what is the function of buchhos rely in transformer
Answers were Sorted based on User's Feedback
Answer / ilononurb
Buchholz is a gas actuated relay which response if there is
any abnormality inside the transformer. Ex. If there a
incipient fault happens in transformer winding. arc causes
decomposition of oil that contains more hydrogen gas which
being light rise upward to bocholz relay. The gas is
collected to upper side of the relay. therby oil level drop
down in the B-relay that tilt the mercury switch that close
the alarm circuit.B-relay gives an alarm so that the
transformer can be disconected before the incipient fault
grows in to serious one.
Is This Answer Correct ? | 11 Yes | 0 No |
Answer / prashant
when there is any abnormal condition like
overloading,overcurrent,or any such things which increase
the tempreture of oil,,,then there will be gas bubble in
oil,,,,buchhos relay senses this abnormal condition,,,,
it will also give alarm signal if oil level is lower than
pre decide value,,,,,,,,,
Is This Answer Correct ? | 13 Yes | 4 No |
Answer / kjh
I agree with answer #2 .I want to add some, B-relay has two
stages one is connected in alarm circuit and the other is
connected wtih tripping circuit.It also tripping the
incomming C.B. of the transformer in case sewear fault.
Is This Answer Correct ? | 3 Yes | 1 No |
Answer / atti
Actually Ans # 04 option # B IS not the function of b-Rely.The
function of B-REly is the smoke detection not to check the
leakage.Allthough It has a oil leve detector .
Is This Answer Correct ? | 0 Yes | 0 No |
It is known as BUCHHOLZ relay.
A buchholz relay is operated by the accumulation of air bubbles within a transformer.
a) When a short circuit happens within the windings or within the contacts of the tap changer or any other shortings a localised heating takes place and gasses are liberated within the transformer.
b) When there is a leak in the transformer and the oil level drops or
c) The temp drops too low and the oil level falls below the required level.
These conditions trigger the float switch within the buchholz relay. The contacts are used for tripping the transformer or to on an alarm.
Is This Answer Correct ? | 0 Yes | 2 No |
what is the formula for computing cable tray size & capacity
If you don’t have coal, salt and copper, then how would you earth your connection temporarily at a campus site?
HOW CAN WE DECIDE THE SUPPLY VOLTAGE FOR MOTOR ACCORDING TO ITS RATING(IF ANYONE KNOWS GIVE IT WITH EXAMPLE AND ITS CALCULATIONS)
in a induction motor if we put capacitor across it will the power factor of the motor will improve? if yes how
what will happen at secondary side of transformer if i increase voltage at primary side?while V1*I1=V2*I2 will secondary voltage or current increase?
Can I parallel 1 MVA generator with 1kVA Generator? if V, F, Ph Seq and Ph angles are same
How we can calculate what type of supply we need for an example sometimes we take 11 KV and sometime 33KV from EB ?
what are the 6 terminals of the motor plss give me in details
What is the Total Power generation Capacity in India at present ??
20 Answers Bhel, College School Exams Tests, IBM, NTPC,
What should the transformer connection of a 11/220 kV step up and 66/11 kV step down transformer ?
Why current transformer is earthed??
if a single phase 3 hp submersible pump of Crompton Greaves is moving in reverse direction and sometimes it moves in rigth direction ,then what may be the cause....