why mccb is not tripping when phase & neutral terminal are
interched ?
Answers were Sorted based on User's Feedback
Answer / v.selvakumar
mccb is a protect device,whenever short circuit fault
happens ,it will isolate healthy system from faulty system
due to heavy .changing the phase neutral in circuit not a
fault,it will work as normal circuit.
| Is This Answer Correct ? | 10 Yes | 1 No |
Answer / pratheesh
What Mr.Rajan mantioned is not correct. Core Balance CT,
CBCT (Also called as Zero CT)is used for detecting the
earth fault current.
MCCB is a protective device by sensing the load current. By
interchanging the Phase and Neutral wires, there will not
be any difference in the load current.
So MCCB will trip on higher load current such as overload
or short circuit.
| Is This Answer Correct ? | 10 Yes | 1 No |
Answer / rajan.l
Shunt Trip Coil is not connected with a core balanced CT
| Is This Answer Correct ? | 5 Yes | 3 No |
Answer / basayya hiremath
mccb is protectve divise over load and shotr ckt,dipinding
ka rating of the mccb supose 25 ka mcc using this mccb
withastading ofthe current up to 25ka .u whant when phase
and nutrul shotr downstrim side using the mcb this will
trip u what to nutrul protect or earth fualt u can use cbct
incomming side of the mccb with shunt coil in side the mccb
and defending opan idmt curv
| Is This Answer Correct ? | 0 Yes | 0 No |
11kv alternator commissioning test?
In single phase ac ups supply when current is measured with tong tester neutral current is found more than phase current.What is the reason?
How to take of Transformer oil Break down voltage test?
why HT armoured cable does not glanding
how do we calculate length of starting time and repeated starting of a direct online starter?
Why stand-by earth fault relay and restricted earth fault relays are connected between neutral and ground in transformer?
In MEP Services what are parts of STP and what are there function?
what will happen if a part of primary winding of a transformer is accidentally short-circuited?
What is the function of earthfault relay?
18 Answers MultiTech, Tech Mahindra,
When we change the tap position of 10MVA transformer it suddenly tripped with Out of step indication and also with Static differential relay indication, Transformer Bucholz relay indn and Low oil level indication. Before 1 week the same problem occured by changing the tap position. but at that time only oltc bucholz relay activated. After testing the TxR Relay team & PET team cant find any solid reason. The values are ok also. So plz answer wat's the reason for this incident? anybody plz help.
What is the diffrence between PS & metering CT (5p20,0.5 etc.)? Why in PS class CT only Vk is given ? Is PS class CT is more accurate than metering CT?
What will happen if we give DC supply to AC motor?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)