what is the differance of acb and mcb and mccb
Answers were Sorted based on User's Feedback
Answer / jessy
All these are circuit breakers of different Current Ranges.
mcb is used for low current ranges, avaiable uo to 63A
mccb is used for medium current ranges up to 3200 A
acb is used for more higher ratings.
Is This Answer Correct ? | 43 Yes | 12 No |
MCB - Miniature circuit breaker is used from 1A to 100 Amps
rating. which is only magentic tripping device
MCCB - Moulded circuit breaker is used from 32amps to
1600amps ( combination of both thermal and magentic
tripping)
ACB - Air circuit breaker is used from 630amps to 5000amps
capacity - in older version only thermal tripping only. now
a days it is combination of both thermal and magnetic
tripping
Is This Answer Correct ? | 24 Yes | 4 No |
Answer / prasad
there are so may circuit breakers, depends upon their ratings
we use up to 63A as mcb and above this current we use mccb or
acb.
acb means air circuit breaker
Is This Answer Correct ? | 15 Yes | 7 No |
Answer / mani777
mcb.......o.5 to 63amp
mccb......upto ...1600 amp
acb(air circuit breaker) used in big transformer...hence
for more amps
Is This Answer Correct ? | 6 Yes | 3 No |
Answer / ram
please correct long form of mccb, it is moulded case
circuit breaker.
all are the different types of ckt bkrs & are used
according to the load in amps.
Is This Answer Correct ? | 4 Yes | 1 No |
Answer / dan
MCB - miniture circuit breaker
MCCB - molded case circuit breaker
acb - air circuit breaker
MCB are upto ~60 amp
MCCB are from 60 amp to thousands amp
ACB are for huge power stations thousands of amps.
Is This Answer Correct ? | 4 Yes | 2 No |
mcb-miniature circuit breaker- 6amp to 63amp
mccb-moulded case circuit breaker- upto 1600amp
acb- air circuit breaker- above 1600amp
regards deepak
Is This Answer Correct ? | 3 Yes | 5 No |
Answer / marc
Hello.
Does someone know what is AACB ? Amp Air Circuit Breaker.
What is the difference with ACB ?
Thank you
Is This Answer Correct ? | 0 Yes | 2 No |
Answer / shiva.sh
mcb-miniature circuit breaker- 6amp to 100 amp
mccb-moulded case circuit breaker- upto 1000 amp
acb- air circuit breaker- above 6000 amp
Is This Answer Correct ? | 0 Yes | 2 No |
Answer / ankush dhiman
mcb (miniature ckt. breaker) is used for low current
ranges, avaiable uo to 63A
mccb (miniature current ckt breaker )is used for medium
current ranges up to 800 A
acb (air ckt breaker)is used for more higher ratings.
Is This Answer Correct ? | 6 Yes | 11 No |
what methods are used to improve power factor?
How you will determine the volume of oil in a particular Distribution transformer.
What is an iron loss or core loss pi?
how we can select a transformer based on a particular load. suppose we have 4 motors of rating 40 h.p , 50 h.p, 80 h.p & 100 h.p. then what rating of transformer we can select. urgent. pls reply
Which system use dc to dc high voltage gain A. Solar system B. Battery backup
how harmonics are generated due to nonlinear load & how harmonic filters work?
why ten delta testing is carried out on power transformer
what is mean by potential and potential free contacts
Am i eligible to get electrical supervisor licence? As i did diploma as well as degree in Electrical Engg. in June 2011. Now i am working in 15 MW Power plant from 2 mnths. i belongs to Maharashtra.
What is the Efficiency in Electric motor ?
how do we calculate cable sq mm size,that if 50 A load
how to connect from a line-to-line connection to a line-to- neutral connection?