1.After synchronising the alternator to the grid,how we r
delivering power to the grid?if the i/p increases does the
speed hence frequency increases?
2.y the power factor is changing when exitation changes?what
is the relation with p.f and flux?
Answers were Sorted based on User's Feedback
Answer / mm
real power delivered per phase=VE*(p.f).when excitation is
increased without increasing input to prime mover the real
power remain constant.as per the above equation as
excitation changes pf has to change correspondingly to
maintain real power constant
| Is This Answer Correct ? | 5 Yes | 3 No |
Answer / k.prakashchandra
If you want to increase the speed more input to prime mover
is required.As the grid is very large ,this will result only
in more sharing of load.You can not change the frequency.If
you increase the excitation, the terminal voltage of gen
will increase ,and you can not increase the entire grid
voltage . This additional voltage will drop in the gen
itself and a small portion of grid ,resulting in more gen
current and increased lagging pf.If the terminal voltage of
the gen is less than grid voltage the power will be
evacuated at leading pf and again more gen current.
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / raul
after synchronising, the real power delivered by d
alternator is VI*p.f.........if the input increases, the
real power power will increase, there will b no effect on
speed n frequency........
when excitation changes, the reactive power changes which
is a function of p.f............
an alternator operates at lagging power factor when over-
excited and operates at leading power factor when under-
excited.........bcoz at leading power factor......the rotor
ampere turn increases and hence flux increases, thereby
increasing the induced voltage......so to keep the induced
voltage constant.........the excitation has to be
decreased..........n vice versa
| Is This Answer Correct ? | 1 Yes | 2 No |
The real power is goverened by Frequency of prime mover.
The relation between real power and frequency of prime
mover is inversly proportional.So as load increase on the
grid it is shared by the genset and increased load met by
reducing the speed .Then governer throat open more to enter
more steam to maintain the frequency.
The voltage at alternator is controlled by the reactive
power flow. So increase in excitation beyond normal provide
capacitive VARs and decrease in excitation less than normal
provides the Inductive VARs required by the system.
generally the system comprises of Inductive load like
motor,transformer so alternator operate mostly in Under
Excitation state.
| Is This Answer Correct ? | 1 Yes | 3 No |
Why primary batteries not rechargeable and secondary batteries are rechargeble??? If any one know please send me.
What is power factor? How to improve Power factor? draw a circuit diagram showing the connection of power factor improvement equipment to the electrical instillation.
Hi frnds :) plz tell me that i have 100 KVA 3 phase generator so by thumb rule 100*1.4 = 144 amps and generaly we can operate at 80% load...so it will 144*0.8 =112 amps.... so now i m confused about single phase load.....if we use that generator only for single phase the that 112 amps is total single phase load or i can give 112 amps at red 112 amps at yellow and 112 amps at blue.... i mean that total single phase load that 100 KVA generator will take is 112+112+112=336 amp ??
can we use 400w coke instead of 250w choke in 250w fittings
How to calculate that clean water supply in one Day from 150 KLD STP?
What are the circuit models used for analysis of medium length transmission lines? Which one is superior? Support your answer.
when a 500kva-400hz single phase transformer operated on a 100hz supply then what will be kva required
why the flooring of substation is done with small pebbles or stones..?
What type of changeover switch needed to run a load of five 1.5 tonn ACs.
can you give me some names of projects which can be used in our daily life & which is having medium cost?
What is meant by sotf,lbb,power swing,pole discrepency,auto reclose?
1 Answers Bunge, Electrical, Omega, TCS, TNEB Tamil Nadu Electricity Board,
Pls explan the OLR setting in VCB at HT yard
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)