what will be the minimum megger value for 132 Kv (earthed)
potential transformer
Answers were Sorted based on User's Feedback
Answer / sethar12
General rule is 1 MOhm/kV + 1, so for 132kV side
transformer, megger value must be at least 133MOhm.
| Is This Answer Correct ? | 13 Yes | 0 No |
Answer / haikal
As general rule in using megger is 1 MOhm/kV, so minimum
value is 132 MOhm.
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / c. devadas
132 x 2 Meg.Ohm at 70 degree celsius. Every reduction of 10
deg.C will double the insulation value.
| Is This Answer Correct ? | 4 Yes | 1 No |
why hv winding is not placed near to transformer core
WHAT MEANT BY SEVICE FOCTOR?
In a Tap changing transformer where is the tap connected , is it connected in the primary side or it is connected in secondary side
what is meant by carrier aided trip protection in transmission line
when conductor rotates in varying magnetic field the emf will induced in it and it is sinusoidal in nature ...? Why it is not in square wave and rectangular wave in nature?
What is meant by unilitrel device?plz tell about h-parametrs
Difference between MCC and PDB
What do you mean by passive circuit elements and why these are called passive?
What are all present producing cost of Per KWH of various Fuel?
is it necessarry to charge the battery of ups always??
why nutral and earthing wire connect with each other in main panel board.
What is the AVR in DG & its functios
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)