Answer Posted / suresh kumar
Anti pumping relay is used to prevent closing coil from
being burnt by the repeated closing command. Closing coil
is not designed for continuous electrical operation and
once the closing coil is energised, breaker will get on and
it will be remain energised mechanically until any trip
command is available. So continuous supply is not required
for closing coil.
| Is This Answer Correct ? | 33 Yes | 8 No |
Post New Answer View All Answers
How to calculate the heat load for a electrical room
i applied for c licence with my one year apperents trainee and i have attaced with A grade contractor company experiance that is for 14 monts experiance this document is sufeicant for c licence? pls tell why they rejected
why current is constant on d.c?
What is the method for testing the differential protection stabilty in generator? When the time of starting What will happen if differentail protection connection wrong means?
What is value of earth resistance required for substation and equipment earthing and what are the reference guidelines
A TRANSFORMER 440/400V,DELTA/STAR CONNECTED.THE NEUTRAL CONNECTED WITH GROUND CABLE THAT IS DIRECTLY CONNECTED TO THE PANEL,FROM PANEL IT IS CONNECTED EARTH PIT.IS IT RIGHT? IF IT IS RIGHT LEAKAGE CURRENT AFFECTED.SECONDATY IS PROTECTED WITH EARTH LEAKAGE RELAY.
HAI SENT HPCL APTITUDE QUESTION PAPER, MY EMAIL ID IS angus_eee04@rediffmail.com,angus_eee04@yahoo.com
physical identification of HT & LT panel
What is Plank's Law?
What is an automatic controller?
What is ferro-resonance in electrical system? Why it occurs and what are measures to prevent it?
how 650 volts creates? where is use?
what is the meaning of 0.5ohm Resistance
1600kva capacity Transformers how the bucholz relay,Oil temperature,winding,surge relay relays setting are to be done
how to select the isolation tranformer for siemens 802dsl cnotroller