copper losses depends on current and iron losses depends on
voltage. Total transformer loss depends on volt-ampere (VA)
and not on phase angle between voltage and current i.e., it
is independent of load power factor. That is why
transformer's rating is in KVA
| Is This Answer Correct ? | 33 Yes | 1 No |
Answer / parthipan
copper losses depends on current and iron losses depends on
voltage. Total transformer loss depends on volt-ampere (VA)
and not on phase angle between voltage and current i.e., it
is independent of load power factor. That is why
transformer's rating is in KVA
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / dinesh giri
Actully Transformer has any no its power factor.Its power
factor depends on the connected Load with it.The connected
load may be inductive or capactive or resistive Load or
mixed of all .
Connected Load rating in KW
As KVA*Power Factor(COS A)=KW
Rating of Transfarmaer is always taken in KVA
| Is This Answer Correct ? | 4 Yes | 2 No |
Answer / mahender mohal
Simply transformer is a power transfer device not a power
consuming device,so it have negligible loss (depends on
volt-ampere),so cos$ is >0.96 approx. 1.P=vi;due to this
reason x-mer rating is in VA Or KVA.
| Is This Answer Correct ? | 4 Yes | 8 No |
Answer / s. kumar
The power factor of the transformer depends on the load P.F
of the system where the transformer is connected. so the
manufacturer cant rate it in terms of KW.
| Is This Answer Correct ? | 1 Yes | 6 No |
power factor is max for which welding a.arc b.resistance c.gas
what is differnce between grounding and earthing or both are same?
how to increase senstivity of ct
how to prepare PPM schudule
The windings of a transformer are divided into several coils, because?
why any surge protection is not provided to UHV ac transmission line (765kv) ?
1 Answers NK Power Systems, Reliance,
What is the power factor you maintain at ur organization?
43 Answers Cummins, Exide, Johnson and Johnson, KTC, Microsoft, Powergear, Secure Meters, Suncity Strips, Wheels India,
enlist types of dc generator
How to detect voltage vector shifting in interconnection protection.
In a company the lines carrying 33KV but the load is below 10000Volts so we know that <11KV we can put 11KV lines but the lines are 33KV,..so how we can step down the voltage to 11KV with out erecting a substation
What is lifting power for 1 wb/m2 and 1 A magnet?
Swg formulae
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)