Why we should use delta connection in primary and star
connection in an distribution transformer, which converts
400v a.c. voltage to 33kv.
Answers were Sorted based on User's Feedback
the answer of Mr. RVG is correct. But I would like to
correct the question itself. Distribution transformer
converts voltage from 33KV to 400V, not 400V to 33KV.
Is This Answer Correct ? | 68 Yes | 11 No |
Answer / engr. abdul barek, electrical
We use in star connection in seconday connection becouse
need neutal point in load sied( some load supply need 3
phase and some need single phase)but it is remember that
only star connection use in distrubution side transformer.
Is This Answer Correct ? | 82 Yes | 30 No |
Star connection having multiple option of voltages, and
availability of neutral point makes useful for earth fault
relay operation.
Delta connection having requirement of 3 conductors and
itself is long distance, with less current and higher
voltage. So economical way is delta at high voltage side
and star at low/ or consumer end.
Is This Answer Correct ? | 55 Yes | 12 No |
Answer / r m koloi
we dont need nuetral at primary side but it is needed at
sec. side because some loads of 3 ph and single phase loads
required nuetral.
Is This Answer Correct ? | 45 Yes | 19 No |
For distribution transformers, loads are connected to
secondry side. hence, requirement of neutral can be
obtained by connecting secondry of the transformer in star.
Secondly, to reduce or minimise the third harmonics in the
transformers, primary side connection generally done in
delta.
Is This Answer Correct ? | 18 Yes | 4 No |
Answer / nitin palaskar
we should use delta connection in primary and star to
secondary because in delta line voltage = pphase voltage
and instar line voltage = 1.732phase voltage hence we get
173.2% more voltage hence we use delta star transformer.
Is This Answer Correct ? | 11 Yes | 3 No |
Answer / siva
in secondary side there is a chance for single phase load,
three phase load, if its single phase load added more there
is a chance for unequal voltage in each phases. here we
need one neutral point that is refered as a reference
potential for load equalise the phase voltages
Is This Answer Correct ? | 8 Yes | 3 No |
Answer / gangadhar
Primary function of Distribution Transformer is to step-
down 33kv into 440v..while designing the transformer we
have to consider conductor size also...in delta side line
current=1.732 times phase current and in star side phase
current=line current...as we know current is directly
proportional to cross-section of the conductor..keeping in
mind about the cost factor of conductor on load side they
prefer star connection on load side..Guys i tried to
explain in different way..i agree with above answers
also
Is This Answer Correct ? | 4 Yes | 1 No |
Answer / swayanjit
WE USE DELTA CONNECTION AT PRIMARY AND STAR CONNECTION AT
SECONDARY IN CASE IF STEP UP OF VOLTAGE REQUIREMENT BECAUSE
IN DELTA/STAR TRANSFORMER THE OUT PUT VOLTAGE WILL BE 1.413
TIMES HIGHER THAN THE PHASE VOLTAGE EVEN WHEN BOTH HAVING
SAME NUMBER OF TURN. SO THE SECONDARY WILL REQUIRE LESS
INSULATION.
Is This Answer Correct ? | 9 Yes | 9 No |
what is load shedding
can any one help me out by posting something related to rvnl interview for site engineer electrical.? what is the procedure? what kinda question they ask us? how long the interview goes? and any tips? and any thing you want to share?
what is ripple component in ac supply?
lenz law application and define
i want design of D.C.MOTOR 1HP 960RPM AND 2HP 960RPM ITS URRGENT
Reversal of corrent feature in MCCB- What is reversalof current -explain broadly.
can we share mvar in parrelell connected alternators
Brief function of stepper motor
True or false question. 1.The fuse provide phase and neutral 2.power loss in electrical circuit can take place in (resistance or inductance or capacitance). 3.two phase system each phase has separated by a phase difference of (90 or 180 or 270 or 45). 4.3 phase balanced star connected load neutral current shall be (line current or phase current or zero or unity)
What is formula of capacitor for 1-phase power connection.how to improve PF. Suppose I want to connect capacitor in refrigerator to reduce power consumptions.
what is the rating of power generation in india?
why the all high voltage transformers are in 11kv , 33kv , 66kv, 132kv like that