HOW GENERATING END VOLTAGE LEVEL (6.6 KV/ 10.5 KV/ 11 KV/
13.5 KV) DECIDED IN POWER PLANT. ON WHAT FACTORS THE
GENERATING END VOLTAGE DECIDED, & WHAT IS THE CALCULATION
USED FOR THIS.
Answers were Sorted based on User's Feedback
Answer / raman jain
The generating end voltages are solely decided by the MVA
capacity of generator and cost. for example 250MVA
generator the generating voltage is 16.5 kV but when we go
for 500 MW generator it is 21 kV. If you try to make the
voltage level 16.5 kV for 500 MW generator , the size of
the generator becomes very much large abd very difficult to
transport and costly. on the other hand if you try to use
21 kV voltage generation for 250 MW generators the cost
will increase due the insulation level you are providing.
So it optimse by the designer .
| Is This Answer Correct ? | 40 Yes | 9 No |
Answer / sumit
generating voltage depends on the power (kva or mva).if
power is incresed voltage will be increased also.by
increasing the voltage we can reduce the current &
conductor size .if cndctr size will be reduce cost reduce
also.
| Is This Answer Correct ? | 6 Yes | 2 No |
Answer / vipul tayal
it is simply due to FORM FACTOR becoz form factor for a
pure sine wave is 1.11 and in all systems whether 1 phase
or 3 phase it will be a multiple of 1.11 and leads to
voltages like 11,6.6,10.5,11 kv) etc.
| Is This Answer Correct ? | 24 Yes | 26 No |
What are the conditions for sustained oscillator or what is backhouse criterion?
If one lamp connect between two phases it will glow or not?
what does the word synchronous mean in 'synchronous machine'
what is the difference between potential Transformers and capacitive voltage transfoemers and where it is used?
what is allowable ac mixing in dc
Why did call copper as a electrical conductor?
what is purpose of using reactor in substations.
20 Answers Heavy Engineering Corporation Ltd HECL,
what is the earthing condition between earth & phase.
Ac generato how produce power I need for camplet defination
upto how much low RPM we will run the commercial motor which is run through VFD without any problem occurs in motor.Motor rating Duty is S1 & RPM is 1400.
could anybody able 2 send me jindal steels previous papers fr electrical steam....pls send 2 my id if possible....sirisha.shaik@gmail.com
Explain principle of Soft-starter & how its working???
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)