HOW TO CALCULATE THE CAPACITOR RANGE FOR LOAD FOR PF
IMPROVEMENT?
EXPLE:FOR 65 HP LOAD HOW TO CALCULATE CAPACITOR RANGE?
Answers were Sorted based on User's Feedback
Answer / deepakindi1
Boss what if u dont have the table?
let Cos(@1) be the present PF
@1=cos'(@1) (cos inverse)
let Cos(@2) be the desired PF
@2=cos'(@2) (cos inverse)
KVAR required= KW[ tan(@1)-tan(@2)]
for 65 Hp load
KW= 65HP*0.746 = 48.49KW
Considering Preent P.F=0.50
desired pf =0.99
ie cos(@1)=0.5
@1=cos'(0.5)=60
@2=cos'(.99)=8.1
kvar=48.49*[tan(60)-tan(8.1)]
=48.49*[1.732-.142]
=77.08
kvar=77.08
| Is This Answer Correct ? | 54 Yes | 6 No |
Answer / mahesh sonawane.
Capacitor range is actually given in Kvar, so to find that
range in kvar
As we know
Power factor = KW/KVA
for 65 Hp load
KW= 65HP*0.746 = 48.49KW
Considering Preent P.F=0.50
Target pf =0.99
Multiplying Factor by standard table= 1.59
Kvar= 48.49 KW * 1.59 = 77.09 Kvar
hence for the load of 65hp, capacitor range will be 77.09
Kvar.
| Is This Answer Correct ? | 73 Yes | 27 No |
Answer / girish kumar samal, hindalco,h
as pf not giving ,taking pf 0.8
let pf of load =0.8
kw of load= 65 hp=65*0.746=48.5kw
kva =48.5/0.8=60.625kva
kvar =sqrt(60.625^2-48.5^2)=36.375kvar
if we want to improve pf to 0.95 then
improved kva= 48.5/0.95=51.052
improved kvar= sqrt(51.052^2-48.5^2)=15.9411
requard capacitor range = 36.375-15.94=20.43kvar.
| Is This Answer Correct ? | 26 Yes | 12 No |
In This case no other detail is given except the power
rating .
Therefore pf=( KW/KVA)
In order to get incentive and good power factor it is
required to maintain power factor above 0.95
So we take pf=0.95 and kw=(65*0.746)=48.49
Therefore KVA= 48.49/0.95 = 51.04
We know that KVAr= Squareroot( (KVA)^2-(KW)^2)
Therefore KVAr = sqrt(51.04^2-48.49^2)
=15.90 approx..
Capacitor required = 16KVAr.
| Is This Answer Correct ? | 11 Yes | 11 No |
Answer / manish deswal
let us conside current p.f = .8 & improved to .9,
Load = 65 hp =65 * 746 = 48.49 KW
KVA1 = 48.49/.8= 60.61
KVAR = Squareroot of [ square(60.61)-square(48.49)]=36.36
KVA2 = 48.49/.9= 53.88
KVAR = Squareroot of [ square(53.88)-square(48.49)]=23.49
Increased Capacitor bank capacity = 36.36-23.49 = 12.87 KVAR
| Is This Answer Correct ? | 3 Yes | 3 No |
Answer / sonu
Deepankandil why we are subtracting initial-final. littele
bit confusion. please throw some light on this issue.
because it will depand on lagging or leading?
| Is This Answer Correct ? | 3 Yes | 6 No |
Answer / ram lal
power factor is not mention so how can calculate ...........
| Is This Answer Correct ? | 4 Yes | 7 No |
Answer / naveen kumar mishra
first we should calculate the load(inductive or capacitive
or resistive).
in case of resistive load-----
in case of resistive load the, actual power factor will be
01(maximum),in this case the voltage will linior with
respecte to load current.
so tatal resistive load is(in example 65 hp),
so total load in kw = 65*0.746
=48.49.
As we know
Power factor = KW/KVA
for 65 Hp load(if pure resistive)
Considering Preent P.F=1
Target pf =0.99
Multiplying Factor by standard table= 1.56
Kvar= 48.49 KW * 1.56= 75.64
hence for the load of 65hp, capacitor range will be 75.64
Kvar.(in pure resistor).
| Is This Answer Correct ? | 2 Yes | 5 No |
Answer / sudhakara
MR. girish
What is meaning of sprt and that calculation
| Is This Answer Correct ? | 5 Yes | 9 No |
how to calculate the over current rating of 3phase motor
What is the d/f between DOL & star delta starter & automatic star delta starter?
23 Answers ACC, Dalkia, Engineering, Indeco, NINL, Novotel, RMH Control Systems, Wipro,
how bucchos relay works in a transformer
What is the transfer function?
when the PFR (POWER FACTOR REGULATOR)change a step to zero,one of the RCCB will triped off,is it the changing step of this PFR effect the RCCB?
what is the relation bw voltage and F in capacitor?
Why we use Delta connection in the secondary side of a High Voltage transformer?
Myself completed B.Tech ECE in private university but i am working as an testing and commissioning engineer in electrical field whether i am eligibility to apply electrical licence.
How to select the proper VSD to operate high inertial load
design a LV scheme for a 15 storied building?
Which generation plant has instant start
why in some trains in India Electric equipment such as Fans , tube light not work until locomotive or engine is attached to the train ??
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)