What will hapen if we run generator below 47.6hz frequency?
Answers were Sorted based on User's Feedback
Answer / manoj sharma
Actually in india our all power system equipments are
designed to operate at 50 HZ. at lower frequency
performance of these component is poor in view of power,
life of equipment and safety. Motors will run slower,
transformers output will reduce, harmonics will increase in
power system. second thing when you run generator at
47.6HZ, your generator will loss its synchronism with the
grid.
| Is This Answer Correct ? | 52 Yes | 2 No |
Answer / a.mishra
According to Alternator voltage eqn., MAX.FLUX is inversly
proportional to FREQUENCY. If we reduce the frequency,then
max. flux will increase and the problem of core saturation
may happen. Other problem of iron losses will increase in
that alternator as well as the system equipments connected
to that source like Transformers,induction motors.
| Is This Answer Correct ? | 9 Yes | 1 No |
since all the equipments are designed to run at a frequency
of 50 Hz ( +/- 2 Hz) , low freuency will make the generator
to run at a speed less than the designed value thus
hindering the designed value of output.
| Is This Answer Correct ? | 8 Yes | 5 No |
Answer / vimal dixit
Generator will go out from synchronizm with grid.
| Is This Answer Correct ? | 5 Yes | 3 No |
Answer / piyush maghnani
A sthe generator frq reduced the inductive load will draw
high current which will result in poor power regulation.
the motors will not be running with standard speeds. there
will be increase in harmonics disturbances. your generator
will be overloaded & loose synchronisation with grid supply.
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / gunasekaran
turbine blade will be damaged frequency variation in india
only +-3% only.
| Is This Answer Correct ? | 2 Yes | 2 No |
Answer / vivekanand
Hi, do any legal standard for frequency tolerance
recommendation is there for the diesel fueled genset?
Do special criteria for frequency tolerance based on loading
is mentioned in any legal standard?
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / rahul
Nothing will happen because we can operate a frequency + or- 5%.
| Is This Answer Correct ? | 0 Yes | 5 No |
Answer / praveen420
In india we can't get power frequency less than 48.5hz.
Below this frequency power system violate.
If we run motor below this range than motor coil will be
burn due to more losses.
| Is This Answer Correct ? | 6 Yes | 25 No |
What does substation operator do in substation?
Why is the starting current high in dc motor?
How can we measure MVAR of a 3 phase transformer.....???
In a company the lines carrying 33KV but the load is below 10000Volts so we know that <11KV we can put 11KV lines but the lines are 33KV,..so how we can step down the voltage to 11KV with out erecting a substation
what is the difference between line voltage meter and relays
why select the 3 phase power supply system in electrical system.
PLEASE TELL ME ABOUT QUESTION PAPER OF UPCL ENTERENCE EXAM.
how to find the 2500 KVA transformer rated primary and secondary volt and current?
Why corona leads to production of Ozone and glow of the color VOILET?
Explain about Dubai electrical sysaem? Explain about Dubai drinking water system? Explain about Dubai Burj tallest building Electrical,Water.etc.. maintenance system?
what is the meaning of elecrical.
what is the ATS .And how it works.
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)