Answer / sudhanva madhukar mahamuni
Hello To every One,
This is Sudhanva Madhukar Mahamuni Electrical Design
Engineer. The reason behind the same is not a alternator /
generator. The reason behind the same is diesel engine.
(Surprise!!!!!!!!!!)
Carefully read the catalog of DG Set for e.g. for 750kVA its
written as 750kVA / 600kW @ 0.8 pf. It means that alternator
size is 750kVA and 600kW is of Diesel engine. It means that
diesel engine can delivery only 600kW power. so if we like
to maintain the same then we need to keep 750kVA load on DG
@ 0.8 (750 x 0.8 = 600kW.
But assume that your load on alternator is 600kVA then you
are allow to improve your power factor till unity i.e. 1.
Therefore load on engine will be 600kVA x 1 = 600kW.
Summary : if multiplication of electrical load (in kVA) to
Power Factor will be upto or less than kW rating of diesel
engine then we can play with power factor i.e. lead or lag.
Note : If we will not do as above mentioned and improve the
power factor then engine will cease off (dead) i.e. cant
repair or modify.
For further clarification you can call me or mail me on
sudhanvamahamuni@structwel.com or sudhanvamahamuni@gmail.com
Regards
Mahamuni
9769317386
Is This Answer Correct ? | 8 Yes | 1 No |
In DG ,we maintein pf .8 because , if pf decrease than
alternator has overload due to more current dron by load .
And if pf is increase ,than engine has overload due to
increase potational (volt ).
So maintain DG pf is 0.8 .
Is This Answer Correct ? | 6 Yes | 2 No |
Answer / vinodth
consider 1 transformer having the power 125mw,33kv...
1)p=125mw,
v=33kv,
cosQ=0.8
p=1.732VlIlcosQ
I=125000/1.732*33000*0.8
I=2733.7
2)cosQ=0.7
I=125000/1.732*33000*0.7
I=3124.29
loss=i*ir..if the pf reduces,then loss get increases...v
cant maintain the pf as unity,tats y the pf s maintained as 0.8
Is This Answer Correct ? | 7 Yes | 5 No |
How to connect a Restricted earth fault relay for 2000KVA,11/0.433 KV Distribution Transformer and What is the neutral CT ratio should be selelcted for 2000 MVA Transformer for estabilishing the Restricted earth fault relay
Calculate torque developed by the 3-phase, 5 H.P., 4 pole induction motor runs at 1500 rpm A 23 N-m B 21 N-m C 10 N-m D 0 N-m
how capacitance is neglected in short transmission lines ?
What is the function of a pressure Switch in a Substation?
can any one help me for my ups inter view , list out few basic technical ups question with answer.
How good are you in resolving the commercial issues to Employer's advantage?
What differance between Circuit brekar and Isolater?
Comparision of Air break circuit breaker, SF6 Circuit breaker and vacuum circuit breaker.
what is the difference between high impedance & low impedance
what is black out?,what is brown out?
What is George phenomena to start the synchronus machine?
Lt motor sfu flashing reasons?