HOW DOES ONE SELECT A TRANSFORMER PHASOR GROUP IE, WHETHER
A STAR-DELTA TR OR A STAR-STAR OR A DELTA-DELTA, ETC.
TRANSFORMER IS MORE SUITABLE FOR A PARTICULAR KIND OF LOAD
OR WORKING CONDITION???
Answers were Sorted based on User's Feedback
Answer / p v
A Delta to Star more practical. Neutral is available on
load side for Line to Neutral voltage.
The Delta on the supply side will filter the undesired 3rd
harmonic.
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / hareesh kumar s d
a delta 2 star transformer s used when there s a need of
neytral for examole industrial lighting. all conversions
depend on your load
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / gurucharan singh
Delta star is required only when distrbution system is
required or for higher voltage transmission line to cut
down high power tranformer insulation cost. Delta at
primary is preferred as it does not passes earth fault to
system at delta side. star with neutral is required for
detection earth fault curren, unbalanced loads, single
phase loads...star star or delta delta are considered
normally at same voltage ratio to lower down system fault
current at secondary side.
| Is This Answer Correct ? | 0 Yes | 0 No |
in three phase with neutral connection, what will happen,if the neutral is in open condition with single phase distribution panel
how is positive, negative, zero sequence is happen.. how is effect on 3 phase system
During Millivolt drop test current leads are applied in the extreme ends and voltage leads are given just before the current leads.. what will be the difference if voltage leads are given in the extreme ends? and why?
In EDO ACBs what is a purpose of closing coil and motor, what is the operation of these devices are they inetconnected. means if we give supply to motor and by BCS we charge Closing coil,what exact is operation is and how it charge a spring of ACB. Sir if anybody has an wiring diagram please send me the link to operate and EDO breaker.
What is the necessary and sufficient condition for stability.
Why the efficiency of generator is more than motor in swinburne's test
why normally Generator rating are between 11Kv to 22Kv?
in catridge heeter watts =110, 260 v , i checked in multimeeter meeter shows 50 ohms but oms law r=v square /w 260*260=67600, and 67600/110=614.5 ohms how to caluclate exact ohms in heetre s
what is mean by parallel operation of permanent magnet generators
What is the Maximum Power generation capacity of a Synchronus Machine ??
what should we do when the CT secodary gets open? how do we short circuit it? using tester or screw driver? not dangerous?
what is the function of potential transformer in s/s
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)