delivered 65% of its rated capacity at 0.67 power factor lagging.Because of low power factor, the power customer was penalized and certain cost was charged accordingly based on every point percentage lower than 85%.This situation may repeatedly happen on the succeding energy bills of power customer.The power customer is desired to improve its historical power factor of 0.67 lagging and no further penalty be impose by the local power company on the next bill. Q: Identify the appropriate solution you want to offer to Client?.Justify SCIENTIFICALLY and MATHEMATICALLY the principles behind the solution.
Why the motor take high starting current for long time(10- 15 sec) which is connected to Blower as compaire with a motor which is connected with pump with same rating?
What is reason to get a power factor nearly zero in resistive loads
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)