Answer / parth belani
The efficiency can be found by finding the losses. because,
efficiency= output/input = output/(output+losses)
Now there are mainly two types of losses in a transformer.
1) Iron losses which can be found by the "No load" test.
2) Copper losses which can be found by the "Full load"
or "Short Circuit" test.
by knowing the losses, and the output rating of the
transformer, we can find efficiency.
| Is This Answer Correct ? | 8 Yes | 0 No |
Answer / sunil kumar
The efficiency of transformer can be predetermined by open
circuit and short circuit test.in case of open circuit test
the high voltage side is kept open and rated low voltage is
applied to the primary(for ex:25mva,230(p)/115(s),230 kept
open and115v applied to secondary winding and the
wattmeter accounts for iron losses.in case of shortciruit
test the lv winding is shorted and the hv winding is
energised because in order to limit current drawn from the
source and the wattmeter accounts for full load copper
losses.in addition to above tests sumpners test or back to
backtest is most accurate where two identical transformers
are loaded simultaneously it gives the actual temp rise in
the transformers wherwe as oc and sc tests can't.
| Is This Answer Correct ? | 2 Yes | 5 No |
Transformer cores are laminated in order to A simplify its construction B minimize eddy current loss C reduce cost D reduce hysterisis loss
What happen if we apply square wave or traiangular waveform voltage to the transformer primary winding instead of sinusoidal wave?
why we use condenser in the thermal power plant, althrough the same vapour will be again heated
What are the technical reasons for soaking transformers for various times before allowing them to pick load after a fault ?
what are adantages of OC and SC test over the load test?
What is the latest generation of circuit breakers called?
What is the out put of a CT? How the ratio is decided ?
what is vector surge & vector shift? we have 25.3 MW(11kv) generator & 11kv/132kv transformer, connected with with 132 kv grid.vector surge relay is tripping frequentaly.what is permissible maximum limit for this.
How to synchronization will be done between two DGs ?
what is the reason for using 110 volt and 60 hertz ac supply for using power distribution in America?
why it is so called as xlpe(cross linked poly ethyline) cable?
different between electrical and electronics Engineering????
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)