HOW GENERATING END VOLTAGE LEVEL (6.6 KV/ 10.5 KV/ 11 KV/
13.5 KV) DECIDED IN POWER PLANT. ON WHAT FACTORS THE
GENERATING END VOLTAGE DECIDED, & WHAT IS THE CALCULATION
USED FOR THIS.
Answers were Sorted based on User's Feedback
Answer / raman jain
The generating end voltages are solely decided by the MVA
capacity of generator and cost. for example 250MVA
generator the generating voltage is 16.5 kV but when we go
for 500 MW generator it is 21 kV. If you try to make the
voltage level 16.5 kV for 500 MW generator , the size of
the generator becomes very much large abd very difficult to
transport and costly. on the other hand if you try to use
21 kV voltage generation for 250 MW generators the cost
will increase due the insulation level you are providing.
So it optimse by the designer .
Is This Answer Correct ? | 40 Yes | 9 No |
Answer / sumit
generating voltage depends on the power (kva or mva).if
power is incresed voltage will be increased also.by
increasing the voltage we can reduce the current &
conductor size .if cndctr size will be reduce cost reduce
also.
Is This Answer Correct ? | 6 Yes | 2 No |
Answer / vipul tayal
it is simply due to FORM FACTOR becoz form factor for a
pure sine wave is 1.11 and in all systems whether 1 phase
or 3 phase it will be a multiple of 1.11 and leads to
voltages like 11,6.6,10.5,11 kv) etc.
Is This Answer Correct ? | 24 Yes | 26 No |
A double circuit with dog conductor 66KV Transmission line from wind farm evacuation to feeding substation having capacity of 25MW for transmission. Can same transmission network be considered for further expansion of Power & how much in MW. If we need to expand next 10-15 MW more will there any augmentation is required in transmission network? Kindly reply asap.
What is In (current rating) shown on the MCCB? Is this full load which can withstand by the circuit breaker
what is the earth to neutral voltage(maximum and minimum) according to ieee standards
What is Negative Potential Bias
Why CT secondary should not be kept open?
I am getting above 60 V as open delta voltage against single phase unit ICT at tertiary delta formed and ICT getting trippped on NDR. ICT tested and found in order. PTs provided on tertiary are tested and in order. what may be the reason?
How to calculate the Efficiency of Chiller
what is differnce between oil transformer & dry type transformer ???????????
What is the formula that shows relationship between voltage and speed in an induction motor
How to decide and select the different earthing wire size for the different types of earthing
i have to install a HT panel, what components, I have to use in this and what will the diagram of that diagram,please tell me each and everything.
what is arc flash and what are the hazards involved