what is the difference betweem star connected motor & delta
connected motor?
Answers were Sorted based on User's Feedback
Answer / a. v. ramana reddy
A star connected motor takes less current compared to a
delta connected motor since the phase current is 1/sqrt3
times the line current, but torque developed by the motor is
affected, since starting current is heavy in order to reduce
the heavy inrush current we place a star delta
starter.....so tat starting current can be comparitively
small...the reason for shifting to delta connection(after
motor attains 80% of the rated speed)is the power output of
the motor wil be 3 times the output wen it is connected in
star.....it doesn;t mean tat the m/c 3 times more efficient
than star connected one..but correspondingly the power drawn
by the motor also increases.........
comments r welcome....
| Is This Answer Correct ? | 175 Yes | 40 No |
Answer / s.r.ramalingam
PHASE CURRENT AND PHASE VOLTAGE IS THE MAJOR DIFFERENCE...
IN STAR CONNECTION,
PHASE CURRENT IS EQUAL TO THE LINE CURRENT.
THT IS,
I LINE = I PHASE
BUT,
V LINE = ROOT 3* V PHASE
IN DELTA CONNECTION,
PHASE VOLTAGE IS EQUAL TO THE LINE VOLTAGE.
THAT IS,
V LINE = V PHASE
BUT,
I LINE = ROOT 3* I PHASE.
| Is This Answer Correct ? | 109 Yes | 12 No |
In star connection motor is taking low current and produce
high torque and in delta connection motor is taking high
current and low torque.to start the motor from stand still
condition we requeired high torque so first motor should in
star connection and then it should have conti. with delta
connection.
| Is This Answer Correct ? | 183 Yes | 149 No |
In star connected motors power consumption will be less
compared to delta connected motors.
| Is This Answer Correct ? | 45 Yes | 22 No |
Answer / krishna
star connected motor gives a more torque compare to delta
connected.
| Is This Answer Correct ? | 60 Yes | 45 No |
Answer / k.mohan kumar
In star connection motor is taking low current and produce
high torque.
In delta connection motor is taking high current and
produce low torque.
In star more power consumption.
In delta less power consumption.
In star connection phase current is equal to line current.
In delta connection phase voltage is equal to line voltage.
In star line voltage is equal to 1.732*phase voltage.
In delta line current is equal to 1.732*phase current.
| Is This Answer Correct ? | 23 Yes | 10 No |
Answer / lovepreet
Bt how it is possible that in star connected motor takes less current nd produce more starting torque than delta connected motor while speed is same????
| Is This Answer Correct ? | 6 Yes | 1 No |
Answer / arthur
Delta connection has a high starting torque which is not our interest since it comes with extremely high current. To reduce this current which only occurs during starting,we use star with relatively low current and low torque.
| Is This Answer Correct ? | 5 Yes | 1 No |
Answer / yasirfraz
STAR CONNECED MOTER TAKE LESS CURRENTAND GNRAT LESS
TOURQE,IN DELTA CONDETION TAKE MORE CURRENT AND DEVLOPED
MORE TOURQ.
| Is This Answer Correct ? | 19 Yes | 17 No |
Answer / pallav
star connected motor voltage is high then delta connected motor. then voltage is increases then current decreases. means delta connected motor speed is high as compare to star connected motor
| Is This Answer Correct ? | 0 Yes | 1 No |
If auto trip is operated, can you close the breaker.
why 3 phase motors are preferable over single phase motors ?
In Electrical 'Single Line Diagram' cable nomenclature shows "2 X 1C X 630sq.mm to be provided for one incomer. The question is how many cable to be proved for one Incomer.
what is the significance of cabability curve of alternator
what transformer we used normally and upto which kva?
When we use air circuit breaker, it has O/L protection ,time delay SC protection, Instataneous SC protection & ground fault protection. They all have some setting range. But what is the suitable/allowable setting for the above protection which will be safe for the equipment? For example-O/L protection setting have a range of (0.4,0.45,0.5,0.55,0.6,0.65,0.7,0.8,0.9,1.0)xIn Time delay SC protection have a range of (1.25,1.5,2,3,4,6,8,10,12)xIn Time delay setting is 0.02,0.1,0.2,0.3,0.4 Instataneous setting is fixed to 20xIn Gound fault setting is given 100A,300A,600A,900A,1200A This setting are for 2500A ACB. So what will be the basic allowable setting for the above protection? is there any formulae to calculate this<
What are the diferences between ELCB and RCCB
Explain Power factor in simple words
Is it possible to protect 3phase overload and earth fault of the 3phase system using two CT's.
Is it true that in the 3 phase transformer, the limbs of the core are at 45 dgrees to each other. if true, why?
what is working of no & nc.
What is the difference between Droop vs Isoch Control?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)