how we can save the power ?
suppose the electricity board gives 11 kw , but the
machine require only 8 kw means how we can save the exese energy
Answers were Sorted based on User's Feedback
Answer / wareagle
That is not possible. You maybe saying that the EB is
providing 11 kva and you need 8 kw. If so, then the power
factor of the load is 8/11 = 0.72. You can add 7 kvar of
capacitors to improve the PF to 0.99 an you would reduce
the load to 8 kw.
Is This Answer Correct ? | 2 Yes | 2 No |
How to calculate CT ratio for 11KV 1500KVA Transformer 500KVA MD and 1400KVA connected load ? Note:- As per MSEB(Maharastra state electricity Board)
a 120 60 watt incandescent lamp has to be operated from 50 c/sec 1 phase ac supply. in order to do this a circuit element has to be connect in series with the lamp. which one of the following sries element is preferable.
how to calaculate the amps in transformer ?
what will be the motor terminal box connection arrangement (star or delta). on what basis it decided?
How earthing of switchgear system to be done.
difference between slippring induction motor and Generator?
why induction motor take more current when motor start time and this current take for 1 hours when motor is start.
how will reduce the voltage. if 12volt/250ma transformer toreduce 6 volt
what is the difference between line & phase current in star delta connection motor?
How does a tertiary winding filter harmonic(espcially 3rd one) from entering into load system?
what is purpose of manual bybass in ups
I have a small system with two motors that are running on 380 vac, 60 hz. These motors are expensive and I usally get them from Brazil. I am adding another motor to the system, but I want to purchase a 480 vac, 60 hz motor to use. It will be on a VFD that is rated fro 380 thru 480. Is this posible and will I have to use a larger motor and derate it?
0 Answers US Electrofused Minerals,