how to select DG set for certain load?
Answers were Sorted based on User's Feedback
Answer / soumendasbiswas
Depending upon the total load and maximum demand of that
plant...
| Is This Answer Correct ? | 21 Yes | 7 No |
Answer / rajani
Actually DG size has to select depends on maximum demand
and considering base load and starting load and step load
base load = total maximum demand - loads which are
taking high loads at startign
starting load = if motor loads are DOL starts 6 times to
the Ifl will take at starting and soft
starters /VFD's will take 3 times to Ifl
step load = Whwn the main power supply is off
immidiently what are the load we can
switched ON through DG -called step load
(generally 40-60% of Dg load can be ON as
first step)
So our selected DG shopuld meet the step load and capable
to withstand startign loads
| Is This Answer Correct ? | 12 Yes | 5 No |
Answer / sheo
Suppose LOAD-1000 KW
So design load of Genset @ 80% inefficiency.
and power factor @80% in case of ( Failure of capacitor)because life of Capacitor and Gen set never equal to each other.
so 100% power back-up for 1000 KW load required DG 1000/0.64=1562.5 KVA
Recommended DG-1500 KVA
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / rakesh kumar sharma
generally the efficiency of the D.G.set is 80% because of
the power factor.so u have to add 20% on the entire
load.
| Is This Answer Correct ? | 6 Yes | 3 No |
Answer / sijish
DG normaly loads up to 80% of the full load rating,
First step.Calaculate the load in KW.
Consider the staring current of the Load.
The minimum Amps rating of the dg shoul be 4 Times the
Running current of the motor load
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / anil
Depending up on the total load to select the dg.for 5kw
load 10kva DG is suitable.
dg can be loaded for 80% of full load ,ie 8kw
calculating PF 6.4 kw can be loaded in 10kva dg.
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / m.prabhakar
Depending up on the total load to select the dg.For example
180KW load is there 200kva capacity genarator is sufficient.
| Is This Answer Correct ? | 23 Yes | 29 No |
WHY HUMMING SOUND OCCURED IN HT TRANSMMISSION LINES ?
purpose of breaker contact multiplication relay?
Different STANDARDS (BS, IS, IEC etc) gives different informations on CT specification. How they correspons w r t each other (i.e I mean to say BS provides "knee point voltage" but IS does not, then how can i select CT)
can we use breather in a SEALED power or distribution transfomer instead of injecting nitrogen.
typically in power distribution substation. 1- Any idea how would be the graph of capacitor bank consumption verses time through the day . 2- How is the switching ( on and off ) of the capacitor bank, per need?
what is the chemical name and formula of refrigarent R-134a.
what are the advantages and disadvantages of speed control of 3 phase induction motor by varying frequency explain with drawing
What is the "IS" for Rising Main?
whenewher three phase supply is given to induction motors revolving/rotating field is created & rotor rotates.When the three phase supply is given to three phase transformer then revolving,/rotating field is created or not? if not why?
Can you explain operating principle of Inverse Definite Minimum Time” (IDMT) relay
who invented electricity?
Explain difference between stand by earth fault and residual earth fault protection?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)