how to calculate short circuit calculation of the transformer
by usuing the percentage impedence?
formula needed.
Answers were Sorted based on User's Feedback
Answer / elangovan kp
Isc (Shot circuit Current ) = Full load current of Tranformer / Impedance(%)
Ex: for 1000 KVA, 11/0.415 KV Transformer , Percentage Impedance - 6% :
Full load current of LV side of Transformer = 1000 * 1000 / ( 415 * 1.732)
= (1391 / 6) * 100
= 23187 Amps.
Is This Answer Correct ? | 4 Yes | 0 No |
why dc did not flows to earth?
What is the practical way to calculate the cable size for known ampere load?
if we keep frequency constant can we cal a synchronous generator as a dc generator
what is load balancing. what maximum load diffence is allowed between phases.
What is sensitivity of a measurement?
how to carry out Magnetizing Current Test on Distribution transformer and what purpose we are doing this test. why transformer rating in always in KVA ? what ispositive, negative, zero sequence impedence? How ElCB tripping if Neutral touch with ground Why AC & DC capacitor are use in UPS ? why motor rating in KW? how to syncronize two dg sets