how to calculate short circuit calculation of the transformer
by usuing the percentage impedence?
formula needed.
Answers were Sorted based on User's Feedback
Answer / elangovan kp
Isc (Shot circuit Current ) = Full load current of Tranformer / Impedance(%)
Ex: for 1000 KVA, 11/0.415 KV Transformer , Percentage Impedance - 6% :
Full load current of LV side of Transformer = 1000 * 1000 / ( 415 * 1.732)
= (1391 / 6) * 100
= 23187 Amps.
| Is This Answer Correct ? | 4 Yes | 0 No |
In which working principal temperature transmitter work.explain in detailed.
What is the basic rule for block diagram reduction technique?
what is the eight bit unit?
why commutator are not used in rectification purpose in power electronics?
A cable with concentric PE conductor must be used with frequency converter circuits what does its means.?
Where is servomechanism used?
I have finish diploma electronics and five years experience in electrical field in ht service how can i get c licensce or other electrical certificate
In Electrical 'Single Line Diagram' cable nomenclature shows "2 X 1C X 630sq.mm to be provided for one incomer. The question is how many cable to be proved for one Incomer.
The neutral&earth voltage is 0v.But we were connected the lighting load at the time ballast was failed.why?
One 15kw motor Why we used star delta feeder?why not used DOL please explain in details
3 Answers BMM Ispat, GSK, Pitti Laminations,
can anyone explain 11kV 3core cable megger,hi pot test procedure with connection details?
what is hysteresis loss?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)