How can w select the cable size for different rating load
& also waht r factors affecting the during selection of
cable?
Answers were Sorted based on User's Feedback
Answer / amit3456
There r so many factors for selection of cable:
1. full load of equipment or load.
2. Length of cable.
3. Derating factor.
4. Insulation level
| Is This Answer Correct ? | 34 Yes | 8 No |
cable size primarily depends on its voltage rating or kW
rating of load. From the kW rating, we can calculate the
current that should be carried by cable and the number of
runs required. we also have to calculate voltage drop
during starting and running in case of a motor load.
| Is This Answer Correct ? | 37 Yes | 18 No |
Answer / ranjan
For sizing of any feeder following are required:-
1. The load for which we are sizing
2.Dearating factor
3.pf
4.Starting voltage drop
5.running voltage drop
6.Spacing/Touching factor
7Effeciency
| Is This Answer Correct ? | 14 Yes | 3 No |
Answer / d.k.kakade
If cable size calulate on load in Amps.basis then please
give the formula, or advice cable size in 3.3kv 104Amps and
52 Amps,67 Amps, 33 Amps, and 15 Amps load.
Powe engrs.
| Is This Answer Correct ? | 10 Yes | 2 No |
Answer / eng.yousef
cable size depends on:
1)total connected load via cable.
2)lenght between the source and the load.
3)temprture
4)isulator type
5)load type
6)wiring place& type
| Is This Answer Correct ? | 16 Yes | 13 No |
Answer / ch.venkateswra rao
first we consider the type of load,voltage
rating,location,power etc will be known after that we
calculate the in put current and 20% extra value will be
added to that currnet and based on that current we refer
the cable manufacture booket and select the suitable size
of the cable
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / rathinam
My point of view, To find the cable size need to divide the
LOAD CURRENT by 3.
i.e:
Cable size= Load current (10A)/ 3
= 3.3
Now the answer is 3.3, But we don't have the 3.3 size of
cable. so we can choose next related size of cable, which
is 4 sq.mm.
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / manishhctm
A) Firstly we have to check for wht type of system we require the cable i.e LV, MV, HV AND EHV
B) then we have to calculate first: the rated current required by load on 3phase or 1phase system i.e
1) For 3-Phase System
KVA= KW/SQRT3*PF
2) For 1-Phase System
KVA=KW/PF
C) In companies there is feeder schedule for every type of cable w.r.t the amp.
Enjoy!
| Is This Answer Correct ? | 3 Yes | 5 No |
What is a current transformer?
for compensate 315mh inductance ,how many capaciance required?
whats the one main difference between UPS & inverter ? And electrical engineering & electronics engineering ?
How the annunciator works ? How to do its wiring
what do you mean by power factor ? in new view
brief notes on ammeters
Is 3 phase induction motor can work as a generator?? if so why & how??
What is differnce b/w tie breaker and bus coupler?
what is the diff between earth leakage relay and earth fault relay?
If the Supply voltage is increased by n times, the cross section of conducter will [increase/decrease] by ________ times ?
why voltage coil in wattmeter called as pressure coil why the pressure term is used in wattmeter?
what is the ohmic value of transformers
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)