what will be the minimum megger value for 132 Kv (earthed)
potential transformer
Answers were Sorted based on User's Feedback
Answer / sethar12
General rule is 1 MOhm/kV + 1, so for 132kV side
transformer, megger value must be at least 133MOhm.
| Is This Answer Correct ? | 13 Yes | 0 No |
Answer / haikal
As general rule in using megger is 1 MOhm/kV, so minimum
value is 132 MOhm.
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / c. devadas
132 x 2 Meg.Ohm at 70 degree celsius. Every reduction of 10
deg.C will double the insulation value.
| Is This Answer Correct ? | 4 Yes | 1 No |
1.what to do if ferquency of any power system continue to decrease ?
What type of DC Generator is used for Arc Welding purposes?
meter ratio is 100/5 CT ratio is 125/5, when the ratios changes i.e., CT ratio is 125/5 meter ratio is 100/5 what is the MF in boths conditions?
how to calculate power
how to calc. current for 5MVAR,50hz,33kv
The control system is used for?
why neutral wire don't shock?
how earth resistance can be improved in dry soil
How the flights will be fly be fly without ground connection under raining with thunder lighting?
what is the difference between UPS and INVERTER?
What is float cum boost charging system?
if we have a power factor 0.99 and we add a capacitive bank with it then what happen?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)