Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


how to select DG set for certain load?

Answers were Sorted based on User's Feedback



how to select DG set for certain load?..

Answer / soumendasbiswas

Depending upon the total load and maximum demand of that
plant...

Is This Answer Correct ?    21 Yes 7 No

how to select DG set for certain load?..

Answer / rajani

Actually DG size has to select depends on maximum demand
and considering base load and starting load and step load

base load = total maximum demand - loads which are
taking high loads at startign

starting load = if motor loads are DOL starts 6 times to
the Ifl will take at starting and soft
starters /VFD's will take 3 times to Ifl
step load = Whwn the main power supply is off
immidiently what are the load we can
switched ON through DG -called step load
(generally 40-60% of Dg load can be ON as
first step)

So our selected DG shopuld meet the step load and capable
to withstand startign loads

Is This Answer Correct ?    12 Yes 5 No

how to select DG set for certain load?..

Answer / sheo

Suppose LOAD-1000 KW

So design load of Genset @ 80% inefficiency.
and power factor @80% in case of ( Failure of capacitor)because life of Capacitor and Gen set never equal to each other.
so 100% power back-up for 1000 KW load required DG 1000/0.64=1562.5 KVA

Recommended DG-1500 KVA

Is This Answer Correct ?    5 Yes 0 No

how to select DG set for certain load?..

Answer / rakesh kumar sharma

generally the efficiency of the D.G.set is 80% because of
the power factor.so u have to add 20% on the entire
load.

Is This Answer Correct ?    6 Yes 3 No

how to select DG set for certain load?..

Answer / sijish

DG normaly loads up to 80% of the full load rating,

First step.Calaculate the load in KW.
Consider the staring current of the Load.
The minimum Amps rating of the dg shoul be 4 Times the
Running current of the motor load

Is This Answer Correct ?    2 Yes 0 No

how to select DG set for certain load?..

Answer / anil

Depending up on the total load to select the dg.for 5kw
load 10kva DG is suitable.
dg can be loaded for 80% of full load ,ie 8kw
calculating PF 6.4 kw can be loaded in 10kva dg.

Is This Answer Correct ?    2 Yes 1 No

how to select DG set for certain load?..

Answer / m.prabhakar

Depending up on the total load to select the dg.For example
180KW load is there 200kva capacity genarator is sufficient.

Is This Answer Correct ?    23 Yes 29 No

Post New Answer

More Electrical Engineering Interview Questions

WHY HUMMING SOUND OCCURED IN HT TRANSMMISSION LINES ?

26 Answers   GE,


purpose of breaker contact multiplication relay?

5 Answers   ABB,


Different STANDARDS (BS, IS, IEC etc) gives different informations on CT specification. How they correspons w r t each other (i.e I mean to say BS provides "knee point voltage" but IS does not, then how can i select CT)

0 Answers  


can we use breather in a SEALED power or distribution transfomer instead of injecting nitrogen.

1 Answers  


typically in power distribution substation. 1- Any idea how would be the graph of capacitor bank consumption verses time through the day . 2- How is the switching ( on and off ) of the capacitor bank, per need?

0 Answers   Siemens,


what is the chemical name and formula of refrigarent R-134a.

0 Answers   Blue Star,


what are the advantages and disadvantages of speed control of 3 phase induction motor by varying frequency explain with drawing

0 Answers   ABB, Genpect,


What is the "IS" for Rising Main?

1 Answers   APTransco, NTPC,


whenewher three phase supply is given to induction motors revolving/rotating field is created & rotor rotates.When the three phase supply is given to three phase transformer then revolving,/rotating field is created or not? if not why?

1 Answers  


Can you explain operating principle of Inverse Definite Minimum Time” (IDMT) relay

2 Answers  


who invented electricity?

20 Answers   L&T,


Explain difference between stand by earth fault and residual earth fault protection?

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)