Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


why maintain the Dg PF is 0.8? Explain?

Answers were Sorted based on User's Feedback



why maintain the Dg PF is 0.8? Explain?..

Answer / sudhanva madhukar mahamuni

Hello To every One,

This is Sudhanva Madhukar Mahamuni Electrical Design
Engineer. The reason behind the same is not a alternator /
generator. The reason behind the same is diesel engine.
(Surprise!!!!!!!!!!)

Carefully read the catalog of DG Set for e.g. for 750kVA its
written as 750kVA / 600kW @ 0.8 pf. It means that alternator
size is 750kVA and 600kW is of Diesel engine. It means that
diesel engine can delivery only 600kW power. so if we like
to maintain the same then we need to keep 750kVA load on DG
@ 0.8 (750 x 0.8 = 600kW.

But assume that your load on alternator is 600kVA then you
are allow to improve your power factor till unity i.e. 1.
Therefore load on engine will be 600kVA x 1 = 600kW.

Summary : if multiplication of electrical load (in kVA) to
Power Factor will be upto or less than kW rating of diesel
engine then we can play with power factor i.e. lead or lag.

Note : If we will not do as above mentioned and improve the
power factor then engine will cease off (dead) i.e. cant
repair or modify.

For further clarification you can call me or mail me on
sudhanvamahamuni@structwel.com or sudhanvamahamuni@gmail.com

Regards

Mahamuni
9769317386

Is This Answer Correct ?    8 Yes 1 No

why maintain the Dg PF is 0.8? Explain?..

Answer / prakash veer singh

In DG ,we maintein pf .8 because , if pf decrease than
alternator has overload due to more current dron by load .
And if pf is increase ,than engine has overload due to
increase potational (volt ).

So maintain DG pf is 0.8 .

Is This Answer Correct ?    6 Yes 2 No

why maintain the Dg PF is 0.8? Explain?..

Answer / vinodth

consider 1 transformer having the power 125mw,33kv...
1)p=125mw,
v=33kv,
cosQ=0.8
p=1.732VlIlcosQ
I=125000/1.732*33000*0.8
I=2733.7
2)cosQ=0.7
I=125000/1.732*33000*0.7
I=3124.29
loss=i*ir..if the pf reduces,then loss get increases...v
cant maintain the pf as unity,tats y the pf s maintained as 0.8

Is This Answer Correct ?    7 Yes 5 No

why maintain the Dg PF is 0.8? Explain?..

Answer / jayashree

Mr. Vinodth, the query is about DG. Please answer it again.

Is This Answer Correct ?    3 Yes 1 No

Post New Answer

More Electrical Engineering Interview Questions

hi, in the event earth grounding is not available in a project, is there any other way to make the elcb work? fyi, i have an instant water heater (6.5kw) installed, however if there is grounding in the heating element inside the heater assembly, i will get grounded. thank you in advance to those who will answer my question.

0 Answers  


What is UJT PNP, NPN transistor & working principles?

1 Answers   TATA,


Why power factor is arising in electrical circuit, is it possible to eliminate from the circuit, why

2 Answers  


why pure sine wave inverter used for desktop ?

1 Answers  


Why ground terminal is used in pot meter 10k ohms

0 Answers   Mahle,


Why transformer called by KVA?

8 Answers   Reliance,


How to calculate the KA rating for a circuit breaker if we know the KVA rating of the generator feeding it?

2 Answers  


if v r considering a 4000/1A ct,if v inject 1 amps in secondary core wat happens?(consider as 2 core ct,each for metering and protection)

1 Answers  


What is the maxvoltage drop allowed at any healthy joint at full load ?

1 Answers   Kirloskar, Seyadu,


What is the formula to calculate the size of Aluminium and copper cable?

0 Answers  


What is the best thing to protect the motor from running over full current. CT or O/L or pressure transducer at the given pressure rating

0 Answers  


salam, hi, how to calculate british temperature unit (B.T.U)?

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)