Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


We have 800KW motor operating at 6600Volt,50 Hz
supply.During 1st startup it tripped on overcurrent
trip.It's FLA is 88 Amps.The K factor of Thermal overloaaad
was set on .94 initially.then we set at 0.97 and then it
started fine.i dont understand why it tripped first?What
are the protections which comes in picture during starting ?

Answers were Sorted based on User's Feedback



We have 800KW motor operating at 6600Volt,50 Hz supply.During 1st startup it tripped on overcurren..

Answer / prabhukumar

we all know that the starting current of motor is 5 times
more than of rated current.
for the starting current also some settings will be their
in that the starting current time may be less and the
starting time the heat will be their.

You just check it out and tell me.

prabhu.jsw@gmail.com

Is This Answer Correct ?    2 Yes 0 No

We have 800KW motor operating at 6600Volt,50 Hz supply.During 1st startup it tripped on overcurren..

Answer / ghani

It is right that starting current of this much big motor is
very high whihc varies as per data from 6 to 8 times, so if
the protection relay is of static or digital then there
must be a restraining setting for starting current with
time delay, so you can increas both values keeping the data
sheet of motor in view.

Is This Answer Correct ?    2 Yes 0 No

We have 800KW motor operating at 6600Volt,50 Hz supply.During 1st startup it tripped on overcurren..

Answer / kiran patil

You have increased thermal overload settings to .97 I think
because of load motor gets hot early and after incresing
the themal rating it will sustain.

Is This Answer Correct ?    5 Yes 5 No

We have 800KW motor operating at 6600Volt,50 Hz supply.During 1st startup it tripped on overcurren..

Answer / a.kossay

FIRST OF ALL THIS MOTOR MUST HAVE A SOFT STARTER BECAUSE
STARTING THIS MOTOR WILL DRAW A HUGE AMOUNT OF INRUSH
CURRENT + HUGE AMOUNT OF STARTING CURRENT, SO YOU HAVE TO
USE SOFT STARTER , AND YOU HAVE TO USE SMART RELAY BECAUSE
STARTING AND INRUSH CURRENT CONATINS A HUGE AMOUNT OF
HARMONIC CONTENTS SPECIALLY THIRD HARMONIC SO THIS SMART
RELAY WILL DETECT THE VALUE OF THE THIRD HARMONIC COMPONENT
AND IF IT EXCEEDS ITS VALUE IT WILL TRIP

Is This Answer Correct ?    2 Yes 2 No

We have 800KW motor operating at 6600Volt,50 Hz supply.During 1st startup it tripped on overcurren..

Answer / karthik_elec

u did'nt mention which type of starter you used,and which type of operation no load or full load, this type large motors always used soft starter only, auto transformer will not use, any way at the time of starting auto transformer only gradually increase the applied voltage , at that time the motor will take more amps to obtain the specific torque, due to that only, after obtain normal amps it will not take 88 amps also, because this is 100% efficiency current, below that only....

Is This Answer Correct ?    0 Yes 0 No

We have 800KW motor operating at 6600Volt,50 Hz supply.During 1st startup it tripped on overcurren..

Answer / parveen garg

I DO NOT KNOW ABOUT 6.6KV MOTORS & ALSO ABOUT K FACTOR.BUT
ACCORDING TO UR QUESTION IT LOOKS THAT MOTOR DRAW MORE
INSTANTANOUS CURRENT THAN ASSUMED BY THE CALCULATION & AT
THIS STARTING CURRENT OLR TRIPPED,WHEN U INCREASE THE
SETTING OF OLR.IT DO NOT TRIP.
FOR THE PROTECTION POINT OF VIEW ONE EXTRA CONTACTOR MAY BE
PROVIDE IN PARALLEL TO THE OPERATING CONACTOR WITH TIMER
WHICH WILL MADE OFF THE CONATCTOR(PROVIDED NEWLY)&ALSO THIS
CONTANCTOR WILL DRAW POWER FROM MAIN BUSBAR WITH EXTRA OLR .

Is This Answer Correct ?    0 Yes 5 No

Post New Answer

More Electrical Engineering Interview Questions

3 ph motor connected in star delta starter. when we start the motor it run in star but when in is going in delta it trips the main incoming supply. why?

3 Answers   Bajaj Hindusthan,


how much air gap in induction motor as per the Indian standards?

1 Answers   Coast Guard,


Motor,transformers,capacitor tubelight etc....

0 Answers  


difference between Ac and Dc mcb ????

0 Answers  


AL=0B9H,bl=75H, ADD AL,BL AL=____________? CF________? OF___________?

0 Answers  


In electrical what is earth(ground)connection, wht is the importance of it, why it is recomended to maitain below 3VAC between Neutral and earthspecially in PLC used machines?

0 Answers   Nissan,


plz explain the auot-reclosing circuit in electrical engineeing

0 Answers   BMC, KFC,


What are various power system instabilities and what are their effects on power system operation?

1 Answers  


why dc supply given to ac alternator rotor

3 Answers  


what are fluorescent lamps (fluorescent fixtures) & what are incandescen lamps (incandescents fixtures) ? differences between these two ?

1 Answers  


What is the basic principal, by which DC voltage level is increased more than the supplied AC voltage during conversion. As upto AC level it is contorrled by firing anlge but after maximum level how is it possible.Please clear picture. OR we have to supply the higher level AC?

0 Answers  


what is size of 3phase 4wire cable to be used for 11 ton ductable A.C and how to calculate cable size for different load

0 Answers   Tata Power,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)