How to calculate KW what is the formula for KW.
Answers were Sorted based on User's Feedback
Answer / pankaj kumar vig
IN SINGLE PHASE
POWER= V*I*COS $/1000 KW
IN THREE PHASE
POWER=1.732* V*I*COS $/1000 KW
| Is This Answer Correct ? | 53 Yes | 9 No |
Answer / dnyaneshwar
for single phase
KW= V*I*COS $
FOR THREE PHASE
KW= 1.73*V*I*COS$
IF U HAVE TO FIND ONLY WATTS THEN DIVIDE THE ANS. BY 1000
| Is This Answer Correct ? | 26 Yes | 8 No |
Answer / manik chatterjee
KW=V*I*COS$ THAT IS INCASE OF AC.
KW=V*I THAT IS IN CASE OF DC.
| Is This Answer Correct ? | 16 Yes | 0 No |
Answer / manik chatterje
IN CASE OF SINGLE PHASE AC
KW=V*I*COS$
In case of three phase
KW=1.732*V*I*COS$
In case of DC
KW=V*I
| Is This Answer Correct ? | 17 Yes | 1 No |
Answer / uzair ahmed
To calculate value in KW, just multiply the power with 1000.
becoz unit of power is Watt (W)
so if we convert it to KW then we mutiply it with 1000.
again if we convert KW into Mega Watt. we shall multiply
the value which is in KW to 1000.
and for low values that is maga watt to KW or KW to W, we
shall divide that values with 1000.
| Is This Answer Correct ? | 12 Yes | 0 No |
Answer / poka
3 phase
________watts___________
voltsxampsxPFx1.732
1 Phase
___________watts______________
voltsxampsxPF
| Is This Answer Correct ? | 10 Yes | 2 No |
Answer / edgar
KILOWATT (kW) = VOLTS x AMPERES x POWER FACTOR x 1.73
---------------------------------------
1000
| Is This Answer Correct ? | 16 Yes | 10 No |
Answer / pradip ramoliya
Watt = ampier x volts and 1kw = 1000watt
| Is This Answer Correct ? | 13 Yes | 8 No |
if we give 60 hz single phase supply to the transformer used in europe , than what will happen
if our load is 65000 watts howcan we find out all char like cable size. mcccb etc
How to size Air Circuit breaker (ACB)? What is the most important factors?
1.Why we use choke?If we use for high starting voltage then different type choke gives different voltage. Is it correct?
How to decide whether A / B / C / D curve type MCB should be used?
What are the test performed on A faulty transformer ?
how to calculate total load in a villa?
What is the function of PMG in DG sets & how it works??????????
in 11kv generators the neutral point is connected to earth via earth coil while in the 33 / 11 kv transformer the neutral point is connected to earth via earth resistor why?
how to make neutral to ground voltage less than 5v? my house is under the high voltage transmission line so,proper grounding using rod salt n coal doesnt help me..so wat i do as i cant operate my computer ..this high voltage cause great problem to the motherboard i already two times replaced it.in my house voltage is coming near to 25 v between ground and neutral.plz kindly post ur answer to my email id manish77777@gmail.com ..
can we use 7volt DC BATTERY to run a 60watt motor by stepup? Give reason for your answer?
for hipot test on 33kV busbar, we will test on 70 kV or 56kV, what is the acceptable leackage current?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)