In a 11000/440 V transformer, when any one phase of 11 KV
supply fails (ie., single phasing), what happens to the
secondary voltage and why?
Answers were Sorted based on User's Feedback
Answer / haiderali
When any one phase of 11 KV supply fails, phase voltage
will be half of the normal voltage in two phases of
secondary side while only one phase will deliver full
voltage (i.e. 440/sq.root3)with respect to neutral.
Is This Answer Correct ? | 31 Yes | 8 No |
Answer / vikas
when one ohase of transformer will fail...then transformer
will behave as open delta connection and give the output
reduced to 53%of the actual output....
Is This Answer Correct ? | 15 Yes | 2 No |
Answer / pravesh
if the 11kv /440 v supply if one phase fails then at that
time open delta circuit takes place in that case the for
which the equipment connected to the secondary side , 440v
side will work below their efficiency
Is This Answer Correct ? | 9 Yes | 14 No |
Approach of a cooling tower is the difference between temperatures of what factors?
What is meant by locking of rotor in synchronous motor? Explain me locking in detail?
Can any one provide the inspection procedure of MIMIC for VFD panel? Details: If someone wants to have a mimic in the VFD panel what are inputs considered for the mimic(like on,off,trip) whether we are able to add speed variation in the mimic(if so how can we get) and what are the parameters to be checked in the MIMIC during inspection?
how to select battery for 15 KVA UPS with formula
how much current in live 11 Kv distribution Line?
What is Diff. btw Cat-5 & Cat-6 Network Cables???
what is transformer?
Pleasd Tell Me..... In Generating Stations Why The Generation Of ELECTRICITY Is In 3 Phase Form?? OR In Generating Station Why We Generates The ELECTRICITY In The 3 Phase?? Why Not In The 4 Phase, 5 Phase Or 6 Phase Form??
How to calculate per unit impedance of transformer?
why compound generator is used in generating station?
What are documents to be required for export of the material?
What is the GI Earth Flat Size recomended for 33KV 2000KVA Distribution Transformer