how to select DG set for certain load?

Answer Posted / rajani

Actually DG size has to select depends on maximum demand
and considering base load and starting load and step load

base load = total maximum demand - loads which are
taking high loads at startign

starting load = if motor loads are DOL starts 6 times to
the Ifl will take at starting and soft
starters /VFD's will take 3 times to Ifl
step load = Whwn the main power supply is off
immidiently what are the load we can
switched ON through DG -called step load
(generally 40-60% of Dg load can be ON as
first step)

So our selected DG shopuld meet the step load and capable
to withstand startign loads

Is This Answer Correct ?    12 Yes 5 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

What will be the fault current of any system when its generation is 10% of BASE generation( FUll Load )?Will is 10% or the same as full base calculation?

1430


what happen when power factor of 2 parallely operated transformer become equle?

1715


Is any AC drive(VFD) had a feature of DC injection braking? if available please mention the detail. i.e drive can supply braking torque when the motor in idle state.

1690


Actuality I have at home electrical panel with 220v 50hz, and I want to converter from there to 110v 60hz, to wiring on the half of my house. Also I like to keep another half of my house with the original 220v 50hz. What is the best and safety way to do?

1360


v/f drive basic princeple

2001






what is the size of ht cable of 33kv ht line and transformers ratings are 1 Mva and 5mva.please send formula also.

998


I want single line diagram for AMF & DG syncronizing panel

6632


what is the use of the circle diagram

4534


Is it good to short Neutral and Ground in the PLC or DCS main Power supply. Pls give YES or NO with reasons...? Simarpreet

2053


Explain the different regions in frequency response?

645


Why the moulded plug comes with domestic appliances instead of assembled plug like anchor, Vinay 5/15 A.

1572


What are the conditions to be satisfied for parallel operation of dc generators?

623


State Maximum Power Transfer theorem.

731


when generator short circuit condition, the current how dissipates. or at short circuit voltage not available then current how can flow?

1758


What is transformation ratio what it describes?

1173