Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


HOW TO CALCULATE THE CAPACITOR RANGE FOR LOAD FOR PF
IMPROVEMENT?
EXPLE:FOR 65 HP LOAD HOW TO CALCULATE CAPACITOR RANGE?

Answers were Sorted based on User's Feedback



HOW TO CALCULATE THE CAPACITOR RANGE FOR LOAD FOR PF IMPROVEMENT? EXPLE:FOR 65 HP LOAD HOW TO CAL..

Answer / deepakindi1

Boss what if u dont have the table?

let Cos(@1) be the present PF

@1=cos'(@1) (cos inverse)
let Cos(@2) be the desired PF
@2=cos'(@2) (cos inverse)


KVAR required= KW[ tan(@1)-tan(@2)]

for 65 Hp load
KW= 65HP*0.746 = 48.49KW
Considering Preent P.F=0.50
desired pf =0.99
ie cos(@1)=0.5
@1=cos'(0.5)=60
@2=cos'(.99)=8.1

kvar=48.49*[tan(60)-tan(8.1)]
=48.49*[1.732-.142]
=77.08

kvar=77.08

Is This Answer Correct ?    54 Yes 6 No

HOW TO CALCULATE THE CAPACITOR RANGE FOR LOAD FOR PF IMPROVEMENT? EXPLE:FOR 65 HP LOAD HOW TO CAL..

Answer / mahesh sonawane.

Capacitor range is actually given in Kvar, so to find that
range in kvar

As we know
Power factor = KW/KVA
for 65 Hp load
KW= 65HP*0.746 = 48.49KW
Considering Preent P.F=0.50
Target pf =0.99
Multiplying Factor by standard table= 1.59
Kvar= 48.49 KW * 1.59 = 77.09 Kvar

hence for the load of 65hp, capacitor range will be 77.09
Kvar.

Is This Answer Correct ?    73 Yes 27 No

HOW TO CALCULATE THE CAPACITOR RANGE FOR LOAD FOR PF IMPROVEMENT? EXPLE:FOR 65 HP LOAD HOW TO CAL..

Answer / bala123

please mention the existing powerfactor....

Is This Answer Correct ?    30 Yes 9 No

HOW TO CALCULATE THE CAPACITOR RANGE FOR LOAD FOR PF IMPROVEMENT? EXPLE:FOR 65 HP LOAD HOW TO CAL..

Answer / girish kumar samal, hindalco,h

as pf not giving ,taking pf 0.8
let pf of load =0.8
kw of load= 65 hp=65*0.746=48.5kw
kva =48.5/0.8=60.625kva
kvar =sqrt(60.625^2-48.5^2)=36.375kvar
if we want to improve pf to 0.95 then
improved kva= 48.5/0.95=51.052
improved kvar= sqrt(51.052^2-48.5^2)=15.9411
requard capacitor range = 36.375-15.94=20.43kvar.

Is This Answer Correct ?    26 Yes 12 No

HOW TO CALCULATE THE CAPACITOR RANGE FOR LOAD FOR PF IMPROVEMENT? EXPLE:FOR 65 HP LOAD HOW TO CAL..

Answer / chandru

In This case no other detail is given except the power
rating .

Therefore pf=( KW/KVA)
In order to get incentive and good power factor it is
required to maintain power factor above 0.95

So we take pf=0.95 and kw=(65*0.746)=48.49
Therefore KVA= 48.49/0.95 = 51.04

We know that KVAr= Squareroot( (KVA)^2-(KW)^2)


Therefore KVAr = sqrt(51.04^2-48.49^2)

=15.90 approx..


Capacitor required = 16KVAr.

Is This Answer Correct ?    11 Yes 11 No

HOW TO CALCULATE THE CAPACITOR RANGE FOR LOAD FOR PF IMPROVEMENT? EXPLE:FOR 65 HP LOAD HOW TO CAL..

Answer / manish deswal

let us conside current p.f = .8 & improved to .9,
Load = 65 hp =65 * 746 = 48.49 KW
KVA1 = 48.49/.8= 60.61

KVAR = Squareroot of [ square(60.61)-square(48.49)]=36.36
KVA2 = 48.49/.9= 53.88

KVAR = Squareroot of [ square(53.88)-square(48.49)]=23.49

Increased Capacitor bank capacity = 36.36-23.49 = 12.87 KVAR

Is This Answer Correct ?    3 Yes 3 No

HOW TO CALCULATE THE CAPACITOR RANGE FOR LOAD FOR PF IMPROVEMENT? EXPLE:FOR 65 HP LOAD HOW TO CAL..

Answer / sonu

Deepankandil why we are subtracting initial-final. littele
bit confusion. please throw some light on this issue.
because it will depand on lagging or leading?

Is This Answer Correct ?    3 Yes 6 No

HOW TO CALCULATE THE CAPACITOR RANGE FOR LOAD FOR PF IMPROVEMENT? EXPLE:FOR 65 HP LOAD HOW TO CAL..

Answer / ram lal

power factor is not mention so how can calculate ...........

Is This Answer Correct ?    4 Yes 7 No

HOW TO CALCULATE THE CAPACITOR RANGE FOR LOAD FOR PF IMPROVEMENT? EXPLE:FOR 65 HP LOAD HOW TO CAL..

Answer / naveen kumar mishra

first we should calculate the load(inductive or capacitive
or resistive).
in case of resistive load-----
in case of resistive load the, actual power factor will be
01(maximum),in this case the voltage will linior with
respecte to load current.
so tatal resistive load is(in example 65 hp),
so total load in kw = 65*0.746
=48.49.
As we know
Power factor = KW/KVA
for 65 Hp load(if pure resistive)

Considering Preent P.F=1
Target pf =0.99
Multiplying Factor by standard table= 1.56
Kvar= 48.49 KW * 1.56= 75.64

hence for the load of 65hp, capacitor range will be 75.64
Kvar.(in pure resistor).

Is This Answer Correct ?    2 Yes 5 No

HOW TO CALCULATE THE CAPACITOR RANGE FOR LOAD FOR PF IMPROVEMENT? EXPLE:FOR 65 HP LOAD HOW TO CAL..

Answer / sudhakara

MR. girish
What is meaning of sprt and that calculation

Is This Answer Correct ?    5 Yes 9 No

Post New Answer

More Electrical Engineering Interview Questions

how to calculate the over current rating of 3phase motor

2 Answers  


What is the d/f between DOL & star delta starter & automatic star delta starter?

23 Answers   ACC, Dalkia, Engineering, Indeco, NINL, Novotel, RMH Control Systems, Wipro,


how bucchos relay works in a transformer

8 Answers   Indeco,


What is the transfer function?

0 Answers  


when the PFR (POWER FACTOR REGULATOR)change a step to zero,one of the RCCB will triped off,is it the changing step of this PFR effect the RCCB?

2 Answers  


what is the relation bw voltage and F in capacitor?

3 Answers   TATA, Tata Motors,


Why we use Delta connection in the secondary side of a High Voltage transformer?

1 Answers  


Myself completed B.Tech ECE in private university but i am working as an testing and commissioning engineer in electrical field whether i am eligibility to apply electrical licence.

1 Answers  


How to select the proper VSD to operate high inertial load

0 Answers  


design a LV scheme for a 15 storied building?

0 Answers  


Which generation plant has instant start

2 Answers  


why in some trains in India Electric equipment such as Fans , tube light not work until locomotive or engine is attached to the train ??

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)