WHAT AC (HI VOLTAGE TEST) VOLTAGE SHOULD APPLY FOR 33KV
CABLES.EXPLAIN IN DETAIL
Answers were Sorted based on User's Feedback
Answer / ran7it
u can use a hipot kit. for a 33kv cable the voltage 2 b
applied can b determined by formula (2E + 1),,whr E is the
system voltage,so for tis case it comes as 2*33 +1=67kv.
tis 67kv is mostly applied for the first time in factory
testing..after tat only 60-70% of 67kv sud b applied.
the cable has to withstand tis voltage for 1min..
| Is This Answer Correct ? | 27 Yes | 4 No |
Answer / rod
Answer 5 is correct, the only thing is it is now not common
practice to Hi-pot cables as this can cause damage to it,
PD tests is the normal method of testing.
| Is This Answer Correct ? | 7 Yes | 3 No |
Answer / john sundararaj
First decide on which type of cable
type of insulation,single core or 3 core
Ans 8 is the right one.Always go by the manufacturers
recommendation.The values differs for each standards and varies for different countries/utilities.Most of them prefer
soak test rather than hipot.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / mc
we have to consider the phase voltage to ground and nature
of material, but for the first test it's every time
manufacture specification as to be follow.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / suresh babu
HI POT test how much KV applied for 33KV Cable and Time
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / s bhattacharya
TO DECIDE THE VOLTAGE APPLICABLE FIRST THING TO SPECIFY
TYPE OF CABLE .
1.IF SINGLE CORE 9NEW CABLE)THEN AS PER IEC GO FOR
BILX0.8/1.732 -AC WITH VARIABLE FREQUENCY CONTROL KIT TO
ADJUST THE FREQUENCY AS PER CABLE LENGTH.
FOR CABLES LESS THAN 132kV.
| Is This Answer Correct ? | 3 Yes | 4 No |
Answer / guest
Cables are naturally made of pvc,so we can apply high
voltage test to the cables and if its in no damage in high
voltage it should be declared good cable.
| Is This Answer Correct ? | 8 Yes | 14 No |
Answer / blake australia
A lot of HV cables are XLPE not PVC. If you Megger a 33kV
cable with a DC voltage then you may damage the XLPE
semiconductor around the cable.
Industry standard in Australia(although very expensive to
buy one) is to use a VLF (very low frequency) tester to
test the cables. Same principal as mentioned, just uses an
AC waveform (~.1Hz) opposed to a DC waveform.
| Is This Answer Correct ? | 5 Yes | 14 No |
how to convert kw in to unit
how to setting Load amps tripping time and extra settings for load Transformer protection relay with RMU panel using C&S model relay..?
Why LVDT have secondary windings connected in differential 1. Higher out put 2. Based on the out put voltage-/+, helps to identify the direction of displacement 3. To establish a null/ reference point
wat is mean by HRC fuse... WHY we choose it...?
what are the disadvantages of low power factor
DIFFERENCE B/W NEUTRAL AND EARTH?
What will happen if 40W and 60W Bulb is Connected in Series.
Is C.T will sense the current in both direction. As i know the C.T will sense the current in only one direction.
boiler is running in rankine cycle and deisel generator is....?
Which of the following statements is incorrect?(a) 1N = 1 kgm/s2(b) 1V = 1 J/C(c) 30mA = 0.03A(d) 1 J = 1N/m
we have provided 30 nos. relay contacts in panel.I want to know how do we do the numbering for the relay contacts as per any applicable standards
in transmission line 11kv is step up or step down? why?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)