In A.C systems, fuse is placed in phase-in order to
disconnect the circuit during faulty condition.
But, what is the reason for putting "LINK" in neutral
istead of connecting through (same) wire.
Answers were Sorted based on User's Feedback
Answer / s k sudhakar
TO ATTEND ANY PROBLEM IN A PARTICULAR SYSTEM, THAT SYSTEM
IS REQUIRED TO BE ISOLATED. IF LINK IS NOT PROVIDED COMLETE
ISOLATION IS NOT POSSIBLE.
Is This Answer Correct ? | 7 Yes | 2 No |
Answer / suseendran
Phase will have voltage(potential) whereas neutral is
potential free.
Imagine
if a phase conductor(wire) gets cut and touches the earth.
Fault current flows thro it and fuses are required to
isolate the circuit.
Whereas if a neutral conductor gets cut and touches the
earth. Nothing will happen since it is potential free. So
fuses are not required.(Links are cheaper than fuses)
Is This Answer Correct ? | 1 Yes | 2 No |
Answer / mritunjay singh yadav
neutral link is provided in neutral to protect the current
transformer from being the open circuit in faulty condition.
Is This Answer Correct ? | 0 Yes | 4 No |
where we use zero sequence current transformer or core balancing ct.
how do you choose the cable size as per amps rating & the voltage drop for the same.
WHAT IS DIFFERENCE BETWEEN MANUAL CONTROL AND MAGNETIC CONTROL AND STATE ITS ADVANTAGE /DISADVANTAGE
how to modify DOL control panel into Delta Y connection?
transformer is connected with 50hz and 60hz at same rating which will give more output on same rating
What is the difference between an ELCB and a RCD?
Is a contactor (or master relay) required between incoming lines and a VFD? The question goes to safety. If a contactor were used before the VFD and an e-stop engaged then the motor will coast to a stop (i.e. VFD loses power) instead of stopping much faster if the VFD braking fucntion were used. It would make more sense to keep power on the VFD.
what is humming noise and wha is the reason to develop humming noise in a mv pannel ?
voltage of a ckt is measured by volt meter having an input impedence camparable with the out put impedance of the ckt Eror caused is 1. Gross Error 2. Errors due to lloading effect
what is the clearances between phease to phease & phease to earth in 400 kv transmission line?
We have AC-transformer 110/13.8kv,40MVA.If DC-Voltage=110kv is applied in its primary what will happen?
Define non-touching loop.