can u tell the difference between star - star transformer
and delta to delta transformer?
Answers were Sorted based on User's Feedback
Answer / dinesh
1. Star-Star(Y-Y) Connections.I gives line voltage √3 times
phase voltage. It is economical for small high voltage
transformers as the number of turns per phase and the amount
of insulation required is less. There is no phase shift
between primary and secondary voltages. The drawback is that
the neutral is unstable because of third harmonic component
in the exciting current.
2. Delta-Delta (Δ - Δ ) Connections. The arrangement is
generally used in systems which carry large currents on low
voltages and specially when continuity of service is to be
maintained even though one of the phases develops fault.
There is no phase displacement between primary and secondary
voltages. There is no distortion of flux as the third
harmonic component of magnetizing current can flow in the
delta connected primary windings without flowing in the line
wires. The conductor is required of smaller x-section as the
phase current is 1/√3 times of the line current. No
difficulty is experienced due to unbalancing of loads on the
secondary side. The disadvantages are that more insulation
is required and the voltage appearing between windings and
core will be equal to full line voltage in case of earth
fault on one phase.
(techie.dinesh@gmail.com)
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / mohd saaim
in star-star T/F primary windings are connected in star
connection and secondry winding sme as well
in delta-deltaT/F primary windings are connected in delta
connection and secondry winding sme as well
| Is This Answer Correct ? | 7 Yes | 9 No |
A 10 MVA, 66KV, 50Hz, Y-connected 3-phase alternator has synchronous reactance of 0.635 Ù. It is working at full load at 0.8 lagging p.f. condition. Find torque angle, neglect armature resistance.
In power transformer YnD0 Vector Group is possible or not? if possible, what will be the vector diagram and what are the conditions?
what is the advantage of NiCd battery over Lead acid battery?
hopkinson's test
what is DG synchronization panel plz explain the working!!!!!!!
12 Answers Kirloskar, Lanco, MPS Techologies, Sedemac,
i am an maintenance engineer. one distribution board have 5 feeder. recently its ELR trips frequently, but it take some times after trip( 10min,20min..)but 3 feeder no load. two feeder only loaded. i checked one feeder IR value all values are above 50Mohm.but B phase to Earth is only 9Mohm.any problem about low value
how does high earth to neutral voltage affects electronic circuit?
a solenoid of inductance 250mH and resistance 10ohm is connected to a battery. the time taken for the magnetic energy to reach 1/4th of its maximum value will be?
Excat meaning of burden in only one word?
3 Answers Bhel, DG Electricals,
for hipot test on 33kV busbar, we will test on 70 kV or 56kV, what is the acceptable leackage current?
What is the difference between Contactor and Circuit breaker ?
What is Synchronization of generator,where and how it is achieved.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)