what happan when ac power transmitted in unity power factor
Answers were Sorted based on User's Feedback
Answer / seraj
If it is made possible to deliver AC power with unity power
factor, it would be most economical for the company as
there would be minimum line losses. Total current would be
active only contributing for watts.
The system stability will however be poor, as there will be
no cussion for variation in load. Be disconnection of a
large load, the system will go over voltage and over
frequency before the mechanical system of the connected
generators respond to decrease the load of the turbines.
similarly if a large load is at once connected to the
system, there will be instantaneous mismatch between inflow
and outflow of power. This will cause the system to go
under voltage and under frequency before the mechanical
system responds.
If power factor is less than unity, in both of the above
cases, the surge will be absorbed by the inductive cussion
(just like a flywheel in mechanical system) and the sytem
would be more stable.
So we can say power factor adjustment is a compromise
between economy and the stability of the system.
| Is This Answer Correct ? | 21 Yes | 1 No |
Answer / balaji
it means that the supply is connected to the resistive
load.then reactive power becomes zero thus increase in the
system efficiency
| Is This Answer Correct ? | 11 Yes | 1 No |
Answer / rakesh ampuri
when ac power supply is done with unity pf then line loss
can be eleminated volage profile of recieving end become
flate there would not be need compensesion . proper
utilization ele. power can be improved ele. m/c performence
would b increase efficiency would also increase.
| Is This Answer Correct ? | 5 Yes | 3 No |
Answer / g.v.suresh kumar
SENDING END VILTAGE=RECEVINRG END VOLTAGE+POWER LOSSES
AT UNITY P.F THERE IS NO LOOSES SO
SENDING END POWER=RECEIVING END POWER
| Is This Answer Correct ? | 3 Yes | 2 No |
Answer / rabia
I consider the answer posted by Seraj to be correct. Most
of the other answers are also partially correct like the
ones posted by Manjeet and Rakesh Rampuri; one can not mark
them incorrect. But these answers do not address the
question "What happens". I suppose the question has been
asked with the thinking in mind that if unity power factor
is the ideal condition having minimum line losses; then why
is it not recommended to keep power factor exactly or very
close to unity?
We should not ask the opinion for the answer simply correct
or incorrect. We should rather ask "Is this a correct and
complete reply to the question?"
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / rathnam
As we know transmission lines are having high X/R ratio ,
nearly 13 for 400kv line and below that for low voltage
levels and more for high voltage levels, so even if we
transmit power at UPF at the sending end, we receive power
at lagging power factor (at high loads) and leading power
factor (at low or no load condition).
But it is possible to send power at unity power factor (at
generating stations)
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / rajendra
if sending end power at upf means only active power and reactive power is zero but at reciveing end side most are inductive load we need reactive power. so we never transmitted power at unity pf
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / h r jadhav
when we transmitte bulk power,from sending end to receiving
end ,the system naturaly demand potetial difference. there
shall be some what reactive power in grid otherwise grid
will be colapsed.so it seems imaginary.
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / karthik
i dnt think transmitting at unity pf. we can produce
voltage in that we normelly used to gen at 0.9 leading pf.
we couldnt go beyond this limit bcz of over rotor heating.
if we use this power for more number of motors and
lightings which is having low power factor the resultant
current drawn from the gen station ll be lagging only..
power factor purely depends on load only. at gen station we
can go upto alternator allowed range of leading pf..
if we consider this question as in the distribution station
if we try to deliver power at unity pf we may fail to judge
the load pf at each instant.. it may vary time to time..
even we further concentrate and done it we can minimise the
losses in line and billing of industry may reduce bcz of
UPF @ they r charged by KVAh tariffs...
| Is This Answer Correct ? | 0 Yes | 1 No |
what is the reqirred voltage in HT motor to get full RPM on no load test?
What are the types of class b amplifier?
How efficiency of thermal plant can be improved?
While starting a high capacity motor, it takes 6 times the full load current. Why it doesn't trip relay or CB's in that network?
What is the vector group of a transformer,how can it be found out?
why transformer cannot rotate though the princplebehind induction motor is similar to a transformer?
At which conditions a synchronous motor acts as a synchronous condenser?
We have 750KVA DG set, we want to introduce REF relay with 1250/1A,CL PS,Current transformers.The lead distance of 2.5mm copper flexible cable from CT to relay is around 5mtrs.We would like to know the knee point votage(VK) & IM calculion for CT's
why the undervoltage relay's interlock is used in earthswitch closing operation of the 400kV line scheme?
how to find 5 kilo meter long under ground 33 kv cable fault location if IR VALUE shows 0.05 M ohm @5000 volt.and cable fault locator shows some time fault distance 3 kilo meter ,3.7 kilo meter and some time 1 kilo meter? now how to find the fault location that where is leakage.
what is the simple meaning of harmonics?
why aggregate is placed all around substation ground.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)