Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


What are the steps for Testing of 6.6KV HT Panels?

Answers were Sorted based on User's Feedback



What are the steps for Testing of 6.6KV HT Panels?..

Answer / rajendran

The type of panel is not mentioned in the question, how
ever following are the general testing steps....
1) Panel allignment
2) control wiring testing
3) Power ccircuit testing
4) Instument transformer testing
5) Beaker testing if any
6) Relays testing in the panel

Is This Answer Correct ?    62 Yes 8 No

What are the steps for Testing of 6.6KV HT Panels?..

Answer / rama raju (essar)

The following test are to be carried out for HT panels..

1) Functional test(In this test we can check control
wiring,power circuit wiring,Breaker Testing & loop test)
2) Relay Testing (all types of relays and power meters)
3) Meggering and hypertest.
4) polarity Test.
5) Primary Injection Testing.
6) Secondary injection Testing.
7) Breaker contactor resistance and timing.
8) MV Drop Test
9) Knee voltage Test depends upon CT.
10)Relay coil resistance & Pickup voltage and
Dropup voltage it depends upon ur relay.
11)IR value for surge Arrestor.

Is This Answer Correct ?    51 Yes 2 No

What are the steps for Testing of 6.6KV HT Panels?..

Answer / siva prasad

1. Check the panel alignment
2. Check the panel wiring as per scheme diagram
3. Check the continuity of Panel wiring
4. Check the meggar values of Bus bars and HT cable
5. Check the millivolt drop test of bus bar
6. Check the status of breaker
7. Primary and Secondary injection, Polarity tests for CT
and PT of bus bar
8. Set the time for fault current objection in relay
9. Knee voltage Test depends upon CT
10. Check DC supply permanent are temporary.
11. Physical inspection for satisfaction

Is This Answer Correct ?    18 Yes 3 No

What are the steps for Testing of 6.6KV HT Panels?..

Answer / c aaron franklin del

1. CT/PT Testing
2. Breaker Testing
3. Control wiring & Interpanel wiring
4. Relay Testing
5. Scheme Check
6. Bus PT and Buscoupler operation check
7. HT Busbar Megger and Hi-pot Test
8. Feeder by Feeder Commissioning

Is This Answer Correct ?    17 Yes 2 No

What are the steps for Testing of 6.6KV HT Panels?..

Answer / sheikh rashid

Berque Technologies Pvt Ltd is one of the manufacturer of
earthing compound and earthing electrodes for maintenance
free, corrosion free, eliminates the step and touch
potentials. long life, good conductivity.

www.berquetechnologies.com

berquetechnologies@gmail.com

Is This Answer Correct ?    9 Yes 3 No

Post New Answer

More Electrical Engineering Interview Questions

What is the actual calculation for transformer short circuit test?.

0 Answers  


what r the checklist while installing a 380 kva DG set

0 Answers   Pepsi,


define the non synchoronism of synchoronous machine in general g or m??

0 Answers  


what is grounding & what is the value of groumding rod 2.5m?

3 Answers  


What is drain current of static relay?

1 Answers  


what collector is used for 100kmph-120kmph tracion application?

3 Answers   APTransco,


what is the difference between metalhalide and mercury vapour lamp

1 Answers  


Earth leakage relay basic knowledge principle

0 Answers   Radiant,


Hi Suppose we have a wye/wye transformer which is grounded at both sides,in this situation, do we have ay ground transformer? in other words, ground transformer can do any thing more (while we have nuetral wire in both sides)? As the last question, what about 3rd harmonic? we have two choices: first using wye/delta transformer + ground transformer and second using wye/wye earthed connection.in the former choice, we dont have 3rd harmoonic at the secondary side but what about Yn/yn conection? do we suffer from 3rd harmonic in the Yn/yn connection?

0 Answers  


Why are the voltage levels in a powersystem are 11KV,33KV etc., why not 10KV,30KV?

2 Answers  


What is 2P*0.5 sqmm screened copper cable and what is the use of it..?

1 Answers  


State four criteria's for selection of site for nuclear power station.

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)