Answer / dinesh lokhande
A simple formula will help to co-orelate power factor, KW
load, and Kvar (i.e reactive power) required.
kvar = KW (Tan Qi - Tan Qd) where,
Qi = Cos inverse pfi = Initial power factor angle
Qd = Cos inverse pfd = Final power factor angle
After calculating Kvar we can select no of capacitors
required by looking at capacitor catalog.
Is This Answer Correct ? | 5 Yes | 0 No |
Answer / iamdon
Before doing mathematical manupulaion,as expaines very well
by our answer poster Dinesh.
Lets understand this simple fact that the power factor
changes due to the variation in Reactive power only.With
the help of power factor, one can easily calculate Reactive
power(Q=P*tan(arc cos pf)). The difference between reactive
power at two power factors is supplied by capacitor.
Author :arbelectbit@yahoo.com
Is This Answer Correct ? | 4 Yes | 0 No |
Answer / wasifkhan2010@yahoo.com
KVAR =KW(tanQ1 - tanQ2)
where
KW= load of installation
tanQ1 = current power factor
tanQ2= target power factor
in thisway we can calculate KVAR of capacitor that how much
KVAR have to be improved.
Is This Answer Correct ? | 2 Yes | 0 No |
There is even no need to calculate. We have these charts which give the exact kvar required to be installed if we only know the load in KW and present pF and PF required.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / k.prakashchandra
You can use the formula KVA^2=KW^2 +KVAR^2
Is This Answer Correct ? | 1 Yes | 3 No |
what is fundamental difference between voltage and current
what is iron loss?
What is the size of a 60 watt and 80 watt tubelight?
What is the Minimum winding resistance of motors ( small & big)? referance range
why two contacts(in series) are using in closing circuit
Explain with example of functional requirements of protection relay in terms reliability, selectivity, sensitivity
In the transformer, in which form we see the losses of transfprmer ?
What is the difference b/w fanuc alpha series 16i and 18i controller. what is stand for i
why we use the fuse in only one wire? althrough in ac current the current flows in both directions. why the neutral wire can be taken half the magnitude of phase wire while same current returns from neutral wire?
why neutral of 6.6 kv star connected sq. cage induction motor does not get earthed, though for earth fault protection it is must.
Please brief what is sinewave