What is ment by KVAR and what are the advantage&dis-
advantages of KVAR
Answers were Sorted based on User's Feedback
Answer / mohd. karim
KVAR - Reactive Power
It's Present only in Inductive load, i.e. X-mer, Motor, X-
mission Line..etc
And This power is required for generating Magnetic field in
inductive load.
Here, i want to explain some formuls
KVA = Sqrt((kw)^2 + (Kvar)^2)
Where , KVA = Apparant Power
KW= Actual Power
Kvar= Reactive Power
PF=KW/Kva = KW/(KW+Kvar) = COS$
1. If the value of kvar is more. it means PF is Less.
2. If the value of Kvar is zero. It means Unity PF (PF=1).
it means Apparant Power is Maxi. and over KW Loading is
Maxi.
--> Practically PF is not Unity (PF=1). its near about One.
For Reducing Kvar Demand We install Capacitor In Ckt.
Dis-Advantage (If Kvar is More)
1. less KW Loading(Low load Allow) in system.
2.Power Factor will Poor.
3.High current in system so Conductor & Cable size increase.
4.Electricity bill will more (Money Loss)
| Is This Answer Correct ? | 33 Yes | 2 No |
Answer / pradeep
kvar is nothing but the reactive power which is injected by
the capacitor bank. this power is similar to the real power
which generated by the generating unit.
by using capacitor bank we reduce losses like transmission
loss etc.,
advantages:
1. easy to convert the 2-phase into 3-phase.
2. reduce the losses and increase the efficiency.
3. it ensure upto 200Mhz
disadvantages:
1. it will inject the more power when bank is not necessary.
2. expensive due to connecting the capacitor bank.
| Is This Answer Correct ? | 6 Yes | 18 No |
what difference between tapping -15% to +5 % and -5% to +15% tap. & how can define HV turns on maximun & minimum tap of power transformer.
While DG is on Load? we can start the capacitor bank?
Differance between ELCB and RCCB?
WHY KVAR IMPORTANT WHEN ANY PLANT IS RUNNING ON IT'S OWN POWER PLANT?
what is the formula for hv test for cable and circuit breaker..????
why are we using resistor in NGR ?
how to claculate earth strip size for 1500kVA transformer for neutral and body
3phase motor can be used as a Prime mover for alternator.
A 60w bulb & a room heater are connected in series.if 60 w bulb is replaced by 100w then what will be the effect on heater out & why?
Why power factor does not occur in DG set ?
resitance in ac=1.6*resistance in dc
Can any horizontally mounted motor be used as vertical?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)