What are the steps for Testing of 6.6KV HT Panels?
Answers were Sorted based on User's Feedback
Answer / rajendran
The type of panel is not mentioned in the question, how
ever following are the general testing steps....
1) Panel allignment
2) control wiring testing
3) Power ccircuit testing
4) Instument transformer testing
5) Beaker testing if any
6) Relays testing in the panel
| Is This Answer Correct ? | 62 Yes | 8 No |
Answer / rama raju (essar)
The following test are to be carried out for HT panels..
1) Functional test(In this test we can check control
wiring,power circuit wiring,Breaker Testing & loop test)
2) Relay Testing (all types of relays and power meters)
3) Meggering and hypertest.
4) polarity Test.
5) Primary Injection Testing.
6) Secondary injection Testing.
7) Breaker contactor resistance and timing.
8) MV Drop Test
9) Knee voltage Test depends upon CT.
10)Relay coil resistance & Pickup voltage and
Dropup voltage it depends upon ur relay.
11)IR value for surge Arrestor.
| Is This Answer Correct ? | 51 Yes | 2 No |
Answer / siva prasad
1. Check the panel alignment
2. Check the panel wiring as per scheme diagram
3. Check the continuity of Panel wiring
4. Check the meggar values of Bus bars and HT cable
5. Check the millivolt drop test of bus bar
6. Check the status of breaker
7. Primary and Secondary injection, Polarity tests for CT
and PT of bus bar
8. Set the time for fault current objection in relay
9. Knee voltage Test depends upon CT
10. Check DC supply permanent are temporary.
11. Physical inspection for satisfaction
| Is This Answer Correct ? | 18 Yes | 3 No |
Answer / c aaron franklin del
1. CT/PT Testing
2. Breaker Testing
3. Control wiring & Interpanel wiring
4. Relay Testing
5. Scheme Check
6. Bus PT and Buscoupler operation check
7. HT Busbar Megger and Hi-pot Test
8. Feeder by Feeder Commissioning
| Is This Answer Correct ? | 17 Yes | 2 No |
Answer / sheikh rashid
Berque Technologies Pvt Ltd is one of the manufacturer of
earthing compound and earthing electrodes for maintenance
free, corrosion free, eliminates the step and touch
potentials. long life, good conductivity.
www.berquetechnologies.com
berquetechnologies@gmail.com
| Is This Answer Correct ? | 9 Yes | 3 No |
What is the actual calculation for transformer short circuit test?.
what r the checklist while installing a 380 kva DG set
define the non synchoronism of synchoronous machine in general g or m??
what is grounding & what is the value of groumding rod 2.5m?
What is drain current of static relay?
what collector is used for 100kmph-120kmph tracion application?
what is the difference between metalhalide and mercury vapour lamp
Earth leakage relay basic knowledge principle
Hi Suppose we have a wye/wye transformer which is grounded at both sides,in this situation, do we have ay ground transformer? in other words, ground transformer can do any thing more (while we have nuetral wire in both sides)? As the last question, what about 3rd harmonic? we have two choices: first using wye/delta transformer + ground transformer and second using wye/wye earthed connection.in the former choice, we dont have 3rd harmoonic at the secondary side but what about Yn/yn conection? do we suffer from 3rd harmonic in the Yn/yn connection?
Why are the voltage levels in a powersystem are 11KV,33KV etc., why not 10KV,30KV?
What is 2P*0.5 sqmm screened copper cable and what is the use of it..?
State four criteria's for selection of site for nuclear power station.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)