What is the amount of no load current of 630 kVA tranformer
voltage ratio 11kV/440V ?
Answers were Sorted based on User's Feedback
Answer / satish babu
The No load current depends on the Core grade used in the
transformer laminations & the flux density at which it
operates,
a) 1-2% in high quality materials
b) 5- 10% in economy grades,
| Is This Answer Correct ? | 24 Yes | 1 No |
Answer / dennis
No Load current will depend on Core Grade, Core Thickness,
Flux Density, Frequency and the quality of workmanship (how
good are gaps closed).
| Is This Answer Correct ? | 15 Yes | 0 No |
Answer / j.prabhakaran
The amount of no load current can be only calculated if we
knows the value of core loss of transformer and capacitance
current across the circuit.....
| Is This Answer Correct ? | 7 Yes | 1 No |
Answer / dr. alaa baiumy abdel azim &a
frist we will get the rated current of the winding
I = 630 * 1000 / CUBIC ROOT OF 3 * 11 * 1000
I = 33 Amper
I NO LOAD = 0.5% OF I RATED
NO LOAD CURRENT = O.OO5 * 33
= 165 m A
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / nyi lwin
transformer no load current 630 KVA....1 hour unite
question
| Is This Answer Correct ? | 0 Yes | 4 No |
Answer / mash
it depend on the turns of coil what is the Gage of wire...
| Is This Answer Correct ? | 0 Yes | 4 No |
Answer / amit sonmale
Ctually No load Curent Depend on Transfarmer eficiancy To
take load.Depend on his Copper loss.
| Is This Answer Correct ? | 1 Yes | 6 No |
Answer / gaurav srivastava
it is a tricky question....
u know that when transformer is at no load. the secondry
windings are open...so that there is no current flow at
secondry winding...
and for primery winding we calcute these value from OPEN
CIRCUIT TEST.
that is mentioned in all books thats have transformer
chapeter...
GAURAV SRIVASTAVA (UNITED COLLEGE OF ENGINEERING AND
RESEARCH) ALLAHABAD
| Is This Answer Correct ? | 3 Yes | 10 No |
what happen ehen synchronisation is done at below rated speed
A Generator is in running condition and Rotor earth fault alarm is coming.How to check on line(i.e in running condition) whether there is actual earth fault in rotor or not.
What are the Safety measures in central chiller plant? Explain them?
22 Answers Carrier, CPIC, HSL, JLL,
what is the difference between switchgear and circuit breakers and is there any difference between outdoor and indoor switchgear and circuit breakers , and how would you differentiate between switch yard and substation and grid station . thanks
How to calculate the cross section area for a 350 m cable, motor power is 26 kw???
What is the function of isolater
4 Answers Getco, Gland Pharma,
what is ic 01,ic 06 ?is it types of cooling?
How much water ( Kilo Liters) a submercible pump of 35 HP can lift from Borewell of 6" and 900 feet dip.
what is dyn 11
what is FET
how to decide the capacity of accl
How we detect the leakage current of 11 KV H.T. motors and waht is the maximim limit?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)