why mccb is not tripping when phase & neutral terminal are
interched ?
Answers were Sorted based on User's Feedback
Answer / v.selvakumar
mccb is a protect device,whenever short circuit fault
happens ,it will isolate healthy system from faulty system
due to heavy .changing the phase neutral in circuit not a
fault,it will work as normal circuit.
Is This Answer Correct ? | 10 Yes | 1 No |
Answer / pratheesh
What Mr.Rajan mantioned is not correct. Core Balance CT,
CBCT (Also called as Zero CT)is used for detecting the
earth fault current.
MCCB is a protective device by sensing the load current. By
interchanging the Phase and Neutral wires, there will not
be any difference in the load current.
So MCCB will trip on higher load current such as overload
or short circuit.
Is This Answer Correct ? | 10 Yes | 1 No |
Answer / rajan.l
Shunt Trip Coil is not connected with a core balanced CT
Is This Answer Correct ? | 5 Yes | 3 No |
Answer / basayya hiremath
mccb is protectve divise over load and shotr ckt,dipinding
ka rating of the mccb supose 25 ka mcc using this mccb
withastading ofthe current up to 25ka .u whant when phase
and nutrul shotr downstrim side using the mcb this will
trip u what to nutrul protect or earth fualt u can use cbct
incomming side of the mccb with shunt coil in side the mccb
and defending opan idmt curv
Is This Answer Correct ? | 0 Yes | 0 No |
what is the function of buchhos rely in transformer
can a rotating machine give the DC output without commutator? if yes, how? if no, why?
The temperature rise in the sys, which leads to ….. a) Increases stress& length b) increases stress but decreases length c) Decreases stress & increase length d) decrease stress & length
1 Answers Engineers India Limited,
If we impress a dc voltage of 230 V on an unloaded 230 V, 50 Hz transformer it wi A give high secondary voltage B burn out C give secondary voltage as per K D none of these
what is the difference between VARIAC,AUTO TRANSFORMER,DIMMERSTAT.
Mention the methods for starting an induction motor?
why we use 110vac in overhead crains? why not 220v, 24v
What causal system?
what is the diffrence between resistive , inductive and capactive load please explain with exmpels?
What is third harmonic?what is the effect of it?
which is best ac or dc
How to synchoronize the generator (with gcb,GT) to grid????? ????? from Grid iam getting power (rated 400kv/20kv) through GT and its goes to UAT.,,ST.,, now my generator(rated 20kv ) ready.,, now iam closing my GCB.,, in GT iam suddenly giving 20kv on that Gt.,, what will happend