What is the resistance of human body from head to toe?
Answers were Sorted based on User's Feedback
Answer / rabi
Continue..
However, a resistance of 1000Ohm is considered between hand-
to-feet and also from hand-to hand-or one foot-to other
foot.
| Is This Answer Correct ? | 7 Yes | 2 No |
Answer / nitu
All the above answers are wrong answers the normal
resistance of human body is about 1500ohms & it varies from
person to person may oftan be less than 1500 ohms.When your
skin is moist, your body resistance could be as low as 300
ohms. Also, breaks in your skin at the point of contact
reduce your skin resistance to nearly zero.
| Is This Answer Correct ? | 5 Yes | 2 No |
Answer / sajin rajan
The resistance of human body varies from person to person.
the recommended value for ELCB tripping is 30 mA, more than
which can create a defibrillation in human heart.if u have
a single phase system (230v ac) then ur body resistance
should more than (230/30)*1000=7666 Ohms = 7.666KOHMS.
| Is This Answer Correct ? | 3 Yes | 3 No |
Answer / loveness chikwanje
Human body resistancewill be 1000 ohms
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / rabi
Value of body resistance including skin range from 500 to
3000Ohm.
| Is This Answer Correct ? | 2 Yes | 4 No |
Answer / kanika sharma
The electrical resistance of the human body depends on the condition of your skin at the time of measurement. If your skin is wet, you could have a resistance of only about 1100 Ohms. With dry skin, the amount is much higher at around 495,000 Ohms.
The electrical resistance of your internal body is much smaller at about 85 Ohms up to 575 Ohms.
| Is This Answer Correct ? | 1 Yes | 3 No |
Answer / durai
In wet conditions human body resistance will 1000 Ohms, Dry
condition human body resistance will be 1000000 ohms.
Durai.
| Is This Answer Correct ? | 1 Yes | 6 No |
why substation ratings are multiple of 11 means 11\33 kv substation
What is the safety factor is to be consider while selecting the switchgear and protection for electrical system
Anybody now how to claculate the Bescom power consumption?
We use ungrounded DC system (220V/110V) for control and protection system in substations etc. Suppose we have long 2 core DC cables running from our DCDB in control room to the load (length of around 2 to 3 km). Do we need to protect these long DC cables from earth leakages or not? If yes how?
what is transient enclosure vltage , very fast transients, very fast transient over voltages
Which fault is caused by lightening and thuderstorm a. Line to line fault b. Single line to ground fault c. Double line to ground fault
how can we check a fully charged battery?
How to setting the volume of RTCC panel AVR (11kv) controller
0 Answers CNF Automotive India,
what kind of material to be used after ngr unit? cu or GI
when we megger is not damaged when we are measuring very low resistance? high d.c. voltage is produced in megger so according to i=V/R. current will be high so what is the reason ?
How can calculate the efficency of the rectifier. input 240V AC, current 5 amps,P.F 0.98, Output is 54 V DC,62.6 A.
How to calculate transformer capacity requirement for a project site?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)