how to select DG set for certain load?
Answers were Sorted based on User's Feedback
Answer / soumendasbiswas
Depending upon the total load and maximum demand of that
plant...
| Is This Answer Correct ? | 21 Yes | 7 No |
Answer / rajani
Actually DG size has to select depends on maximum demand
and considering base load and starting load and step load
base load = total maximum demand - loads which are
taking high loads at startign
starting load = if motor loads are DOL starts 6 times to
the Ifl will take at starting and soft
starters /VFD's will take 3 times to Ifl
step load = Whwn the main power supply is off
immidiently what are the load we can
switched ON through DG -called step load
(generally 40-60% of Dg load can be ON as
first step)
So our selected DG shopuld meet the step load and capable
to withstand startign loads
| Is This Answer Correct ? | 12 Yes | 5 No |
Answer / sheo
Suppose LOAD-1000 KW
So design load of Genset @ 80% inefficiency.
and power factor @80% in case of ( Failure of capacitor)because life of Capacitor and Gen set never equal to each other.
so 100% power back-up for 1000 KW load required DG 1000/0.64=1562.5 KVA
Recommended DG-1500 KVA
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / rakesh kumar sharma
generally the efficiency of the D.G.set is 80% because of
the power factor.so u have to add 20% on the entire
load.
| Is This Answer Correct ? | 6 Yes | 3 No |
Answer / sijish
DG normaly loads up to 80% of the full load rating,
First step.Calaculate the load in KW.
Consider the staring current of the Load.
The minimum Amps rating of the dg shoul be 4 Times the
Running current of the motor load
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / anil
Depending up on the total load to select the dg.for 5kw
load 10kva DG is suitable.
dg can be loaded for 80% of full load ,ie 8kw
calculating PF 6.4 kw can be loaded in 10kva dg.
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / m.prabhakar
Depending up on the total load to select the dg.For example
180KW load is there 200kva capacity genarator is sufficient.
| Is This Answer Correct ? | 23 Yes | 29 No |
For refrigerators the motor current is raised beyond its rating on both conditions when the voltage of the system is more(say 270v) than the rated voltage(220v) as well as when the voltage of system is less(say 160v) than normal voltageof 220v, why explain?
0 Answers Electrical Tech, UPSE,
What is the current carrying capacity of 1.5 rm and 2.5 rm cable
what is kondo syatem in eletrical traction
Wheather there exist any dc transformer
Why the capcitor to be discharged after put in to operation & why not inductor though the both elements stores energy?
What is the meaning of 40X8X2 busbar dimensions for carring load of 400 Amps
What will happen if primary of transformer is fed with Square wave instead of sinsoidal wave ?Will it operate or Not?
What is ferrite affects and what is disadvantage of ferrite affects.
In legging current reactive power is arise but in leading current which power will be arise ? and in this case, is active power more than rated ?
What is an iron loss or core loss pi?
how to increase the power factor in machines
why capacitor is not discharged phase to body
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)