What will be the capcity of 3 phase DG set require for 25
KVA single phase lighting load?
Answers were Sorted based on User's Feedback
Answer / mrfbdr
Approximately 3-Ph 10kva Diesel generator will be enough
considering future loads too.
| Is This Answer Correct ? | 9 Yes | 6 No |
Answer / b.dhanasekaran
dg set we normally connect 75% of it,s capacity of dg, so
in lighting load single ph is 25 kva/3=8.33kva,
so nearest 3 phase dg is 15kva,
we can use 75% so 11.25 kva lighting load @ 3 phases you
can connect.
| Is This Answer Correct ? | 1 Yes | 3 No |
Answer / mel holmes
A 75kVA 3-phase generator is required to supply a 25kVA
load.
Consider a 75kVA, 400V, 3ph, 50Hz, 0.8pf DG set.
Full load current is 108A
A 25kVA 1ph load will require 108A.
| Is This Answer Correct ? | 0 Yes | 2 No |
Answer / rajiv garg
25kva dg also work but this will run 100% all time.
So u have to take some margin as DG mfg suggest as given
below.
for 25kva lighting load u have to use single phase
25/.8=31.25kva dg. available dg is 33kva
so u have to go for 33kva dg.
| Is This Answer Correct ? | 1 Yes | 4 No |
Answer / varma
can anyone explain more?
how can 10kva dg supplies load of 25kva(20kw)?
| Is This Answer Correct ? | 2 Yes | 6 No |
We can use 25 KVA Generator, but generator run as 100 %.
generator is over load.
pls we can use 25 KVA to 40 KVA Generator.
| Is This Answer Correct ? | 5 Yes | 10 No |
Answer / ashish
Here Your Load Is 25 KVA lighting load,& Incase Case Of
Lighting load The Load Diversity factor Factor Is Consider
as 1 so on Basis Of That We Must required 25 KVA 3Ph
generator ....but There May Be Possibiliry that All
Lighting Can Not Be ON.
| Is This Answer Correct ? | 1 Yes | 7 No |
The mechanical angle is electrical angle A always less than B greater than or equal to C equal to D less than or eaual to
why 6.6,11,22,33,66kv? what basis they have considered?
We have two Al.busbars each of size 125mm*10 mm connected in parallel.To increase the current rating ,can we connect third busbar of size 100mm*10mm in parallel to existing two busbars?In my opinion ,if we connect busbars of different sizes in parallel,then the busbar of lowest size will take much current.So this type of paralleling should be avoided .Am I correct?
how to size a diesel generator set?
What should be the setting of an earth fault relay.
EXPLAIN THE WORKING OF SERIES REACTOR IN HT CAPACITOR BANKS (FOR VOLTAGES & CURRENTS)
how many testing is necessary for 27 MVA transformer?
what is the reason of power development in synchronous generator due to saliency ?
what are the particle used along with silica gel in transformer breether,explain their functions.
flush point of transformer?
what is power factor? is it good or bad for a system? what will happen if power factor increase or decrease?
Generally we denote power in 'p',voltage in 'v'but why can't we denote current in 'c' instead of I.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)