What will be the capcity of 3 phase DG set require for 25
KVA single phase lighting load?
Answers were Sorted based on User's Feedback
Answer / mrfbdr
Approximately 3-Ph 10kva Diesel generator will be enough
considering future loads too.
| Is This Answer Correct ? | 9 Yes | 6 No |
Answer / b.dhanasekaran
dg set we normally connect 75% of it,s capacity of dg, so
in lighting load single ph is 25 kva/3=8.33kva,
so nearest 3 phase dg is 15kva,
we can use 75% so 11.25 kva lighting load @ 3 phases you
can connect.
| Is This Answer Correct ? | 1 Yes | 3 No |
Answer / mel holmes
A 75kVA 3-phase generator is required to supply a 25kVA
load.
Consider a 75kVA, 400V, 3ph, 50Hz, 0.8pf DG set.
Full load current is 108A
A 25kVA 1ph load will require 108A.
| Is This Answer Correct ? | 0 Yes | 2 No |
Answer / rajiv garg
25kva dg also work but this will run 100% all time.
So u have to take some margin as DG mfg suggest as given
below.
for 25kva lighting load u have to use single phase
25/.8=31.25kva dg. available dg is 33kva
so u have to go for 33kva dg.
| Is This Answer Correct ? | 1 Yes | 4 No |
Answer / varma
can anyone explain more?
how can 10kva dg supplies load of 25kva(20kw)?
| Is This Answer Correct ? | 2 Yes | 6 No |
We can use 25 KVA Generator, but generator run as 100 %.
generator is over load.
pls we can use 25 KVA to 40 KVA Generator.
| Is This Answer Correct ? | 5 Yes | 10 No |
Answer / ashish
Here Your Load Is 25 KVA lighting load,& Incase Case Of
Lighting load The Load Diversity factor Factor Is Consider
as 1 so on Basis Of That We Must required 25 KVA 3Ph
generator ....but There May Be Possibiliry that All
Lighting Can Not Be ON.
| Is This Answer Correct ? | 1 Yes | 7 No |
how to find number of run for transformer & alternator secondary side? give the example.
2 Answers Powergear, Regen Powertech,
how we can check that any motor is faulty may be single phase or three phase?
If we says that current is flow only when there is closed path & neutral work as a return path for the same. Then how circuit is closed in three phase as no neutral available ??
1 Answers Nimbus Harbor Facilities Management,
According to general circuit diagram of 1-Phase t/f , why the primary is not get short circuited ,even though the supply terminals both are directly connected through primary winding?
in transformer the unit of power is in kva why?
Explain about c.t?
Please brief what is sinewave
why we use carbon brush in exciter&genrator?
why Transformers power mentioned in KVA?. and why Generators and Motors power mentioned in KW?.
which one has maximum efficiency autotransformer or transformer?? and why??
What are the factors to be considered during the Synchronization?
If i=10+10sin314t then find the rms and average value of current with explain?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)