how can we calculate that how much capacitor is needed for
a system to increase the pf?
Answers were Sorted based on User's Feedback
Answer / dinesh lokhande
A simple formula will help to co-orelate power factor, KW
load, and Kvar (i.e reactive power) required.
kvar = KW (Tan Qi - Tan Qd) where,
Qi = Cos inverse pfi = Initial power factor angle
Qd = Cos inverse pfd = Final power factor angle
After calculating Kvar we can select no of capacitors
required by looking at capacitor catalog.
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / iamdon
Before doing mathematical manupulaion,as expaines very well
by our answer poster Dinesh.
Lets understand this simple fact that the power factor
changes due to the variation in Reactive power only.With
the help of power factor, one can easily calculate Reactive
power(Q=P*tan(arc cos pf)). The difference between reactive
power at two power factors is supplied by capacitor.
Author :arbelectbit@yahoo.com
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / wasifkhan2010@yahoo.com
KVAR =KW(tanQ1 - tanQ2)
where
KW= load of installation
tanQ1 = current power factor
tanQ2= target power factor
in thisway we can calculate KVAR of capacitor that how much
KVAR have to be improved.
| Is This Answer Correct ? | 2 Yes | 0 No |
There is even no need to calculate. We have these charts which give the exact kvar required to be installed if we only know the load in KW and present pF and PF required.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / k.prakashchandra
You can use the formula KVA^2=KW^2 +KVAR^2
| Is This Answer Correct ? | 1 Yes | 3 No |
How to select a contactor? How many types of contactors are available
what is cogging and crawling
Mention the methods for starting an induction motor?
what happan when ac power transmitted in unity power factor
what will be the maximum winding temperature of 6.6kv HT motor 450kw, Full load current 49A. 50Hz Frequency.
Why we should use delta connection in primary and star connection in an distribution transformer, which converts 400v a.c. voltage to 33kv.
15 Answers ABC, Kirloskar, Sify,
I WANT BHEL PREVIOUS QUESTION
how DC motor operating in detail .pls any one guide me .iam not clear idea about that .thank u
Why star delta starter is preferred with induction motor?
What is hipot test procedure?
how work the differential protection relay in details?
what is the difference between watts and volts?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)