WHAT IS THE DIFFRENCE BETWEEN EARTHED AND UNEARTHED CABLE
(XLPE)?
Answers were Sorted based on User's Feedback
Answer / c.satheeshkumar
1.For earthed and un earthed XLPE cables, the IS 7098 part2
1985 does not give any difference in specification. The
insulation level for cable for unearthed system has to be
more. In simple statement the manufacturers states that 11
KV earthed cable is suitable for use in 6.6 KV unearthed
system.The process of manufacture of cable is same. The
size of cable will depend on current rating and voltage
level.
what IS specifies and I quote below:
" b) Voltage Grade (Uo/U)
1) Earthed System - 1.9/3.3 kV, 3.8/6.6 kV, 6.35/11 kV,
12.7/22 kV and 19/33 kV.
2) Unearthed System - 3.3/3.3 kV and 11/11 kV.
Note 1 - Cables of 6.35/11 kV grade (earthed system) are
suitable for use on 6.6/6.6 kV (unearthed system) also.
Is This Answer Correct ? | 44 Yes | 4 No |
Answer / ajay patel
Basically, Power Systems are defined as Earthed System,
Resistive Earthed or Un-Earthed System.
Hence, Cables are designed for Earthed & Unearthed Power
System. For Example, 11 kV (E) cable is used for 11 kV
Earthed System & 11 kv (UE) cables are uded for 11 kV not
effectively Earthed System. Insulation Thickness is more of
11 kV (UE) cables compare to 11kV (E) cables.
Is This Answer Correct ? | 40 Yes | 9 No |
Answer / ashim sarkar
I fully agree with the comments of Mr. C. Satheeshkumar.
Insulation level for Unearthed system is root over 3 times
the insulation level for Earthed system.
Earthed system - Insulation of 19 KV for 33 KV system
Unearthed system - Insulation of 33KV for 33 KV system
Is This Answer Correct ? | 14 Yes | 0 No |
Answer / karthikeyan.s
For an earthed power system, phase to phase voltage is
equal to line voltage and phase to earth voltage shall be
VL/1.732. But for an unearthed power system, phase to earth
voltage shall be equal to line voltage (VL). Hence for an
unearthed system the cable insultation should be very high
to withstand the abnormal voltage during fault.
That is why it has been widely said that 6.6kV unearthed
cable shall be used in 11kV earthed application, since the
insulation level for an unearthed cable is very high
compared to earthed cable.
Is This Answer Correct ? | 11 Yes | 0 No |
Answer / b. ramachandra rao
Cables of 6.35/11 kV grade (earthed system) are
suitable for use on 6.6/6.6 kV (unearthed system) also.
But is it true other way as well?
Can Cables of 6.6/6.6 kV grade (unearthed system) are
suitable for use on 6.35/11 kV (earthed system) also.
Is This Answer Correct ? | 4 Yes | 2 No |
Answer / kalyan chekuri
I have a system which had 400kV 100 MVA/11 kV 50 MVA/11kV 50
MVA transformer whose secondary is earthed with NGR of 300
Amps. I have bought 18000 Km of 11 kV earthed cable to lay
on 11 kV side of it. If the phase to earth voltage is 6.4kV
and root 3 times is the voltage expected to go up i.e 11kV,
why cant it be used if the power frequency withstood for
17kV for 5 minutes
Is This Answer Correct ? | 0 Yes | 0 No |
hey guys i scored 910 on GRE and 67 on TOEFL respectively.I have an aggregate of about 74%in my B tech.For which colleges should i apply for an MS program in electrical engineering.I am looking for colleges in NJ,SC,NC,GEORGIA, NY. Please reply with a good response.....
should Dy11 and Dy1 group can be operated in parallel??????
what is earthing
what is the difference between brushed alternator ,brushless alternator & permanent alternator ?
Define peak time.
why extension in transmission tower is made?
wat is the criteria we use the diff. relay ?
Why Utility Distribution System in India is mainly at 11 kV? Why not Utility go for 33 kV?
working of a diesel generator.
34 Answers ABC, AC, Cognizant, CTS, Directorate of Lighthouses and Lightships, KSL, Quippo, Shree Renuka Sugars, SRF, Svam Power, Tech Mahindra,
how can we avoid magnetostriction in transformer?describe the suitable methods.
a)In a 3-phase 4-wire circuit, a circuit breaker is selected to protect the circuit whose highest fault level is 6.6 MVA. Determine the required minimum breaking capacity in kA. (Note: Covert 3-phase power in terms of kA to find answer.) b)Using the below, determine the required minimum making capacity in kA as a “peak value”. Rate breaking capacity (Icn) ka: Icn<= 1.5 Factor = 1.41 1.5
How much current does a motor take in no load condition?