How we find the size of cable if we know the current
Answers were Sorted based on User's Feedback
Answer / aju
We can choose the cable according to the current rating
after considering overload and voltage drop factors
Usually cables are loaded upto 75-80 % of the rating
specified by manufacturer ..
For instance, if you need to choose a cable for a current
rating of 25 A, we can simply choose 6 sq.mm cable since it
can carry 35 Amps. It is desirable not to use 4 sq.mm cable
which has a current rating of 28 A since it has no
sufficient spare capacity for overload condition.
Again, the cable size also depends upon the voltage drop
which depends upon the length of the cable....
usually voltage drop must be within 3-5 % range.If it
exceeds this limit then next higher size must be used until
it satisfies the 3% range
Eg. for calculation of voltage drop in 25A, 240V single
phase feeder having 150M length
Voltage drop/Ampere/Metre for 35 Sq.mm cable=2.1mV
Voltage drop= (2.1x25x150)/1000 =7.88V
% Voltage drop= (7.88x100)/240 = 3028%
Since it exceeds the 3% range, take next cable size
Voltage drop of 50Sq.mm cable= (1.6x25x150)/1000 =6V
% Voltage drop =(6x100)/240 =2.5%
Hence, we can select 50Sq.mm cable
| Is This Answer Correct ? | 74 Yes | 15 No |
cable size can be selected like ,suppose if u have any
motor with u of 110kw and its full load current is 190 then
when it is in dol stater starting torque is high up to 2
times of that full load so we have to use 300sq mm.if it is
in star delta 240 sq mm is enough because in a star
starting current is low it means 70 to 60 percent of full
load .after that some time delay delta pick ups
| Is This Answer Correct ? | 40 Yes | 21 No |
what is the contact resistance of sf6 circuit breaker??
why do we prefer VCB over OCB? what are the advantages of Vaccum Ckt. Breaker over Oil Ckt. Breaker?
Why current Transformer is rated by 100A/5A/5A?
In industries Power factor is maintained by installing a suitable KVAR bank, How is the PF maintained for domestic use, where is the capacitor bank connected
why we use end termination xlpe cable on ht kit
How to parallel a alternator without using synchro scope or lamp methods
why ct secondary side shortlink provided? its open what will happen?while running ?
i want to ask that as everybody knows that in star connection on star point is called neutral. my question is that why on that poin called neutral. what is the reason behind it. what is the logic behind it. i heared somewhere that on this point all phases current become zero thats why. if this answer is right then prove why on that point is current become zero. if this answer is not right then tell me the right answer. post ur answer here or on my mail address. m.ikram786@yahoo.com m.ikram555@gmail.com. thanks.
what is meant by transformer differential protection ?
Q2). When 3 dice are simultaneously thrown, which of the following would be obtained? (a) Result 1: “A 5, a 3 and a 6” (b) Result 2:” A 5 three times” (c) Result 3:”A 5 twice and a 3” (d) All three results are equally likely. (Musigma Question)
how to setting voltage RTCC panel
Why do we will ground the positive terminal in electrostatic precipitator
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)