why maintain the Dg PF is 0.8? Explain?
Answers were Sorted based on User's Feedback
Answer / sudhanva madhukar mahamuni
Hello To every One,
This is Sudhanva Madhukar Mahamuni Electrical Design
Engineer. The reason behind the same is not a alternator /
generator. The reason behind the same is diesel engine.
(Surprise!!!!!!!!!!)
Carefully read the catalog of DG Set for e.g. for 750kVA its
written as 750kVA / 600kW @ 0.8 pf. It means that alternator
size is 750kVA and 600kW is of Diesel engine. It means that
diesel engine can delivery only 600kW power. so if we like
to maintain the same then we need to keep 750kVA load on DG
@ 0.8 (750 x 0.8 = 600kW.
But assume that your load on alternator is 600kVA then you
are allow to improve your power factor till unity i.e. 1.
Therefore load on engine will be 600kVA x 1 = 600kW.
Summary : if multiplication of electrical load (in kVA) to
Power Factor will be upto or less than kW rating of diesel
engine then we can play with power factor i.e. lead or lag.
Note : If we will not do as above mentioned and improve the
power factor then engine will cease off (dead) i.e. cant
repair or modify.
For further clarification you can call me or mail me on
sudhanvamahamuni@structwel.com or sudhanvamahamuni@gmail.com
Regards
Mahamuni
9769317386
| Is This Answer Correct ? | 8 Yes | 1 No |
In DG ,we maintein pf .8 because , if pf decrease than
alternator has overload due to more current dron by load .
And if pf is increase ,than engine has overload due to
increase potational (volt ).
So maintain DG pf is 0.8 .
| Is This Answer Correct ? | 6 Yes | 2 No |
Answer / vinodth
consider 1 transformer having the power 125mw,33kv...
1)p=125mw,
v=33kv,
cosQ=0.8
p=1.732VlIlcosQ
I=125000/1.732*33000*0.8
I=2733.7
2)cosQ=0.7
I=125000/1.732*33000*0.7
I=3124.29
loss=i*ir..if the pf reduces,then loss get increases...v
cant maintain the pf as unity,tats y the pf s maintained as 0.8
| Is This Answer Correct ? | 7 Yes | 5 No |
hi, in the event earth grounding is not available in a project, is there any other way to make the elcb work? fyi, i have an instant water heater (6.5kw) installed, however if there is grounding in the heating element inside the heater assembly, i will get grounded. thank you in advance to those who will answer my question.
What is UJT PNP, NPN transistor & working principles?
Why power factor is arising in electrical circuit, is it possible to eliminate from the circuit, why
why pure sine wave inverter used for desktop ?
Why ground terminal is used in pot meter 10k ohms
Why transformer called by KVA?
How to calculate the KA rating for a circuit breaker if we know the KVA rating of the generator feeding it?
if v r considering a 4000/1A ct,if v inject 1 amps in secondary core wat happens?(consider as 2 core ct,each for metering and protection)
What is the maxvoltage drop allowed at any healthy joint at full load ?
What is the formula to calculate the size of Aluminium and copper cable?
What is the best thing to protect the motor from running over full current. CT or O/L or pressure transducer at the given pressure rating
salam, hi, how to calculate british temperature unit (B.T.U)?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)