how to select DG set for certain load?
Answers were Sorted based on User's Feedback
Answer / soumendasbiswas
Depending upon the total load and maximum demand of that
plant...
Is This Answer Correct ? | 21 Yes | 7 No |
Answer / rajani
Actually DG size has to select depends on maximum demand
and considering base load and starting load and step load
base load = total maximum demand - loads which are
taking high loads at startign
starting load = if motor loads are DOL starts 6 times to
the Ifl will take at starting and soft
starters /VFD's will take 3 times to Ifl
step load = Whwn the main power supply is off
immidiently what are the load we can
switched ON through DG -called step load
(generally 40-60% of Dg load can be ON as
first step)
So our selected DG shopuld meet the step load and capable
to withstand startign loads
Is This Answer Correct ? | 12 Yes | 5 No |
Answer / sheo
Suppose LOAD-1000 KW
So design load of Genset @ 80% inefficiency.
and power factor @80% in case of ( Failure of capacitor)because life of Capacitor and Gen set never equal to each other.
so 100% power back-up for 1000 KW load required DG 1000/0.64=1562.5 KVA
Recommended DG-1500 KVA
Is This Answer Correct ? | 5 Yes | 0 No |
Answer / rakesh kumar sharma
generally the efficiency of the D.G.set is 80% because of
the power factor.so u have to add 20% on the entire
load.
Is This Answer Correct ? | 6 Yes | 3 No |
Answer / sijish
DG normaly loads up to 80% of the full load rating,
First step.Calaculate the load in KW.
Consider the staring current of the Load.
The minimum Amps rating of the dg shoul be 4 Times the
Running current of the motor load
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / anil
Depending up on the total load to select the dg.for 5kw
load 10kva DG is suitable.
dg can be loaded for 80% of full load ,ie 8kw
calculating PF 6.4 kw can be loaded in 10kva dg.
Is This Answer Correct ? | 2 Yes | 1 No |
Answer / m.prabhakar
Depending up on the total load to select the dg.For example
180KW load is there 200kva capacity genarator is sufficient.
Is This Answer Correct ? | 23 Yes | 29 No |
how we select fuse rating for motor?
what is volt drop formula?stm
A resistance, inductance & capacitance are connected in series between points A & B.The voltage drops across the resistance,inductance&capacitance are found to be 40V,70V&100V respectively. What is the total voltage between between points A&B (Vab)? a)210V b)70V c)50V d)230V
What will hapen if we run generator below 47.6hz frequency?
What is mean by nominal voltage,Explain?.How much nominal voltage?.
What is negative phase sequence?
7 Answers Hindalco, Universal Associate,
Mention the disadvantages of low power factor? How can it be improved?
1. When do you use a VFD motor? 2. If the ceiling fan is on slow speed, does it consume less electricity? 3. If we want the fan to consume less electricity at low speed, what do we have to do? 4. What does “battery of 180 AMP HOUR” mean to you? 5. What does “battery of 180 AMP HOUR” mean to you? 6. If you don’t have coal, salt and copper, then how would you earth your connection temporarily at a camp site.?
6 Answers Asian Power, Bhel, Focus, Focus Energy, L&T,
please tell me when we start motor without load in star or delta connection whose current above condition,pl write formula
What are the steps for Testing of 6.6KV HT Panels?
what is meaning of phase angle in two phase.
how we can varying the speed of dc motor ?