Answer / manoj sharma
Actually in india our all power system equipments are
designed to operate at 50 HZ. at lower frequency
performance of these component is poor in view of power,
life of equipment and safety. Motors will run slower,
transformers output will reduce, harmonics will increase in
power system. second thing when you run generator at
47.6HZ, your generator will loss its synchronism with the
grid.
Is This Answer Correct ? | 52 Yes | 2 No |
Answer / a.mishra
According to Alternator voltage eqn., MAX.FLUX is inversly
proportional to FREQUENCY. If we reduce the frequency,then
max. flux will increase and the problem of core saturation
may happen. Other problem of iron losses will increase in
that alternator as well as the system equipments connected
to that source like Transformers,induction motors.
Is This Answer Correct ? | 9 Yes | 1 No |
since all the equipments are designed to run at a frequency
of 50 Hz ( +/- 2 Hz) , low freuency will make the generator
to run at a speed less than the designed value thus
hindering the designed value of output.
Is This Answer Correct ? | 8 Yes | 5 No |
Answer / vimal dixit
Generator will go out from synchronizm with grid.
Is This Answer Correct ? | 5 Yes | 3 No |
Answer / piyush maghnani
A sthe generator frq reduced the inductive load will draw
high current which will result in poor power regulation.
the motors will not be running with standard speeds. there
will be increase in harmonics disturbances. your generator
will be overloaded & loose synchronisation with grid supply.
Is This Answer Correct ? | 2 Yes | 1 No |
Answer / gunasekaran
turbine blade will be damaged frequency variation in india
only +-3% only.
Is This Answer Correct ? | 2 Yes | 2 No |
Answer / vivekanand
Hi, do any legal standard for frequency tolerance
recommendation is there for the diesel fueled genset?
Do special criteria for frequency tolerance based on loading
is mentioned in any legal standard?
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / rahul
Nothing will happen because we can operate a frequency + or- 5%.
Is This Answer Correct ? | 0 Yes | 5 No |
Answer / praveen420
In india we can't get power frequency less than 48.5hz.
Below this frequency power system violate.
If we run motor below this range than motor coil will be
burn due to more losses.
Is This Answer Correct ? | 6 Yes | 25 No |
One Township having 850 house and each house load is 2.2KW single phase & 5HP 3 Phase motors of 10 Nos .Who can calculate 11 KV transformer capacity .dilip_bhasker@yahoo.co.in
aternator every parts and its working
WHY MOSTLY Rph IS USED FOR CONTROL CIRCUITS AUX. SUPPLY ?
why 15 kw motor winding resistance is low then 5 kw motor winding resistance?
what is meant by leading or lagging power factor?like in capacitor power factor is leading and in inductor power factor is lagging
which of the following can produce maximum induced voltage..... (a)1amp dc current (b)50amp dc current (c) 1amp 60 cycle ac current (d)1amp 490 cycle ac current.
What is the lockout relay
R u say ,that is there is any flux in your room.
Explain the advantages and disadvantages of thermal power plant?
How out of step protection relay works?
In a three phase transformer(delta/star connected)when i touch one end of the bulb in any one phase and other end to earth..will the bulb glow or not..if not why?..i'm touching the bulb in star connected side...
Squirrel cage induction motor has constant A slip B stator current C rotor resistance D speed at all load