when power transformer is flashed which gas is produce in
side?
Answers were Sorted based on User's Feedback
Answer / abbeer
Each of the fault result in thermal degradation of the oil
either alone or in combination with paper insulation. This
gives rise to the evaluation of various hydrocarbon gases,
hydrogen and oxides of carbon, in quantities depending on
the type of fault.
Heavy current arcing is characterized by the evolution of
significant quantities of hydrogen and acetylene (C2H2). If
the arcing also involves paper insulation, the oxide of
carbon will also be present.
Partial discharge usually results in evolution of hydrogen
and lower order hydrocarbons.
Localized heating or hot spot gives rise to methane and
ethane in appreciable amount.
Prolonged overloading or impaired heat transfer can cause
CO and CO2 to be generated due overheating paper
insulation.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / arunava
Hydrogen
O2
N2
Methane
CO
Ethane
CO2
Ethylene
Acetylene any of these.
| Is This Answer Correct ? | 2 Yes | 6 No |
how much value of resistance should connect to 15 kw, 6 pole 3 phase slip ring induction motor having RV-240, RA-42.
What are disadvantages of capacitor
How much load can give on 1600 kva transformer 11kv/440
What is partial discharge in power cable?
Maximum efficiency occurs in electrical machines is at i)Full load,ii)50% of full load,iii)Near full load,iv)None of these
what is the disadvantage of lagging power factor & why ?
Why dose an electric meter record KVA when there is no load on a 500 KVA transformer
why we did not mention ryb like byr in 3 phase
when i am going to take trail on a 3ph sq.i/m motor 5.5kw, i observed that RPM of the motor is very low as compared to the rated RPM and also it rotates in clockwise in first ON command,and anticlock wise in second ON command. finally i observed that on phase is no available . but iam not clear about, why the motor is rotates in both directions without any phase interchanging.pls answer to my question.
Simple calculation of improving power factor?
How can we deside Short Ckt level of electrical System,Breakers etc.please provide formula to find SC of HV side & LV side
how to increase senstivity of ct
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)