what is the use of Antipumping in HT breakers.
Answers were Sorted based on User's Feedback
Answer / mm
the anti pumping device is used to avoid continously
energising the breaker closing coil once the CB has already
closed. this is done to avoid burning the coil
Is This Answer Correct ? | 85 Yes | 12 No |
Answer / s.prakash
The anti-pumping relay allows the breaker to close only
once for each press of the 'close' pushbutton (or rotation
of the handle).
Is This Answer Correct ? | 58 Yes | 11 No |
Answer / k.ramesh,vepl
This Coil is used to avoid the continuous supply of the
breaker coil during faulty condition,once we are giving the
closing pulse during uncleared faults condition the breaker
will close one time only. After we are giving many more
closing pulse to the breaker,cannot perform that closing
operation with the help of anti pumping coil.
Is This Answer Correct ? | 48 Yes | 7 No |
Anti pumping relay is used to prevent closing coil from
being burnt by the repeated closing command. Closing coil
is not designed for continuous electrical operation and
once the closing coil is energised, breaker will get on and
it will be remain energised mechanically until any trip
command is available. So continuous supply is not required
for closing coil.
Is This Answer Correct ? | 33 Yes | 8 No |
Answer / sukhdev negi
the anti pumping device is used to avoid continously
energising the breaker closing coil once the CB has already
closed. this is done to avoid burning the coil
Is This Answer Correct ? | 20 Yes | 5 No |
Answer / ahmed arafa _bapetco
Anti-pumping relay is used to avoid closing of the circuit
breaker when there is afaulty case , so the closing coil of
the circuit breaker can not be energised until the path is
healthy and the trip is not exist
Is This Answer Correct ? | 15 Yes | 4 No |
Answer / lokesh thota
Pumping means if breaker is close & give close command (electrical or manual) to it,spring will discharge & charge again. To prevent this pumping anti pumping feature is required,which in turn will help to restrict unnecessary operations of breaker mechanisms.
Is This Answer Correct ? | 9 Yes | 9 No |
The function of Anti Pumping relay is to cut off the supply to CB closing coil in case of TNC switch spring failure and prevent CB hunting effect i.e. continuous closing, opening operation.
Is This Answer Correct ? | 0 Yes | 0 No |
A device, which function to trip a circuit breaker, contactor or equipment or to permit immediate trip by other device or to prevent immediate re-closure of a circuit interrupter in case it should open automatically even through its closing circuit is maintained in closed condition.
Is This Answer Correct ? | 1 Yes | 2 No |
Hi everyone. Some Generators uses 3-Pole breakers with extra contactors for Neutral. Some uses 4-Pole. Why so? What is the idea behind this? Thanks in advance for the solution. Kr.
fuses rated by amperes but not power,why?
what's producer of XLPE cable laying in undergroung
Draw torque - speed curve and load curve of induction motor? mark operating point ?
Please help me regarding my one concern. - During earth pit testing we noticed that the Clean earth pit and dirty earth pit showing continuity (Resistance value - 5ohm) . I want to know that if both earth pit have separate location and there is not internal looping between PIT then why such continuity is showing on it . Because of this issue the field side all earthing point showing short. In PLC panel we are providing two types of earthing cable which is coming from separate earth pit (Clean and Dirty earth pit) because of earth PIT showing short our PLC is not complying spec . please help regarding this issues.
where does core based current transformer is used? and what is the value of lux in a work station?
What are the types of power in electrical power?
What r the specification furnishid in motor name plate?
What is the difference between EARTH & NEUTRAL?
What is an Isolation Xformer? What is the use of it?
what is vfd?
if single phase is having 220v supply then why three phase is having 440v instead of 660v?