How we find the size of cable if we know the current
Answers were Sorted based on User's Feedback
Answer / aju
We can choose the cable according to the current rating
after considering overload and voltage drop factors
Usually cables are loaded upto 75-80 % of the rating
specified by manufacturer ..
For instance, if you need to choose a cable for a current
rating of 25 A, we can simply choose 6 sq.mm cable since it
can carry 35 Amps. It is desirable not to use 4 sq.mm cable
which has a current rating of 28 A since it has no
sufficient spare capacity for overload condition.
Again, the cable size also depends upon the voltage drop
which depends upon the length of the cable....
usually voltage drop must be within 3-5 % range.If it
exceeds this limit then next higher size must be used until
it satisfies the 3% range
Eg. for calculation of voltage drop in 25A, 240V single
phase feeder having 150M length
Voltage drop/Ampere/Metre for 35 Sq.mm cable=2.1mV
Voltage drop= (2.1x25x150)/1000 =7.88V
% Voltage drop= (7.88x100)/240 = 3028%
Since it exceeds the 3% range, take next cable size
Voltage drop of 50Sq.mm cable= (1.6x25x150)/1000 =6V
% Voltage drop =(6x100)/240 =2.5%
Hence, we can select 50Sq.mm cable
| Is This Answer Correct ? | 74 Yes | 15 No |
cable size can be selected like ,suppose if u have any
motor with u of 110kw and its full load current is 190 then
when it is in dol stater starting torque is high up to 2
times of that full load so we have to use 300sq mm.if it is
in star delta 240 sq mm is enough because in a star
starting current is low it means 70 to 60 percent of full
load .after that some time delay delta pick ups
| Is This Answer Correct ? | 40 Yes | 21 No |
a 440v 60hz 03 phase 100kw generator can deliver how much power in kw for 220v 60hz 01 phase load?
how we calculate the short circuit capacity of the busbar in LV & HT?
what is the differance of acb and mcb and mccb
how to calculate the settings for shaft ct protn in hydro generators
What does Magnetic Neutral Axis
2 Answers Eskom, Genus, Lanco,
why we are using DC supply for all protection relays, why cant we use AC supply..???
what is different between synchronous & asynchronous motors
hello friends..... any one have papers or any study materials?sail ,hpcl...?
why maintain the Dg PF is 0.8? Explain?
Show formula which gives full load current 4.8 amps of a 3 HP motor and 27 amps of a 20 HP motor having 3 phase 460 volts, 0.8 Pf.
Is your generator is automated or manual if so do you know the circuits?
what is meaning volt-hz ration,where is necessry tomaintain and why. specialy during increase the power of generator.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)