Answer / dinesh lokhande
A simple formula will help to co-orelate power factor, KW
load, and Kvar (i.e reactive power) required.
kvar = KW (Tan Qi - Tan Qd) where,
Qi = Cos inverse pfi = Initial power factor angle
Qd = Cos inverse pfd = Final power factor angle
After calculating Kvar we can select no of capacitors
required by looking at capacitor catalog.
Is This Answer Correct ? | 5 Yes | 0 No |
Answer / iamdon
Before doing mathematical manupulaion,as expaines very well
by our answer poster Dinesh.
Lets understand this simple fact that the power factor
changes due to the variation in Reactive power only.With
the help of power factor, one can easily calculate Reactive
power(Q=P*tan(arc cos pf)). The difference between reactive
power at two power factors is supplied by capacitor.
Author :arbelectbit@yahoo.com
Is This Answer Correct ? | 4 Yes | 0 No |
Answer / wasifkhan2010@yahoo.com
KVAR =KW(tanQ1 - tanQ2)
where
KW= load of installation
tanQ1 = current power factor
tanQ2= target power factor
in thisway we can calculate KVAR of capacitor that how much
KVAR have to be improved.
Is This Answer Correct ? | 2 Yes | 0 No |
There is even no need to calculate. We have these charts which give the exact kvar required to be installed if we only know the load in KW and present pF and PF required.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / k.prakashchandra
You can use the formula KVA^2=KW^2 +KVAR^2
Is This Answer Correct ? | 1 Yes | 3 No |
what is synchronous speed.? if an induction motor is made to run at full load, then is this synch. speed too..?
how to select the automotive wire size by mathematical calculation. for xenon headlamp with ballast. the ballast given data voltage 10-17v,current permenant 6amp, run up phase is 15amp, peak at swicth on max 400micro sec is 40amp.the sum of cable resistance is 150mohm.please provide referenc document if any for relating the peak at switch on current,time & wire wire size
How to design CT for connected with Transformer OLTC operation? normally CT output design for 1A/5A range but during OLTC Tap position changing time how to function the CT?
Why we specify TNC switch with 1NO 1NC ,2NO 2NC ? how we get connection.?
how to find total current when kva is 30.4 given ? should we use root 3 (1.732) in the formula?
Multi-step core is used in transformer to: A) Increase the output B) Decrease the cost of core material C) Decrease the cost of copper D) Increase the efficiency
What is meant by positive and negative feedback?
What is the difference between solid grounding and impedance grounding?
The importance of resonant filters in converters?
all electricals questions
can we connect PARALLEL 2 D.G set with different rating?? How ? What is the requirement for this connections?
what is the difference between underreach and overreach.what is the advantage of using overreach instead of underreach.explain