Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...

What will be the capcity of 3 phase DG set require for 25
KVA single phase lighting load?

Answer Posted / mel holmes

A 75kVA 3-phase generator is required to supply a 25kVA
load.
Consider a 75kVA, 400V, 3ph, 50Hz, 0.8pf DG set.

Full load current is 108A

A 25kVA 1ph load will require 108A.

Is This Answer Correct ?    0 Yes 2 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

Can anyone please provide me details of MCCB/Contactor/SFU rating calculations for a motor feeder..for example 50 kw.. not from type-2 cordination chart. i want manual calculations..

2581


Define availability (operational)?

1143


What are the basic component of a cro?

1238


where is the need for short circuit test for 3 see is required and why? can you explain in brief with application

1949


why ten delta testing is carried out on power transformer

1811


when generator short circuit condition, the current how dissipates. or at short circuit voltage not available then current how can flow?

2175


In general bus riser follows the bus section in SWGR. What are impacts if bus section follows bus riser?

1542


What will be the effect of circulating current in HT xlpe cable when both the armour ends are grounded. Will the termination fils after some time in case of 33 kv supply.

2065


can we synchronize star system generators with delta system generators?

2049


what can be the causes of capacitor start motor having a higher current that its actual

1965


how to estimate wiring ins roughing ins. and boxes

2395


Difference between field rheostat and armature rheostat.

1212


How we calculate DC inducation moter Amp? Sir pls give me formula......

1829


mccb service sittings be done?

1804


Why do we require transformer with less specific weight if supply frequency is increased?

1575