What are the steps for Testing of 6.6KV HT Panels?

Answers were Sorted based on User's Feedback



What are the steps for Testing of 6.6KV HT Panels?..

Answer / rajendran

The type of panel is not mentioned in the question, how
ever following are the general testing steps....
1) Panel allignment
2) control wiring testing
3) Power ccircuit testing
4) Instument transformer testing
5) Beaker testing if any
6) Relays testing in the panel

Is This Answer Correct ?    62 Yes 8 No

What are the steps for Testing of 6.6KV HT Panels?..

Answer / rama raju (essar)

The following test are to be carried out for HT panels..

1) Functional test(In this test we can check control
wiring,power circuit wiring,Breaker Testing & loop test)
2) Relay Testing (all types of relays and power meters)
3) Meggering and hypertest.
4) polarity Test.
5) Primary Injection Testing.
6) Secondary injection Testing.
7) Breaker contactor resistance and timing.
8) MV Drop Test
9) Knee voltage Test depends upon CT.
10)Relay coil resistance & Pickup voltage and
Dropup voltage it depends upon ur relay.
11)IR value for surge Arrestor.

Is This Answer Correct ?    51 Yes 2 No

What are the steps for Testing of 6.6KV HT Panels?..

Answer / siva prasad

1. Check the panel alignment
2. Check the panel wiring as per scheme diagram
3. Check the continuity of Panel wiring
4. Check the meggar values of Bus bars and HT cable
5. Check the millivolt drop test of bus bar
6. Check the status of breaker
7. Primary and Secondary injection, Polarity tests for CT
and PT of bus bar
8. Set the time for fault current objection in relay
9. Knee voltage Test depends upon CT
10. Check DC supply permanent are temporary.
11. Physical inspection for satisfaction

Is This Answer Correct ?    18 Yes 3 No

What are the steps for Testing of 6.6KV HT Panels?..

Answer / c aaron franklin del

1. CT/PT Testing
2. Breaker Testing
3. Control wiring & Interpanel wiring
4. Relay Testing
5. Scheme Check
6. Bus PT and Buscoupler operation check
7. HT Busbar Megger and Hi-pot Test
8. Feeder by Feeder Commissioning

Is This Answer Correct ?    17 Yes 2 No

What are the steps for Testing of 6.6KV HT Panels?..

Answer / sheikh rashid

Berque Technologies Pvt Ltd is one of the manufacturer of
earthing compound and earthing electrodes for maintenance
free, corrosion free, eliminates the step and touch
potentials. long life, good conductivity.

www.berquetechnologies.com

berquetechnologies@gmail.com

Is This Answer Correct ?    9 Yes 3 No

Post New Answer

More Electrical Engineering Interview Questions

what will happen if we will not use commutater means if we will give dc to the windings in dc motor

1 Answers  


"TRANSFORMER MODELING AND ANALYSIS" MEANS WHAT AND WHICH TOPICS U READ IN THIS

0 Answers  


What is Procedure the procedure to select CT's & PT's in 66kV and above substation?

2 Answers   BEL,


what is the write prosidure of stringing of 8meter pcc pole.

0 Answers  


How to specific gravity of battery will check, i didnt saw any hydrometer. & say me how to dip into the battery what are the specifications are given in the hydrometer?

1 Answers  






y we use neutral,all r told its used to for closed path..k its a just used to closed path,in a transmission line y we put same conductor used n both phase and neutral..if we use less than phase conductor in neutral mean we ll reduce cost its right r wrong..if we use mean any problem occur in transmission line..

0 Answers   ME,


what current is taken from a double wound 500kva transformer

4 Answers  


Is it possible Z axis excess error alarm reflect in X axis if yes explain ?

0 Answers  


The speed of a dc motor can be controlled by the variation of 1. armature voltage. 2. field current. 3. armature circuit resistance. 4. angle of brush shift. Which of the statements given above are correct? (a) 1,2 and 3 (b) 2,3 and 4 (c) 1,3 and 4 (d) 1,2 and 4

1 Answers  


Whether the Dc motor Droping the power factor like AC motor if lot of motor running in factory is it necessary to connect capacitor bank

2 Answers  


can i use 2000/5A Clamp meter to measure HT cable

0 Answers   century, Engro,


why ups rated in kva

1 Answers   MRF,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)