What is ment by KVAR and what are the advantage&dis-
advantages of KVAR
Answers were Sorted based on User's Feedback
Answer / mohd. karim
KVAR - Reactive Power
It's Present only in Inductive load, i.e. X-mer, Motor, X-
mission Line..etc
And This power is required for generating Magnetic field in
inductive load.
Here, i want to explain some formuls
KVA = Sqrt((kw)^2 + (Kvar)^2)
Where , KVA = Apparant Power
KW= Actual Power
Kvar= Reactive Power
PF=KW/Kva = KW/(KW+Kvar) = COS$
1. If the value of kvar is more. it means PF is Less.
2. If the value of Kvar is zero. It means Unity PF (PF=1).
it means Apparant Power is Maxi. and over KW Loading is
Maxi.
--> Practically PF is not Unity (PF=1). its near about One.
For Reducing Kvar Demand We install Capacitor In Ckt.
Dis-Advantage (If Kvar is More)
1. less KW Loading(Low load Allow) in system.
2.Power Factor will Poor.
3.High current in system so Conductor & Cable size increase.
4.Electricity bill will more (Money Loss)
| Is This Answer Correct ? | 33 Yes | 2 No |
Answer / pradeep
kvar is nothing but the reactive power which is injected by
the capacitor bank. this power is similar to the real power
which generated by the generating unit.
by using capacitor bank we reduce losses like transmission
loss etc.,
advantages:
1. easy to convert the 2-phase into 3-phase.
2. reduce the losses and increase the efficiency.
3. it ensure upto 200Mhz
disadvantages:
1. it will inject the more power when bank is not necessary.
2. expensive due to connecting the capacitor bank.
| Is This Answer Correct ? | 6 Yes | 18 No |
if we use a normal natural thundering; than approx how much amount of electricity we generate?
Why is ignitor used in sodium vapour lamp
generator means
who to select a swicth fuse unit......?
give 5 differences between relay and contactor
how to calaculate the amps in transformer ?
We have 800KW motor operating at 6600Volt,50 Hz supply.During 1st startup it tripped on overcurrent trip.It's FLA is 88 Amps.The K factor of Thermal overloaaad was set on .94 initially.then we set at 0.97 and then it started fine.i dont understand why it tripped first?What are the protections which comes in picture during starting ?
What are the main advantages of generalized error co-efficients?
I have CNC Turning lathe,while doing electrical preventive maintenance what should I do & please brief me plan & shedule for the same.
please write motor, transformer, Generator setting, fault level calculation of Tr.etc
in case dc we mark as + ve & -ve..but in case a.c. we mark as ph&N...Y LIKE PLZ TELL ME
what is efficient motors and how it is different from normal induction motors
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)