what is the use of Antipumping in HT breakers.
Answers were Sorted based on User's Feedback
Answer / mm
the anti pumping device is used to avoid continously
energising the breaker closing coil once the CB has already
closed. this is done to avoid burning the coil
| Is This Answer Correct ? | 85 Yes | 12 No |
Answer / s.prakash
The anti-pumping relay allows the breaker to close only
once for each press of the 'close' pushbutton (or rotation
of the handle).
| Is This Answer Correct ? | 58 Yes | 11 No |
Answer / k.ramesh,vepl
This Coil is used to avoid the continuous supply of the
breaker coil during faulty condition,once we are giving the
closing pulse during uncleared faults condition the breaker
will close one time only. After we are giving many more
closing pulse to the breaker,cannot perform that closing
operation with the help of anti pumping coil.
| Is This Answer Correct ? | 48 Yes | 7 No |
Anti pumping relay is used to prevent closing coil from
being burnt by the repeated closing command. Closing coil
is not designed for continuous electrical operation and
once the closing coil is energised, breaker will get on and
it will be remain energised mechanically until any trip
command is available. So continuous supply is not required
for closing coil.
| Is This Answer Correct ? | 33 Yes | 8 No |
Answer / sukhdev negi
the anti pumping device is used to avoid continously
energising the breaker closing coil once the CB has already
closed. this is done to avoid burning the coil
| Is This Answer Correct ? | 20 Yes | 5 No |
Answer / ahmed arafa _bapetco
Anti-pumping relay is used to avoid closing of the circuit
breaker when there is afaulty case , so the closing coil of
the circuit breaker can not be energised until the path is
healthy and the trip is not exist
| Is This Answer Correct ? | 15 Yes | 4 No |
Answer / lokesh thota
Pumping means if breaker is close & give close command (electrical or manual) to it,spring will discharge & charge again. To prevent this pumping anti pumping feature is required,which in turn will help to restrict unnecessary operations of breaker mechanisms.
| Is This Answer Correct ? | 9 Yes | 9 No |
The function of Anti Pumping relay is to cut off the supply to CB closing coil in case of TNC switch spring failure and prevent CB hunting effect i.e. continuous closing, opening operation.
| Is This Answer Correct ? | 0 Yes | 0 No |
A device, which function to trip a circuit breaker, contactor or equipment or to permit immediate trip by other device or to prevent immediate re-closure of a circuit interrupter in case it should open automatically even through its closing circuit is maintained in closed condition.
| Is This Answer Correct ? | 1 Yes | 2 No |
how to select the mpcbs and contactor for 3 phase 30 hp star delta motors.for plc control.and tell me the calaculation for future use.
what is a kit kat fuse?
Dear Sir, I willing to know if one 15Hp induction motor run in star connection. What happen power capacity of motor? Plz tell me.
1 Answers Amtek Tekfor Automotive,
why is that a 4*4mm cable,is always powdered internally
Draw an S.L.D of the main panel for a hospital, showing meter position. Essential loads are: 1) Equipment load 100 KW 2) Critical load 500 KW 3) Life AID Safety load 400 KW 4) NON-Essential load 200 KW 5) Other service loads 200 KW Calculate and suggest the size of the transformer, size of main cable, capacitor bank, and calculate the capacity of an emergency load having above first three mentioned loads is supplied by an emergency generator.
why power factor is important?
How to increase solar cell efficiency ?
why doesnt the back emf hold the speed of unloaded series motor?
what is the min and max dc voltage for a dc system (110vdc)
what will be the minimum megger value for 132 Kv (earthed) potential transformer
As per the theory current doesn’t flows in Neutral, but practically it is not applicable, explain why?
What is the lifetime of a Thyristor? Is there a recommended lifetime for thyristors after which they should be replaced?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)