1.Can anybody explain Why starters are not used for motor
starting in industries?
2.
Answers were Sorted based on User's Feedback
i dont think. In all places ,motors are used to start by
starters only.
Is This Answer Correct ? | 6 Yes | 1 No |
Answer / dani jindal
who told you dat starters r not used in an industry. we
always go for a DOL (direct on line starter)which includes
type1 r type 2 protection co ordination n people ve above
replied i thnk about star delta starter which nt at all
depends upon the rating of the motor, as we knw the motor
drawas around 6 to 8 times the full load current during
starting if dat effects ur other equipment connected to
same line then go for star delta starter, if ur
distributiom Transformer is capable enough to withstand dat
surge inherited go for DOL starter.
Is This Answer Correct ? | 5 Yes | 0 No |
Answer / arun_sekar_1986
No for low rating of motors starters may not required.But
for higher rating starter is Mandatory. To reduce high
starting current starter are used while starting in step by
step it is used.
Is This Answer Correct ? | 3 Yes | 1 No |
Answer / suresh
In industries they normally use it.Ofcourse it may not be
required for motor of lower ratting say below 1kW or around
it.
Is This Answer Correct ? | 2 Yes | 1 No |
oh/...well frnd...u must have seen at any small industries.
they must have used be cos of cost.U can never find in any
standard company.it may happen if its very low rating motor
like up to 0.33kw.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / ravikumar.g
With out starter in the industries motor are not starting.
If the starte is having a safty for the motor.
If the single phases some times will start directly.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / dharmaraj
mostly lower rating not used for starter upto 1 kw more
then we should be used for starter
Is This Answer Correct ? | 0 Yes | 0 No |
Scott connection is used for A 3-phase to 2-phase conversion B to achieve higher effciency C to save copper D to reduce harmonics
what are the factors to be considered while design the breaker either HT or LT??
how does a submersible pump work..?
Explain the working principle of servomotor
20 Answers ABB, Bhel, FANUC, GE, Jindal Steel and Power, L&T, SIA, Steelco Gujarat Ltd,
how to calculate Transformer loss?
any body know about lighting arrestor. how to determine the height of lighting rod from top of bulding and how many area it cover.
why are you use the crgo core lamination in transformer
The D.C. spark test is applicable to single conductor cable & assemblies of insulated single conductor cables without insulation shield,metallic sheath or metalic armor?
why can tv operate at low voltage??
In india the power supply is always in multiple of 11, eg.220 V, 440 V... what is the reason?
11 Answers BSES, Electrical, L&T, PSIT,
what is the reason of current flow in nutral although load is balanced (three phase equal current)
how dia of wire and angles are calculated for overhead shielding wire to protect substation equipment from lightening strokes???