how we can save the power ?
suppose the electricity board gives 11 kw , but the
machine require only 8 kw means how we can save the exese energy

Answers were Sorted based on User's Feedback



how we can save the power ? suppose the electricity board gives 11 kw , but the machine require ..

Answer / pillay

The EB gives 11 kw means that is the max load you can put on
EB but you only pay for what you use so ther is no saving
unless you find ways to reduce the 8 kw of the machine.

Is This Answer Correct ?    1 Yes 0 No

how we can save the power ? suppose the electricity board gives 11 kw , but the machine require ..

Answer / wareagle

That is not possible. You maybe saying that the EB is
providing 11 kva and you need 8 kw. If so, then the power
factor of the load is 8/11 = 0.72. You can add 7 kvar of
capacitors to improve the PF to 0.99 an you would reduce
the load to 8 kw.

Is This Answer Correct ?    2 Yes 2 No

Post New Answer

More Electrical Engineering Interview Questions

How to calculate CT ratio for 11KV 1500KVA Transformer 500KVA MD and 1400KVA connected load ? Note:- As per MSEB(Maharastra state electricity Board)

1 Answers  


a 120 60 watt incandescent lamp has to be operated from 50 c/sec 1 phase ac supply. in order to do this a circuit element has to be connect in series with the lamp. which one of the following sries element is preferable.

1 Answers   SSC,


how to calaculate the amps in transformer ?

2 Answers  


what will be the motor terminal box connection arrangement (star or delta). on what basis it decided?

3 Answers  


How earthing of switchgear system to be done.

0 Answers   KSEB, L&T, Siemens,






difference between slippring induction motor and Generator?

1 Answers  


why induction motor take more current when motor start time and this current take for 1 hours when motor is start.

2 Answers  


how will reduce the voltage. if 12volt/250ma transformer toreduce 6 volt

0 Answers  


what is the difference between line & phase current in star delta connection motor?

2 Answers  


How does a tertiary winding filter harmonic(espcially 3rd one) from entering into load system?

0 Answers  


what is purpose of manual bybass in ups

3 Answers  


I have a small system with two motors that are running on 380 vac, 60 hz. These motors are expensive and I usally get them from Brazil. I am adding another motor to the system, but I want to purchase a 480 vac, 60 hz motor to use. It will be on a VFD that is rated fro 380 thru 480. Is this posible and will I have to use a larger motor and derate it?

0 Answers   US Electrofused Minerals,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)