How we find the size of cable if we know the current
Answers were Sorted based on User's Feedback
Answer / aju
We can choose the cable according to the current rating
after considering overload and voltage drop factors
Usually cables are loaded upto 75-80 % of the rating
specified by manufacturer ..
For instance, if you need to choose a cable for a current
rating of 25 A, we can simply choose 6 sq.mm cable since it
can carry 35 Amps. It is desirable not to use 4 sq.mm cable
which has a current rating of 28 A since it has no
sufficient spare capacity for overload condition.
Again, the cable size also depends upon the voltage drop
which depends upon the length of the cable....
usually voltage drop must be within 3-5 % range.If it
exceeds this limit then next higher size must be used until
it satisfies the 3% range
Eg. for calculation of voltage drop in 25A, 240V single
phase feeder having 150M length
Voltage drop/Ampere/Metre for 35 Sq.mm cable=2.1mV
Voltage drop= (2.1x25x150)/1000 =7.88V
% Voltage drop= (7.88x100)/240 = 3028%
Since it exceeds the 3% range, take next cable size
Voltage drop of 50Sq.mm cable= (1.6x25x150)/1000 =6V
% Voltage drop =(6x100)/240 =2.5%
Hence, we can select 50Sq.mm cable
| Is This Answer Correct ? | 74 Yes | 15 No |
cable size can be selected like ,suppose if u have any
motor with u of 110kw and its full load current is 190 then
when it is in dol stater starting torque is high up to 2
times of that full load so we have to use 300sq mm.if it is
in star delta 240 sq mm is enough because in a star
starting current is low it means 70 to 60 percent of full
load .after that some time delay delta pick ups
| Is This Answer Correct ? | 40 Yes | 21 No |
How to calculate the electrical load for a standard telecom BTS shelter and capacity of DG set required to cater to this load?
3 Answers Bhel, INDUS, Indus Towers,
What shall be the secondary output voltage if the primary winding of a 220/6V, 50 Hz transformer is energized by an 110V, 60 Hz supply?
11kv = LT 440v , how many amp.supose 440v side 5000 amp curent drown
In my project i am layout cables under the Maintainance bay /Maintainance yard in the TG Building. Whether in this route i can lay the H.T.Cables??? i am taking all H.T cables from the H.T Transformer to the TG Building..
What is Grounding? any difference b\w earthing? if yes plz explan??
In Ferantti Effect Receiving end voltage is greater than sending end voltage but how it is possible. I know its all about charging current but give me some more detailed explaination?
i Have 1000kva 11/.4 kv voltemp make t/f Its a 2 year old. i wants to known how much iron losses & copper loses during no load condition.
Why star pointed terminal have no current? how?
how can i improve the power factor in domestic (230v)
what is daiod
i have install 750 kva distribution transformer at my site and want to do neutral earthing. what calculations should i follow to determine earthing conductor material and size?
How to distinguish whether MCB is DC or AC looking at it physically
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)