In a 11000/440 V transformer, when any one phase of 11 KV
supply fails (ie., single phasing), what happens to the
secondary voltage and why?
Answers were Sorted based on User's Feedback
Answer / haiderali
When any one phase of 11 KV supply fails, phase voltage
will be half of the normal voltage in two phases of
secondary side while only one phase will deliver full
voltage (i.e. 440/sq.root3)with respect to neutral.
| Is This Answer Correct ? | 31 Yes | 8 No |
Answer / vikas
when one ohase of transformer will fail...then transformer
will behave as open delta connection and give the output
reduced to 53%of the actual output....
| Is This Answer Correct ? | 15 Yes | 2 No |
Answer / pravesh
if the 11kv /440 v supply if one phase fails then at that
time open delta circuit takes place in that case the for
which the equipment connected to the secondary side , 440v
side will work below their efficiency
| Is This Answer Correct ? | 9 Yes | 14 No |
ELECTRICAL MACHINE
At no load the PF of an alternator -Zero -Zero Lagging -Zero leading -None of the above
what will be the minimum megger value for 132 Kv (earthed) potential transformer
what do you mean by every IC 74 first digit.why are you using this no.why not using another no.
meter ratio is 100/5 CT ratio is 125/5, when the ratios changes i.e., CT ratio is 125/5 meter ratio is 100/5 what is the MF in boths conditions?
how percentage impedence effect on the size of the power transformer?
which loses are in transformer .explane each loses
We have 2 Nos. Transformer with the capacity of 2000KVA and 1250 KVA and currently using only one 2000KVA T/R during operational hours while non- operational hous 1250 KVA T/R also used to reduce T & D losses. Similarly, 2 capacitor bank of 500KVAR and 300 KVAR also installed to balance reactive power. Now problem is around 1000 KW load PF is not maintaning 0.99 as 350 KVAR capacitor is in healty condtion. Now the PF is maintain 0.95 to 0.96.
a transformer runs by electro-induction principle like all motors.then why dosen't it rotate just like any other motor
electrical
How to select a cable size for particular load?
0 Answers Amit Enterprises, Takasago Engineering, Techno Electric and Engineering,
Two bulbs of 100w and 40w respectively connected in series across a 230v supply which bulb will glow bright and why?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)