In A.C systems, fuse is placed in phase-in order to
disconnect the circuit during faulty condition.
But, what is the reason for putting "LINK" in neutral
istead of connecting through (same) wire.
Answers were Sorted based on User's Feedback
Answer / s k sudhakar
TO ATTEND ANY PROBLEM IN A PARTICULAR SYSTEM, THAT SYSTEM
IS REQUIRED TO BE ISOLATED. IF LINK IS NOT PROVIDED COMLETE
ISOLATION IS NOT POSSIBLE.
| Is This Answer Correct ? | 7 Yes | 2 No |
Answer / suseendran
Phase will have voltage(potential) whereas neutral is
potential free.
Imagine
if a phase conductor(wire) gets cut and touches the earth.
Fault current flows thro it and fuses are required to
isolate the circuit.
Whereas if a neutral conductor gets cut and touches the
earth. Nothing will happen since it is potential free. So
fuses are not required.(Links are cheaper than fuses)
| Is This Answer Correct ? | 1 Yes | 2 No |
Answer / mritunjay singh yadav
neutral link is provided in neutral to protect the current
transformer from being the open circuit in faulty condition.
| Is This Answer Correct ? | 0 Yes | 4 No |
The coulomb is a unit of:(a) Energy(b) Voltage(c) Power(d) Quantity of electricity
how do you reduce the skin effect
why we use condenser in the thermal power plant, althrough the same vapour will be again heated
What happens when generator is running with leading power factor on it say -0.96. what are the effects of it on alternator and the other generators operating in parallel to it.
In an ACB shunt trip coil and undervoltage coil operated normally( breaker open and charged). But closing coil not operating untill manually discharge and recharging. Any help.
What is meant by a linear circuit and what is a non- linear circuit?
Compare salient pole and Hndrical rotor machines.
what is formula in determining the size of Circuit Breaker for transformer with the following specifications. 7 units of 1600 volts (primary) and 400 volts (secondary). Both Primary and Secondary will have a circuit breaker which is SF6. What should be the Switchgear Main Breaker Size anf the sizes of each brances Circuit Breaker for Primary.
i am confused about generator. i have generator of 380 KVA that is 304 KW by that formula KW=KVA*0.8... then by this formula I=KW/V*1.732*0.8 the amperes are 528.673. so that is the load which i put on one phase of generator or this is total 3 phase load on Generator.......
How to test the thyresitor or SCR by multmeter?
Why does the power consumed is always constant even if a fan speed is altered?
what r the checklist while installing a 380 kva DG set
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)