why maintain the Dg PF is 0.8? Explain?
Answers were Sorted based on User's Feedback
Answer / sudhanva madhukar mahamuni
Hello To every One,
This is Sudhanva Madhukar Mahamuni Electrical Design
Engineer. The reason behind the same is not a alternator /
generator. The reason behind the same is diesel engine.
(Surprise!!!!!!!!!!)
Carefully read the catalog of DG Set for e.g. for 750kVA its
written as 750kVA / 600kW @ 0.8 pf. It means that alternator
size is 750kVA and 600kW is of Diesel engine. It means that
diesel engine can delivery only 600kW power. so if we like
to maintain the same then we need to keep 750kVA load on DG
@ 0.8 (750 x 0.8 = 600kW.
But assume that your load on alternator is 600kVA then you
are allow to improve your power factor till unity i.e. 1.
Therefore load on engine will be 600kVA x 1 = 600kW.
Summary : if multiplication of electrical load (in kVA) to
Power Factor will be upto or less than kW rating of diesel
engine then we can play with power factor i.e. lead or lag.
Note : If we will not do as above mentioned and improve the
power factor then engine will cease off (dead) i.e. cant
repair or modify.
For further clarification you can call me or mail me on
sudhanvamahamuni@structwel.com or sudhanvamahamuni@gmail.com
Regards
Mahamuni
9769317386
| Is This Answer Correct ? | 8 Yes | 1 No |
In DG ,we maintein pf .8 because , if pf decrease than
alternator has overload due to more current dron by load .
And if pf is increase ,than engine has overload due to
increase potational (volt ).
So maintain DG pf is 0.8 .
| Is This Answer Correct ? | 6 Yes | 2 No |
Answer / vinodth
consider 1 transformer having the power 125mw,33kv...
1)p=125mw,
v=33kv,
cosQ=0.8
p=1.732VlIlcosQ
I=125000/1.732*33000*0.8
I=2733.7
2)cosQ=0.7
I=125000/1.732*33000*0.7
I=3124.29
loss=i*ir..if the pf reduces,then loss get increases...v
cant maintain the pf as unity,tats y the pf s maintained as 0.8
| Is This Answer Correct ? | 7 Yes | 5 No |
Shall I use 40A semiconductor Fuses in 32 A SFU ? Frame size is same. What Happen if Fuses burn on SFU?
Why battery is always operate on dc supply?
1 Answers Vikram Ispat Industries,
if we convert watt into kva,which one formula use by us,pls tell me?
in VFD when freq is reduce the voltage will reduceor not if it will reduced upto ...
if transmission voltage expressed as the multipple of form factor(1.11)........11,33,66,220 etc......then why madakkathara substation(kerala) voltage is 400kv..not 440.....?
In the market there is availability of MCCB & ACB (800A), So, Where i can use MCCB & ACB for the same Rating?
what are the basic insulation levels & what its Unit
Why breakers not synchronized when the synchroscope is going in the anticlockwise direction?
how to deside the capacity of chock for drive?
hi this toufik here. i am doing my b.e.degree.now i am in final year and supposed to do a project in this year so i thinking to control the buchholz relay using software base means checking the status of transformer oil using microcontroler, plc or scada. so can i do so...??? alz suggest me...
what is the difference between earthing and unearth
What is the difference IN MCCB's between thermal magnetic and electronic tripping system ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)